I would say Sam is right, the latest UK heat pump MCS standards MCS3005v3 www.microgenerationcertification.org/installers/installers ( thanks to jonG for the link) also say between .8 and 1.2M. Any ground freezing problems at these depths is going to be due to undersized loops.
In 1980īs we also buried ground loops too deep. That caused lot of problems, which almost stopped GSHP installations for decade. Iīm glad that UK is also jumped to this century.
There is absolutely no reason to dig it any deeper than 70cm in UK. Another important thing is that forget slinkies (and other voodoo-snakes). Use 32mm or 40mm 10bar pipe for ground loops.
Space between pipes should be around 1-1,5 meter. More is better, if you have space.
Big question is how long ground loop you need? That depends how much your house consume energy. There is some thumb rules:
- Donīt go under 300m. Reason is that plastic pipe is good insulation and when GSHP is running, heat needs some time to transfer from soil to fluid inside the pipe.
- Donīt go over 450m loops. If you need more, just connect more loops to parallel. We try to keep flow turbulent (
http://en.wikipedia.org/wiki/Turbulent ) and not stress ground loop pump. Way better is 2x250m loops, than 1x500m loop.
- We get in Southern part of Finland max. 60kWh/meter from ground loop if soil is clay.
Example: You have house with radiators, which need 21000 kWh/year for heating and warm water. You need 7000kWh from grig to GSHP and you get 14000kWh from ground. Your ground is not clay, so letīs estimate: 40kWh/meter.
14000kWh/40kWh = 350m loop 40mm/10bar pipe with 1-1,5m space.
Same consumption with underfloor heating stress ground loop more, so you need 5250 kWh from grid and 15750 kWh from ground. 15750/40 = 393 meter ground loop.
My advice for choosing GSHP:
- Buy Nibe, Thermia etc. Swedish GSHP. Sweden have over 500 000 GSHP installed, so they know how to build one. Here you pay 6-8kW:n GSHP with 180l hot water tank around 5000-6000.
If you are thinking about COP in GSHP we have some fresh measurements from year 2010 Nibe 6kW here in Finland (112m2, floorheating, 140m borehole, 125m in bedrock):
Power from grid: 1,43kW
Flow to UFH: 0,669 m3 Power to UFH: 6,39 kW
COP 4,47Flow to UFH: 0,743 m3 Power to UFH: 7,10 kW
COP 4,97 Temp to UFH: +35,3°C
Temp return from UFH: +27,1°C
Groundfluid in to GSHP: +2,1°C
Groundfluid back to borehole: -0,9°C
COP will go down from these numbers, but we hope that year-COP 3.5 is achieved.As you may know, you get 3-4% better COP in every degree what you can rise ground fluid temperature or reduce your temperature to radiators.
5 degree from ground 30 degree to radiators equals to 10 degree from ground 35 degree to radiators. You get pretty good benefit from boosting your radiators with fans ( poor example
http://www.radiatorbooster.com/ )
In UK you get year-COP 3 easily with radiator (max. 50 degree water to radiators) and year-COP 4 in UFH (max. 35 degree to floor).
That means you buy 4 kilowatts at price of one including all domestic hot water.
Hope this helps.
Merry Christmas, Sami