Paul
I have 4000 watt PV and two MPPT controllers and a 1 kw windturbine . The windturbine has basically no controller

anymore ( disconnected the dump for a reason) , cause the outback MPPT slows down in amps , when Wind picks up , so they basically think those Amps from the turbine are theirs

Surely , if you have 1000 watt connected directly to your battery , while the rest about 2800 watt is regulated and decreases to 0 AMP charge while battery gets stuffed , 1000 watt is still too much for a float charge , so some sort of regulator or dump would be ideal ( like the internal relay in the outback) or just a voltage sense relay that kicks in at say 30 volt and dumps say 300-500 watt
But read your Inverter manual , cause they(Studer ) have something as well
All the Best
Billi
7.5 AUXILIARY CONTACTS
The XTH, XTM and XTS, with TCM-01 and ARM-02 module, have two dry reversing contacts that are potential-free. The status of the contacts in deactivated mode is indicated by the annotations, N.C. = normally closed and N.O. = normally open. When the contact is activated
Maximum contact loads: 230 Vac / 24 Vdc: 16 A or: max. 50Vdc/ 3A
These dry contacts are programmed by default for the following functions:
Contact no. 1 (AUX 1): The contact has a function of automatic start of generator (two wires). The contact will be activated when the battery voltage is below a value, during a given time fixed by parameters {1247/48}/{1250/51}/{1253/54} The contact will be deactivated or when the charge cycle has reached floating {1516}, or when the "Aux. 1 deactivation voltage" {1255} is reached during a predetermined time {1256}
The voltage of the battery is automatically compensated according to the instantaneous battery current the same way as it is done for compensation of LVD (see sect. 7.3 – p.26) if parameter {1191} is activated.
Contact no. 2 (AUX2) : alarm contact by default. It is deactivated when the inverter is out of service or is working at reduced performance, either because of manual control or if there is an operational fault such as overload, under-voltage of the battery, over-temperature, etc.
If the operator or installer requires different behaviour for the auxiliary contacts, they are both freely and individually programmable depending on the battery voltage, the output power, the inverter status, the internal clock and the Battery state of charge (if BSP module is present) . These setting can be done with the the RCC-02/-03 (remote control unit)
The intelligent programming of the auxiliary contacts allows many applications to be considered such as:
Automatic startup of the generator (two or three wires)
Automatic load shedding of lower priority loads of the inverter (2 sequences)
Global or individual alarm
Automatic disconnection (load shedding) of the source
For more information on the auxiliary contacts nr 1 and 2 programming, do refer to our application notes available on Studer web site
www.studer-innotec.com. Like:
AN003: Anti-blackout system for grid connected application (Solsafe)
AN005: Automatic management of 2 different energy sources
"AN007 Automatic start of a generator" available on our website www.