News: Anyone wishing to register as a new member on the forum is strongly recommended to use a "proper" email address - following recent spam/hack attempts on the forum, all security is set to "high", and "disposable" email addresses like Gmail, Yahoo and Hotmail tend to be viewed with suspicion, and the application rejected if there is any doubt whatsoever
 
Recent Articles: UPDATE ON DECC APPLICATION FOR LEAVE TO APPEAL TO THE SUPREME COURT | Yingli Green Energy's PV Module Ranks No.2 in TUV Rheinland Energy Yield Test | Navitron Solar Showers at Glastonbury for Year 5!
   Home   Help Search Login Register  
Pages: 1 [2]   Go Down
  Print  
Author Topic: my new 3.9kw install  (Read 3940 times)
BruceB
Hero Member
*****
Offline Offline

Posts: 621

MCS certified for Solar PV & thermal, GSHP & ASHP


« Reply #15 on: February 22, 2011, 01:12:50 PM »


All SMA inverters have galvanic isolation as far as I am aware.

Jonathan

No, I do not believe so.  The SMA TL series are 'transformerless'.  Galvanic isolation as I understand it means with an isolating transformer.

Regards
Bruce
Logged
Outtasight
Hero Member
*****
Offline Offline

Posts: 843



WWW
« Reply #16 on: February 24, 2011, 02:16:22 PM »

Yep, the TL models are not fully isolated but are considered safe due to other measures.

In order to get away without using a transformer, they use H5 inverter switching topology.  At times in the AC cycle, the AC and DC sides are disconnected by a switch.  During the times in the AC cycle when the two sides are connected, a RCD monitors the AC side for earth leakage current, and if detected, it causes a ground fault signal that disconnects the inverter from the grid and shuts down the system.  They also employ a start-up test of the DC side insulation resistance before connection to further check if there is a ground leak on the DC side.  The disconnect relay is double pole (L and N) and has uses two relays in series so that if one fails to open, there is a backup.

A paper here explains the switching topologies being used in transformerless inverters.

http://www.elkraft.ntnu.no/eno/Papers2008/Schimpf-norpie08.pdf   
Logged

http://solarbodge.blogspot.com/ also BDPV Production Graph (daily update)
2.80kWp & 400Ah LiFeYPO4 off-grid. See 'Cobbled together PV in W.Sussex' (in "Show Us Yours")
ecotrician
Full Member
***
Offline Offline

Posts: 158



WWW
« Reply #17 on: February 26, 2011, 04:54:26 PM »

RCD protection can not be used as primary fault protection, all transformerless inverters need the array frame to be bonded as per DTI guidance note, if TNS or TT then to MET, if TNCS then to earth rod.

SMA guidance in instructions also states this:

Grounding the PV generator
Comply with the local requirements for grounding the modules and the PV generator.
SMA Solar Technology recommends connecting the generator frame and other electricity
conducting surfaces such that there is continuous conduction and to connect them to the
ground in order to reach maximum protection for property and persons.


Logged

MCS registered installer
NICEIC Approved Contractor
firepete
Full Member
***
Offline Offline

Posts: 231



« Reply #18 on: February 27, 2011, 09:22:34 PM »

well mine has not been earthed. should it have been then.

i have had 3 trips on my main circuit board rcd since install. not sure what caused it. but on two ocasions i think i was cleaning the panels outside. facepalm
Logged
tange179
Full Member
***
Offline Offline

Posts: 197


« Reply #19 on: May 08, 2011, 07:14:22 PM »

Word of a caution - be careful where you place your earth rod i.e. keep well away from any underground electrical cables as you do not want to be responsible for taking out your street should you be unlucky enough to be hit by lightning  fume

John
Logged
firepete
Full Member
***
Offline Offline

Posts: 231



« Reply #20 on: May 11, 2011, 08:46:11 PM »

removed rcd protection and now just on a mcb . seems fine
Logged
Alan
Guest
« Reply #21 on: May 11, 2011, 10:43:32 PM »

Quote “ Word of a caution - be careful where you place your earth rod i.e.  fume
keep well away from any underground electrical cables as you do not want to be responsible for taking out your street should you be unlucky enough to be hit by lightning 

John “

Bit OTT

Any house with a T.V. Aerial on the Chimney pot has got more chance of copping one. Thats why lightning protection rods are made with pointed tips to encourage discharge to take place.

If I had a T.V. Aerial on the roof it would be very low on the lists of things to worry about.

Regards

Alan