We are on grid but not selling our energy or claiming Feed In Tariffs.
We have PV and 3 windturbines (max 8KW) Hugh Piggott designs, and a 52.6v 660amp hour battery system, and a APC UPC (computer back up supply) 48v 3.7kw Inverter. Installing more, 3KW, PV - photo Voltaic panels.
Running the washing machine with our Inverter and batteries would within half an hour have the batteries down to shut down voltage.
I think biff's right regards having a Genny ready/on standby for that extra loading. Us, we then draw from the mains supply.
Battery choice is difficult and really will have to be your choice for what you actually want.
Quated to me, "Batteries are a Black Art".
(This could be read as teaching you to suck eggs, but I've written this for those who don't know, so please don't take offence.)Hi,
I think you have a serious problem with your system. You should not experience any issues running your washing machine from a system with the specifications yours is.
Your battery bank (48v, 660AH) stores 31.68kWh of energy. Let's assume that your washing machine draws the full 13 amps allowable from UK mains sockets and your inverter voltage is high at 240v, then your washing machine draws 240v * 13a = 3.12kW.
Lets assume your inverter is not very efficient - say 80%. The 3.12kW draw from the washing machine is presented as 3.12kW / 0.8 = 3.9kW to the batteries.
So multiply the power by the time to find the energy usage: 3.9kW * 0.5 Hours = 1.95kWh.
1.95Kwh / 31.68kWh = 6.2% of capacity used.
If you prefer to work direct in Amp-Hours...
3.9kW / 48v = 81.25 amps drawn from the battery.
Multiply current by time = 81.25 * 0.5 hours = 40.625Ah.
40.625Ah / 60Ah = 6.2%.
Of course this is a worse case scenario as the machine will not be running the heaters all the time, and your inverter is likely much more efficient and set to 230v...
I can see the following scenarios why you inverter is cutting out:
1. Your batteries are shot and the voltage really is collapsing to the cut off voltage of the inverter.
2. Your inverter is struggling to power the load and is thermally limited, thus shutting off for a safety reason to prevent damage / fire.
3. Your inverter (Computer UPS manufactured by American Power Conversion) is not of the "XL" product line and is shutting down prematurely due to its internal assumptions about the battery state.
4. Your inverter (Computer UPS manufactured by American Power Conversion) is of the "XL" product line, but is mis-configured and is shutting down prematurely due to its internal assumptions about the battery state.
Item #1 is easy to diagnose and will require new batteries if this is the issue.
Item #2 could be resolved by increasing the air flow and lowering the ambient temperature - I hope it is not operating in a small cupboard or shed in which the air temperature can rise. UPS are designed to be run in air conditioned data centres at a constant 21'C.
Item 3# cannot be resolved so easily. A UPS must provide power to the load for as long as it can, however it must ensure that in the event of the mains power not being restored that all connected computers etc receive a shut down signal in a timely manner, so that there must be sufficient battery time left for the machines to perform the shut-down process. In heavily loaded server environments this can be quite a few minutes. In order to do this the UPS knows the capacity (in watt hours) of the battery that the UPS was fitted with at the factory, and it can measure the connected load. The UPS can then estimate the battery state and time the shut-down sequence accordingly. The UPS will prevent excessive discharge of the battery in order to maintain the quality of the system - no point having a UPS that is unreliable! If you have added external batteries to a standard UPS, it will be under estimating the size of the battery, and timing everything too early.
Item 4#: The XL versions allow additional external battery packs to be attached. The UPS in this case needs to be informed how many external battery packs are installed so it can perform the functions outlined above, otherwise you shall experience the same issues of premature shut-down. To configure the number of external battery packs you need to use the APC UPS management software. Unfortunately APC do not specify their battery packs in terms of voltage and Amp-Hour, but you can work them out with a little Googling. You shall need to select the number of APC batteries that is the closest match for your bank.
Hope this helps
-Tim