Simon, that sounds like a great idea. It wouldn't need to be the solar controller that triggered the change... just a thermostat on the thermal store. If it's the log boiler overheating the thermal store then the change of flow in the solar circuit won't make anything worse!
Indeed. The downside of course is that you would have two separate overheat protections - one for solar, one for woodburner.
I can see 3 options for the diversion -
1) when thermostat activates, solar circuit is diverted to only go through the dump load (not the thermal store).
2) when thermostat activates, solar circuit is diverted so that it goes first through dump load and then secondly through the thermal store.
3) when thermostat activates, solar circuit is diverted so that it goes first through thermal store and then secondly through the dump load.
I know it's late (or should that be very early?) and my brain isn't working properly. For some reason I my instinct is that 2) is better, but I can't explain why. Just exhaustion, or am I right?
I'd suggest 1 as being by far the simplest - once the store is up to max safe temp, then you might as well just dump your solar altogether. On the other hand, it does depend on the capacity of your dump and what your priorities are. Ie, if your lump of concrete under the woodpile gets very hot, what do you want to do - keep heating it and eventually have your solar overheat, or keep putting heat into the store and deal with it elsewhere ?
2) may actually cool the bottom of the store - if solar input is not too high, then you could cool your solar loop below the store temp before putting it through the solar coil. Thus you will be throwing away heat you might actually want later - but only from the bottom of the store.
3) may continue to put heat into the store, depending on your dump capacity and flow rates.
If you wanted fail-safe-ish then you could arrange for the diverter to go to the dump load by default, and rely on it motoring over to heat the store. That way the valve is exercised regularly and you shouldn't find it seized when it is needed.
On the other hand, if you wanted to protect the store from both solar and woodburner (and avoid needing two different dump loads) then you could either put an extra coil in the top and run the dump load on it's own loop, or use a plate heat exchanger (which of course then needs two pumps, one for the store side, one for the load side). Whether this is enough for an uncontrolled input like the woodburner I don't know.