News: Anyone wishing to register as a new member on the forum is strongly recommended to use a "proper" email address - following recent spam/hack attempts on the forum, all security is set to "high", and "disposable" email addresses like Gmail, Yahoo and Hotmail tend to be viewed with suspicion, and the application rejected if there is any doubt whatsoever
 
Recent Articles: UPDATE ON DECC APPLICATION FOR LEAVE TO APPEAL TO THE SUPREME COURT | Yingli Green Energy's PV Module Ranks No.2 in TUV Rheinland Energy Yield Test | Navitron Solar Showers at Glastonbury for Year 5!
   Home   Help Search Login Register  
Pages: [1]   Go Down
  Print  
Author Topic: G83 changes?  (Read 801 times)
splyn
Jr. Member
**
Offline Offline

Posts: 61


« on: September 17, 2011, 05:39:23 AM »

Looking at the 'Distributed Generation Connection Guide' http://2010.energynetworks.org/storage/DGCG%20G83%20S1%20June2011.pdf

It says:

2. The generating unit has to be connected through an inverter (see note on next page)  that has been tested in accordance with one of the annexes in G83/1-1, e.g. Annex C for Photovoltaic generation*.

The note on the next page being:

*At the time of writing this alternative to making a G59/2 connection, whereby non type tested generation technology is connected via a type tested inverter under G83/1-1, is valid until the 2nd March 2012. Any connection proposed via route 2 after this date will need to be discussed with the DNO

So what is the significance of the 2/3/2012 date? Is it just some minor technicality wrt the legislation/documentation or is it potentially something more important?

Ta, Splyn

Logged
GavinA
Hero Member
*****
Offline Offline

Posts: 1190

Solar PV & water heating installer


WWW
« Reply #1 on: September 17, 2011, 04:50:20 PM »

I expect they'll tell us on about 1st March.
Logged

at home | 80 tubes, 2 tanks direct PV powered SWH + 5 x Yingli 185Wp solar PV panels.
ecogen
Jr. Member
**
Offline Offline

Posts: 75


Our friend electricity


« Reply #2 on: September 17, 2011, 05:16:36 PM »

DCRP GUIDANCE NOTE 2

03 March 2011 – valid until 02 March 2012
ENGINEERING RECOMMENDATIONS G83 AND G59
The Distribution Code Review Panel has reviewed the application of G83 and G59 for the cases of small
scale wind turbines.
G83 should apply to wind turbines of less than 16A per phase, and G59 to wind turbines of greater than
16A per phase. The Distribution Code Review Panel is aware that there is no formal annex for wind in
G83, but is also aware that the majority of small wind turbines in this size range are connected through
inverters that are type tested for the connexion of photovoltaic generation.
Until G59 was re-issued as G59/2 in August 2010 it was common practice for DNOs to connect small
scale wind turbines in accordance with G83.
Recognizing the efforts now being made by small wind turbine manufacturers and developers to establish
type tested designs for use in GB, both under G59 and G83, the Distribution Code Review Panel has
agreed that:
• For all small scale generating equipment of up to 16A per phase, it is permissible to connect to
the general requirements of G83 provided this is through an inverter that has been type tested in
accordance with G83 for another technology in G83, such as PV.
• For all small scale generating equipment of more than 16A per phase and up to 17kW
(50kW three phase) it is permissible to connect under the specific relaxation allowed in
Section 6.2 of G59 provided that both the connexion is through an inverter type tested in
accordance with G83 and the high frequency setting of the protection in the type tested
inverter is set to 51.5Hz with a time delay of no more than 0.5s. All other requirements
of G59 apply in full.
Note that although this issue was raised by installers of small scale wind, the guidance above is generic to
all technologies.
The interpretation of G83 and G59 in this Guidance Note is valid for applications or notifications made
up until 02 March 2012.