egogen - you're missing a vital point
Err... you installed the extra PV without referring to G83, G59 and the Distribution Code?
You installed the extra PV without a connection agreement?
You have a headache?
My ego has just eaten a whole packet of custard creams and is not looking very well...... I'll clean the mess up later.
In my last post I referred to the wind turbine as EXISTING. I then referred to parts of G83/1-1 that apply to it. The reason being to show that it does not fit well with using Stage 2 to connect the additional PV. Because 1). The definition of a SSEG [1] used in 5 Requirements. 5.1.2 Stage 2 Connection (multiple / planned install) and 2). It would be G59 if not for the DNO considering G83 more appropriate, for a SINGLE unit. [2] [3].
Excerpt from the Distribution Code.
(DPC7.1.3 For the avoidance of doubt a user who has installed a Generation Set in accordance with Item 13 DGD Annex 1 Engineering Recommendation G83/1-1 ("Recommendations For The Connection Of Small-Scale Embedded Generators (Up To 16 A Per Phase) in Parallel With Public Low-Voltage Distribution Networks") and where this is (are) their ONLY Generation Set(s), and which has been installed, commissioned and operated in accordance with Annex 1, Item 13, that User shall not be required to comply with the requirements of DPC7 in respect of that (those) Generation Set.
DPC7.2.1 Embedded Generators connected to the DNO’s Distribution System WILL comply with the requirements of Item 3, DGD Annex 1 Engineering Recommendation G59/2, "Recommendation for the connection of generating plant to the distribution systems of licensed distribution network operators". )
I see this as generation installed using G83 (Stage 1) or sets (Stage 2) does NOT have to meet the requirements of G59.
However this is applicable to the users ONLY generation set(s). If additional generation is to be added then it WILL have to comply with G59.
Therefore, 6 Connections 6.1.6 Amalgamations and additions needs to be considered. I repeat that the solar PV does NOT require G59 protection settings.
A contactor and supervisory relay installed and tested would comply with the requirements of 12.2.5.
http://www.g59-test.co.uk/page5.html This will require A 13.3 commissioning tests. All together £2k of pain.
In my last post I was trying to find a way within the documents to save the need for this. Refer to 12.2.2 and consider trying to persuade the DNO to accept the wind turbine as "type approved generating plant", even though it is G83 approved and not G59, by changing the protection settings and adding comment on the inverters type verification test sheet. You then self certify that "type approved generation plant" is installed and complies 12.2.4 c.
With regard to G83 / G59 protection settings there is no Over Voltage difference, 1.8 Under Volt difference, 0.5 Hz Under difference and 1 Hz Over difference.
Trip times depend on the type of inverter, but if generic then G83 is quicker to trip.
It seems obvious that the G83 protection settings in the individual inverters are more than adequate to safeguard 9kVA of connected generation.
Common sense would be to choose appropriate settings that keep within the limits and achieve stable system operation at that location.
I have tried to get as close as possible to this end by using the ER docs quoting chapter and verse. If G83 had been extended to 17kW 1 ph. and 50kW 3 ph. then this level of absurd complexity would be avoided.
[1] G83 1-1. 4 Definitions. SSEG. A source of electricity rated up to and including 16A phase single or multi 230/400V.
[2] G83. 2. Scope. Note 2. As the SSEG has a rating greater than 16A phase the DNO may choose to use G83 if it is considered to be more appropriate than G59-1 (G59-2). For example the connection of a 5kVA PV array or 10kVA wind turbine.
[3] G83. 2. Scope. As the SSEG has a rating greater than 16A phase the reader is referred to ER G59-1 and ETR 113 (G59-2).