Hi David - welcome to the fun!
Why would you opt for a gravity fed solar loop? The pressurised loop is far simpler and removes the potential pitfalls of having a low-head gravity fed circuit.
You will need sufficient tank height above the height of the manifold to create a head pressure on the solar system - if not, removal of air (and possible airlocks on filling) will be a potential issue. Arguably, by the time you have installed a header tank, overflow pipe, mains feed, lagging jacket, built a platform for the tank to sit on etc, the £65 pressure kit will seem like a bargain

Due to the low water content in the solar loop, unsuitable placement of conventional feed and expansion pipes could cause problems such as tank pump-over, sucking in air etc.
It would be interesting to hear other comments / opinions but:
I would use 15mm pipe to feed the solar loop from the tank, tee'd in
below the pump and one-way anti-syphon valve in the Return pipe. Even if you use 10mm pipe for the solar loop itself, you must feed from 15mm otherwise filiing could be a problem with low head to the manifold. This will allow the loop to fill from the bottom up. Also ensure that the fill pipe from the tank has a general upward slope i.e. no horizontal runs to prevent airlocking.
Do
not fit an isolating valve in the tank feed pipe.
I would not bother with an expansion pipe as per gravity CH systems - the tank feed pipe will perform both roles - but fit a pressure relief valve on the
flow pipe near the manifold.That way if the tank f/e pipe should ever block or freeze, the PRV will operate. The PRV can also be used to vent the circuit at the manifold if placed on a short rising pipe from the highest part of the manifold flow pipe.
You can pour an appropriate quantity anti-freeze/inhibitor into the tank during final system filling (after leak testing and flushing).
Regards
Antman