News: Anyone wishing to register as a new member on the forum is strongly recommended to use a "proper" email address - following recent spam/hack attempts on the forum, all security is set to "high", and "disposable" email addresses like Gmail, Yahoo and Hotmail tend to be viewed with suspicion, and the application rejected if there is any doubt whatsoever
 
Recent Articles: UPDATE ON DECC APPLICATION FOR LEAVE TO APPEAL TO THE SUPREME COURT | Yingli Green Energy's PV Module Ranks No.2 in TUV Rheinland Energy Yield Test | Navitron Solar Showers at Glastonbury for Year 5!
   Home   Help Search Login Register  
Pages: 1 [2]   Go Down
  Print  
Author Topic: Grid Voltage Too High - What can I do?  (Read 3622 times)
SnaxMuppet
Full Member
***
Offline Offline

Posts: 223



WWW
« Reply #15 on: January 19, 2011, 08:13:17 PM »

Had the recorder installed today... removal next Wednesday or Thursday.

They definitely seem to be taking this seriously. While he was here this morning voltage was 248V. He said it was high but didn't think that they would change anything if it stayed below 254V. We will see...
Logged

Grid-tied 2.4kWp PV, 10 x 240Wp Phono Solar modules, Fronius IG20 inverter, Cornwall.
aloha
Jr. Member
**
Offline Offline

Posts: 54


« Reply #16 on: January 19, 2011, 11:15:25 PM »

263 volts is the tripping voltage of SMA SunnyBoys.

And the ESQCR's say that the maximum 230V voltage should be 253V.  If you run your voltage (or anyone elses) at >253 volts for any length of time (so thats short term transients excepted), then the ESQCR's are not being complied with.  This needs to be borne in mind when you set up your inverter parameters.
Logged
Other-Power
Sr. Member
****
Offline Offline

Posts: 366


« Reply #17 on: January 20, 2011, 10:46:37 AM »

263 volts is the tripping voltage of SMA SunnyBoys.

And the ESQCR's say that the maximum 230V voltage should be 253V.  If you run your voltage (or anyone elses) at >253 volts for any length of time (so thats short term transients excepted), then the ESQCR's are not being complied with.  This needs to be borne in mind when you set up your inverter parameters.

Agreed, the 263 volts limit applies to transients.
Logged
aloha
Jr. Member
**
Offline Offline

Posts: 54


« Reply #18 on: January 20, 2011, 11:49:57 AM »

And therefore the 10 minute average limit of 253V needs to be applied.  For systems with too high a grid voltage, or too high an impedance, the 264V trip setting will not resolve the issue, as when you get a sunny period, the production will up steadily, and so will the grid voltage if the impedance is too high.  Running continuosly at 263.5 volts all day is not a suitable way around dealing with a supply voltage or impedance that is too high!
Logged
Other-Power
Sr. Member
****
Offline Offline

Posts: 366


« Reply #19 on: January 20, 2011, 12:48:01 PM »

Voltage flicker is directly proportional to source impedance.

High source impedance being due to long high voltage and or low voltage runs as well as high loading of a transformer, typical of Cornwalls distributed network.

So yes the 253 volts should be applied for durations and the 263 volts for transients (SunnyBoy should kick out a 261 volts)

Jonathan
Logged
SnaxMuppet
Full Member
***
Offline Offline

Posts: 223



WWW
« Reply #20 on: February 08, 2011, 05:48:15 PM »

Update:

The result of the logger installed by the DNO is that they agree that the voltage is too high and they are adjusting it at the substation tomorrow! They will then install a logger again to confirm that it is then at an acceptable level.

RESULT!  extrahappy
Logged

Grid-tied 2.4kWp PV, 10 x 240Wp Phono Solar modules, Fronius IG20 inverter, Cornwall.