Electrolyte circulation: LUXURY!

After the solar panel install the batteries are doing very well and am really pleased with the power from the panels - have not had to use the generator at all since we moved into the house over Christmas.
The morningstar mppt has a normal absorb setting which I've set to 2 hours at 2.42V and an extended absorb in case the battery voltage drops below a certain value the night before, which I've set to 2.5 hours. So the day after an overcast day, the batts will absorb for 4.5 hours at 2.42V.
But I noticed that even with this setting they never seem to reach the full SG value of 1.29. Even after a few days of full sun, they hover around 1.27 - 1.275, and only reach 1.29 after an EQ.
There seems to be two schools of thought for charging:
- The yanks who use Rolls and Trojan batts say that the batts should ideally be fully charged every day (but then they rarely have batts that last longer than 10 years). And they don't have PzS cells over there.
- The victron whitepaper (
http://www.victronenergy.com/upload/documents/Book-EN-EnergyUnlimited.pdf) where the author says that it's not necessary to fully charge every day, just keep the batt above 80% charge and then EQ once a month. This reduces corrosion of the positive plate. Incidentally, he also advices lower float voltages to also reduce corrosion.
The added complication is that my cells are very tall at about 1m, so I think an EQ more often will help sort out the stratification even though they're typically only discharged 10% every day.
So right now I'm not sure how often and how long to EQ for:
- Do a very short EQ at 2.6V, say 2 hours every week to prevent stratification and rely on the normal absorb charge to do the full charging.
- Do a longer EQ at 2.6V for 3 hours every 14 days
- Do a proper EQ at 2.6V for 4 hours every month.
And I don't know which will be best for the batts because grid corrosion at the more frequent EQ will only show up after many years of use.