google tlc cable calulator if you have not found it already.
Putting your numbers in (4kw, 180m and SWA 2 core) gives a cable size of 16mm2 and voltage drop of 3.9%.
At that length you are limited by 5% voltage drop rather than cable capacity.
So is that 5% voltage drop limit due to this? :
Another thing to consider is grid voltage at your site.
The inverter will run at grid voltage plus cable loss voltage. If grid voltage is high, it might cause the inverter to trip out due to over voltage protection.
from dti
http://www.dti.gov.uk/energy/reliability/quality-continuity-supply/index.htmlIn Great Britain domestic supplies must be maintained within the range 216 volts to 253 volts, corresponding to a nominal value of 230 volts, minus 6% to plus 10%.
The inverter I was considering, Aurora PVI-3.6-OUTD, has spec:
Nominal AC voltage range 200-245V
Maximum AC voltage range 180-264V (may vary to comply with country regulations)
So don't really know what the inverter might allow, need the spec for UK grid tie.
If it was 253V +5% that would explain that '5% voltage drop limit' for the cable (in order to always deliver full power).
With 4kW system and cable Voltage Drop 8.33 Volts (3.5% @230V), if inverter limits at 253V that means the power delivered would reduce as grid voltage rose above 245V.