I suspect the key is the water usage.
According to EU M324EN the average European family usage is the equivalent of 100 litres @ 60 degrees.
But I'm sure that if the house is occupied all day and no changes in life style have been made this number can be easily exceeded.
To heat the 100 litres of water from 15 degrees (assumed cold water temperature) to 60 degrees takes 4,500 litre-degrees or 5.3KWh (1kWh = 850 litre-degrees)
As the peak output of 30 tubes is around 1.5Kw they ought to be capable heating it during a reasonable day.
You will see from my sig. that we have a somewhat 'under tubed' system.
I have had to re-train my wife (AKA discussion, heated debate, "of course I know how a thermostat works") to not keep using hot water during the day.
If she reverts to type, and rinses everything under the hot tap after every cup of tea, then our system's performance is only 'ok'.
If I can persuade her to just put stuff in the dishwasher during the day, then the system works fine.
Right now at 18:09 we have 210L at 62C. Boiler not been on for a few days now.