News: Anyone wishing to register as a new member on the forum is strongly recommended to use a "proper" email address - following recent spam/hack attempts on the forum, all security is set to "high", and "disposable" email addresses like Gmail, Yahoo and Hotmail tend to be viewed with suspicion, and the application rejected if there is any doubt whatsoever
 
Recent Articles: UPDATE ON DECC APPLICATION FOR LEAVE TO APPEAL TO THE SUPREME COURT | Yingli Green Energy's PV Module Ranks No.2 in TUV Rheinland Energy Yield Test | Navitron Solar Showers at Glastonbury for Year 5!
   Home   Help Search Login Register  
Pages: [1] 2   Go Down
  Print  
Author Topic: Not all solar coils created equal?  (Read 1752 times)
Jaded
Newbie
*
Offline Offline

Posts: 5


« on: May 26, 2011, 08:46:23 PM »

I've been mooching about for a new vented cylinder but can't fathom why each supplier has similar recomendations about cylinder volume for panel size but apparently completely different standards regarding solar coil area.
What am I missing, sage advice welcome.  Huh
Logged
martin
Administrator
Hero Member
*****
Offline Offline

Posts: 11428



WWW
« Reply #1 on: May 26, 2011, 08:54:01 PM »

All coils are not equal - some are just coiled tube, some are finned (giving a larger surface area), some are less efficient because they're stainless steel instead of copper, copper thermal conductivity varies according to the "type", and then opinions vary as to what is the optimum area....
Personally, I'm lazy and have always followed the sage advice from the fellas at Newark who make the "house brand" tanks - they've never let me down yet - http://www.newarkcoppercylinder.co.uk/ Wink
Logged

Unpaid volunteer administrator and moderator (not employed by Navitron) - Views expressed are my own - curmudgeonly babyboomer! - http://www.farmco.co.uk
desperate
Guest
« Reply #2 on: May 26, 2011, 08:54:55 PM »

Some coils use smooth pipe, some corrugated or finned, and some bundles of 10 or 8mm micro in parallel, I'm guessing but probably different designs call for different areas.

Desp

PS Martin types quicker than me Smiley

PPS welcome to the Forum.
Logged
Brandon
Hero Member
*****
Offline Offline

Posts: 1245



« Reply #3 on: May 26, 2011, 09:26:46 PM »

not equal indeed.

The requirement for a clear skies cylinder solar coil was that it was 0.58m2

some cylinders still use that size to this date, and they are often in stainless.

I use newark stores and cylinders a lot, as they fit a 1.2m2 copper coil as a minimum (if you are installing what would be regarded as a larger than normal array, then speak to them, and they will put in a longer (and hence with greater area) coil.

whilst the stainless coil will work, it will not transfer as quickly, and therefore the panel return will be warmer, the panel will therefore get hotter for a give insolation and flow rate, this will help the heat transfer at the cylinder end (it being related to conductivity, surface area and delta T) but the system as a whole will be less efficient, as the heat loss through the pipes will also increase in line with the temperature for the same reason.

So the poor client who has the aforementioned stainless cylinder will see higher panel temps initial than his neighbour with the better unit, but an overall lower energy capture.
Logged

changing the world, one roof at a time...

"We can't be B&Q astroturfers. That's one conspiracy theory too far. You should cut down on the pot." - Wookey
Jaded
Newbie
*
Offline Offline

Posts: 5


« Reply #4 on: May 26, 2011, 09:36:28 PM »

Thanks for the quick replies and the welcome note.
Am I correct in thinking that there should be a correlation between solar coil area and the panel header area, I'm sure I saw that mentioned somewhere but have been unable to find it again?

 Smiley

Edit:

I guess you've allready anwered this question. On balance, solar sizing is all about following accepted practice and general guidelines. Lips Sealed
« Last Edit: May 26, 2011, 10:02:44 PM by Jaded » Logged
titan
Full Member
***
Offline Offline

Posts: 208


« Reply #5 on: May 27, 2011, 12:41:23 PM »

All coils are not equal - some are just coiled tube, some are finned (giving a larger surface area),

But how much better is a finned coil. Manufacturers figures are misleading, Newark includes the fins as the surface area of the coil which is incorrect. The surface area should be the area the heating fluid is in contact with. ie the internal surface area of the pipe. I was looking for a suitable cylinder for a heat pump, a few manufacturers quote 3m2 coils but they are including the fins the actual pipe contact area is 1.6m2. Has anyone seen performance figures of the various coil options.
Logged
martin
Administrator
Hero Member
*****
Offline Offline

Posts: 11428



WWW
« Reply #6 on: May 27, 2011, 01:33:20 PM »

It's not wrong, dishonest or misleading in any way, they are quoting "surface area", not the internal capacity of the pipe - simple physics will show that if other factors are the same, more heat will pass from the coil into the surrounding liquid with a finned coil (with a larger surface area) than just a pipe.... Roll Eyes
Logged

Unpaid volunteer administrator and moderator (not employed by Navitron) - Views expressed are my own - curmudgeonly babyboomer! - http://www.farmco.co.uk
titan
Full Member
***
Offline Offline

Posts: 208


« Reply #7 on: May 27, 2011, 10:03:43 PM »

they are quoting "surface area", not the internal capacity of the pipe - simple physics will show that if other factors are the same, more heat will pass from the coil into the surrounding liquid with a finned coil (with a larger surface area) than just a pipe.... Roll Eyes

You clearly have problems reading I said " The surface area should be the area the heating fluid is in contact with. ie the internal surface area of the pipe not the internal capacity. I don't have a problem with fins  but I do when they include them as part of the coil area. Incidental other manufactures do produce 3m2" coils that is a coil with an internal surface area of 3m2 not Newark's 1.6m2 coil with fins described as 3m2. I would like to see some data to show how each coil compares, Newark can't provide it but they say it is the same how do they know.
Logged
Brandon
Hero Member
*****
Offline Offline

Posts: 1245



« Reply #8 on: May 27, 2011, 10:41:51 PM »

I have only ever seen newark state 1.6m2
Logged

changing the world, one roof at a time...

"We can't be B&Q astroturfers. That's one conspiracy theory too far. You should cut down on the pot." - Wookey
wookey
Hero Member
*****
Offline Offline

Posts: 2672


WWW
« Reply #9 on: May 27, 2011, 11:12:35 PM »

Indeed, although finned pipe of 1.6m2 total surface area will have a slightly lower heat transfer rate than 1.6m2 of actual pipe. Not sure how much lower.
Logged

Wookey
bigj
Newbie
*
Offline Offline

Posts: 13


« Reply #10 on: May 27, 2011, 11:21:24 PM »

Does all the above meen that the 1m2 finned stainless steel coil in a DPS TS is pretty useless?
Logged
Brandon
Hero Member
*****
Offline Offline

Posts: 1245



« Reply #11 on: May 28, 2011, 11:19:00 AM »

Quote
But how much better is a finned coil. Manufacturers figures are misleading, Newark includes the fins as the surface area of the coil which is incorrect. The surface area should be the area the heating fluid is in contact with. ie the internal surface area of the pipe. I was looking for a suitable cylinder for a heat pump, a few manufacturers quote 3m2 coils but they are including the fins the actual pipe contact area is 1.6m2. Has anyone seen performance figures of the various coil options.

If it were only the surface in contact with the fluid that allowed heat transfer, then why do radiator manufactures bother with fins?  Be the CH rads or automobile type rads?
Logged

changing the world, one roof at a time...

"We can't be B&Q astroturfers. That's one conspiracy theory too far. You should cut down on the pot." - Wookey
titan
Full Member
***
Offline Offline

Posts: 208


« Reply #12 on: May 28, 2011, 11:48:56 AM »


If it were only the surface in contact with the fluid that allowed heat transfer, then why do radiator manufactures bother with fins?  Be the CH rads or automobile type rads?

Because fins help with the heat transfer increasing the surface area,  I am not disputing that, although both your examples are used in air which is a poor heat conductor. My comments are about  how the coils are described by various manufactures. If heat transfer rates were used for the description the surface area would be meaningless as it would account for different materials conductivity and finning. I spoke with most of the  manufactures about a cylinder for my heat pump, they all said they did special 3m2 coils but only one did have a 3m2 coil all the others had much smaller finned coils but none could provide any data to support how effective their designs were compared with a true 3m2 coil.
Logged
Justme
Hero Member
*****
Offline Offline

Posts: 2877



« Reply #13 on: May 28, 2011, 12:08:40 PM »

When I was looking for a TS / multi use cylinder I contacted lots of makers. I was looking for a bespoke unit so wanted to have usage performance stats for their units.

NONE of them would quote what the output dhw temperature would be at a fixed flow rate through a unit of X deg C evenly through the tank with out adding the complexity of stratification.

Now that cant be that hard to computer model can it?

The closest I got was from a Navitron employee saying that it would work as their system worked at 60c with a smaller dhw coil.

I reckon I could get close just using the real world usage of our 20 tube SFD unit I have, as we know that a tank temp of 50c will let you have 2 hot showers with reasonable flow rates but is to cold for filling the sink fast to wash up (but I do like washing up water to be so hot most people would need gloves and cooling it down some).
Logged

Navitron solar thermal system
30 x 58mm panel 259L TS
1200watts solar 120vdc
FX80 Solar controller
Victron 12v 3000w 120a
200w (250w peak) 12v turbine as a tester
6kva genny
6 x 2v cells 1550amp/h 5C
24 x 2v cells 700amp/h 5C
Total bank 4350 amp/h @12v
Brandon
Hero Member
*****
Offline Offline

Posts: 1245



« Reply #14 on: May 28, 2011, 02:35:54 PM »

most coils are rated at W/K, allowing you to do the extrapolation required for your desired delta T and therefore your optimum flowrate.

Some store manufactures will say it is an x kW coil as a head line, but then you need to look mat the primary and secondary temperatures, and the flow rates.  This is where a lot of the misinformation comes from in the anti thermal store camp, they believe that you absolutely MUST maintain your store at 85oC as that is what the manufactures say, (indeed they do say that , but merely to be able to claim say a 30l/min flow at x oC).  Obviously a lower primary temp will suffice if you are content with either a lower flow rate, lower temp or both.
Logged

changing the world, one roof at a time...

"We can't be B&Q astroturfers. That's one conspiracy theory too far. You should cut down on the pot." - Wookey