http://www.engineeringtoolbox.com/hazen-williams-water-d_797.htmlhttp://www.freecalc.com/fricfram.htmYou need to know the gallons per minute that you want to transfer.
Is it a variable speed pump. You need to be able to take the maximum amout of heat away from the panels.
Information provided on the data sheet provided from your pump manufacture
You also need to know the pump head capacity.
Below is two examples for
first ( pipe inside diameter ) 0.622 inch. At 10 gallons per minute gives a loss of 30.62 P.S.I. Across 100 ft of pipe
second ( pipe inside diameter ) 1.049 inch. At 10 gallons per minute gives a loss of 2.5 P.S.I. Across 100 ft of pipe
This is based on clean pipe, when you factor in pipe roughness for calcium deposits it gets far worse.
Its all down to how many gallons per minute you need to transfer to stop the system from over heating.
How mant right angle bends. The losses get silly with bends ?
Pressure Loss (psi): 30.62 Head Loss (ft): 70.7Line Number:
Date: 5/3/2011
Nominal Pipe Size: 0.5
Pipe Schedule: SCH 40
Flow Rate (gpm): 10
Viscosity (cP): 1
Specific Gravity (water=1): 1
Temperature (F): 180
Pipe Roughness (ft): 0.000005
Actual Pipe ID (in.): 0.622
Fluid Velocity (ft/sec): 10.56
Reynolds Number: 50845
Flow Region: Turbulent
Friction Factor: 0.021
Overall K: 40.82
Pressure Loss (psi): 2.5 Head Loss (ft): 5.8Line Number:
Date: 5/3/2011
Nominal Pipe Size: 1
Pipe Schedule: SCH 40
Flow Rate (gpm): 10
Viscosity (cP): 1
Specific Gravity (water=1): 1
Temperature (F): 180
Pipe Roughness (ft): 0.000005
Actual Pipe ID (in.): 1.049
Fluid Velocity (ft/sec): 3.71
Reynolds Number: 30149
Flow Region: Turbulent
Friction Factor: 0.024
Overall K: 27.01
Go large and insulate.
Regards
Alan