News: Anyone wishing to register as a new member on the forum is strongly recommended to use a "proper" email address - following recent spam/hack attempts on the forum, all security is set to "high", and "disposable" email addresses like Gmail, Yahoo and Hotmail tend to be viewed with suspicion, and the application rejected if there is any doubt whatsoever
 
Recent Articles: UPDATE ON DECC APPLICATION FOR LEAVE TO APPEAL TO THE SUPREME COURT | Yingli Green Energy's PV Module Ranks No.2 in TUV Rheinland Energy Yield Test | Navitron Solar Showers at Glastonbury for Year 5!
   Home   Help Search Login Register  
Pages: [1]   Go Down
  Print  
Author Topic: Please could someone check my calculations...  (Read 551 times)
acresswell
Full Member
***
Offline Offline

Posts: 189


WWW
« on: November 06, 2011, 05:56:36 AM »

I'd really appreciate it if someone could check my calculations and assumptions...  I've set up the attached spreadsheet (which I've converted to open document format) to help with sizing a log gasification boiler top cope in the depths of winter.

The structure of the building is now fixed, so the only variables are the internal and external temperatures, occupancy and water use. The outputs I'm interested in are how many times each day I'd have to load the boiler in particularly poor weather (-5degrees C average temp).  I'm trying to decide between the 25kW boiler and the 40kW boiler.  Either of them has plenty of output overall, but the 40kW boiler has a bigger loading chamber, so would need loading less often.

The boiler itself will be outside the main thermal envelope (in a space that is separately insulated to keep it frost-free).
The thermal store will be inside the main envelope (which is why I haven't included heat losses from there in the main calculation... any heat lost from the thermal store will just reduce the demand on the UFH)
We're fitting a MVHR system - stated efficiency is over 90% but I never believe manufacturers figures, which is why I've reduced it to 70%.
We're fitting solar thermal panels, but this "midwinter" scenario assumes that the solar thermal isn't making any noticeable contribution.
If the average temperature dropped below -5 degrees C, we could allow the internal temperature to drop a little, light the woodburner in the evenings, or resort to using an electric heater.  I've ignored the contribution of our metabolic heat to allow for weeks when we are at work all day, but the dogs need to stay warm.
The house will have a fairly high thermal mass, so varying the temps sigificantly at different times of day is unlikely to make a big difference, though we'd certainly try it if necessary.

Have I missed anything obvious (or important but not obvious?)

Thanks for your help

* boiler sizing.ods (6.08 KB - downloaded 33 times.)
Logged

Building a new home in North Worcestershire
 see http://ecobodger.wordpress.com
rondurrans
Hero Member
*****
Offline Offline

Posts: 700



WWW
« Reply #1 on: November 06, 2011, 06:56:15 AM »

acresswell is the floor area only 107 m2?
Logged

4 kW PV Array on the North Wales Coast - http://energy1.moonfruit.com/
'Nullius in verba' & 'Nothing Endures but Change' (Heraclitus)
acresswell
Full Member
***
Offline Offline

Posts: 189


WWW
« Reply #2 on: November 06, 2011, 03:41:20 PM »

Thank you... you're right.   Big gold star to rondurrans!

The ground floor is 137m2. Typing error, I'm afraid   surrender.
The total floor area is double the ground floor.  New version of spreadsheet attached. I've double-checked the other sizes and they're correct.


* boiler sizing.ods (6.06 KB - downloaded 20 times.)
Logged

Building a new home in North Worcestershire
 see http://ecobodger.wordpress.com
KLD
Hero Member
*****
Offline Offline

Posts: 1340


« Reply #3 on: November 06, 2011, 04:59:57 PM »

Hm, only looking at the bottom line, I'm surprised by the total amount of heat you seem to require. This is for a new-build house, isn't it? Just for comparison, we live in an 1850th Cotswold stone cottage, some added improvements, but no major changes to the old centre of the cottage. Our daily heating rate is about 3kWh per deg C. So, for 20°C in- and -5°C outside, that's 75kWh a day.

Klaus
Logged
acresswell
Full Member
***
Offline Offline

Posts: 189


WWW
« Reply #4 on: November 07, 2011, 07:10:47 AM »

Klaus,

Does your 3kW per deg C include water heating?

Thanks
Logged

Building a new home in North Worcestershire
 see http://ecobodger.wordpress.com
rondurrans
Hero Member
*****
Offline Offline

Posts: 700



WWW
« Reply #5 on: November 07, 2011, 07:52:40 AM »

I think there is a problem with the calc in cell N11 - you will not require that amount of kWh for 365 days year; my 205m2 1960's house uses approx. 120 kWh per square meter for heating and DHW annually.

Try:

http://www.idhee.org.uk/calculator.html

http://www.retscreen.net/ang/home.php

Laughton, C. (2006) Home Heating with Wood. Aberystwyth: Cambrian
‘Rule of thumb’ volume to be heated divided by 34 (Laughton, 2006)
Peak boiler size ‘rule of thumb’ volume divided by 32 (Laughton, 2006)
 
« Last Edit: November 07, 2011, 08:21:27 AM by rondurrans » Logged

4 kW PV Array on the North Wales Coast - http://energy1.moonfruit.com/
'Nullius in verba' & 'Nothing Endures but Change' (Heraclitus)
KLD
Hero Member
*****
Offline Offline

Posts: 1340


« Reply #6 on: November 07, 2011, 09:13:25 AM »

Klaus,

Does your 3kW per deg C include water heating?

Thanks
Yes, that is all inclusive, daily consumption figures measured for several years. See attached plot. For lower temp differences you'll see more scattering in the data, since both DHW and solar input for DHW make a higher contribution. There's hardly any solar input in winter, so don't worry about that effect here.

But please do note the units: this is 3kWh per day per degree Celsius.

Klaus


* Untitled 1.jpg (22.22 KB, 794x194 - viewed 69 times.)