Thanks for suggestions.
__________________________
It's just single phase. So I guess it's 4 cores to double up conductors.
__________________________
Found the tlc site. Also see branches stock lengths up to 1,000 mtrs in some sizes, would be good to avoid having a join.
The tlc calculator for 4kW, 240V 200m comes up with
Required Cable Size 16 mm
Voltage Drop 8.33 Volts.
Percentage Drop 3.5%
Current Load 16.0 Amps
Max Cable Load* 75.0 Amps
8.7V at 17A gives 0.51ohm, power loss 148W.
200m of three core SWA (using per 100m price) is £988 for 16mm², £702 for 10mm². A £286 difference.
____________________________
My calculation (used BASEC spec as had all the figures):
The BASEC 16mm² cable spec
http://www.neweysonline.co.uk/basec-standard-cable-black-100m-copper-16mm-three-core/1050300610/ProductInformation.ractionquotes resistance of 1.15ohm/km@20C. So 400m is 0.46ohm (similar to above)
For BASEC 10mm² resistance quoted 1.83ohm/km. So 400m is 0.73 ohm.
BASEC costs, for 200m, are £874; £626. That's £247 more for 16mm².
To make that up, at top FIT solar rate, would mean supplying £247/ £0.413 = 598 kWh more.
4kW at 240V = 16.6A RMS.
Loss at 16.6A over 200m run (400m wire) I²R : 16mm² 127W; 10mm² 200W
At loss difference 73W, to feed in 598kWh more would take 598kWh / 73W = 8,192 hours.
I believe 700-750 return hours is quoted for here (North Scotland). Using 725 hours gives annual production of 2900kWh. Twould mean over 11 years for return on cable investment.
Looking at it another way, 725 hours annual production is 2900kWh, with annual cable loss of 92kWh/£38 (16mm²) or 145kWh/£60 (10mm²).
I got the return on 10mm² cable over 6mm², to be 5.5 years. That seems reasonable.
Doubling up 10mm² gives a loss of 100W, and costs £378 more than 16mm².
£378 at £0.413per kWh is 915 kWh. At the 27W loss difference this would take 33,898 hours - nearly 47 years! Don't think I'd see any saving.
Also ground temperature is usually below 15C, and 4kW (without tracker) would only be produced at peak hours. Would guess maybe >3kW for <3hours a day. So losses will be lower than above for most of the time.
________________________
The only problem I can imagine, is that the grid-tie inverter (anti-islanding protection) might detect resistance / voltage drop as a fault and so cut out.
Any ideas on UK grid-tie limits?
I was considering the Aurora PVI-3.6-outd-s, as its IP65 and includes RS485 comms, good over the distance involved, and there's the free Aurora communicator pc prog.