« on: November 24, 2011, 10:57:07 PM » |
|
Hi I need to put one or more Blocking Diodes in between the Battery and my windturbine so no power can flow towards the turbine and its dump So am i right that the diode is placed just in line with the positive wire ? and the threaded connection faces towards battery  Problem is my wire is 70 mm2  and that tiny diode a bit small , but i could use 3 or 4 in parallel and connect to a bus bar to achieve a biger diameter at the connection Any ideas Thanks Billi
|
|
|
|
« Last Edit: November 25, 2011, 09:47:16 AM by billi »
|
Logged
|
Guinness no Grid comes near
1.6 kw and 2.4 kw PV array , Outback MX 60 and FM80 charge controller ,24 volt 1600 AH Battery ,6 Kw Victron inverter charger, 1.1 kw high head hydro turbine as a back up generator , 5 kw woodburner, 36 solar tubes with 360 l water tank, 1.6 kw windturbine
|
|
|
|
johnrae
|
 |
« Reply #1 on: November 25, 2011, 12:17:03 AM » |
|
Ideally you should have provided the part number but I can just see the symbol which suggests the cathode is the screwed stud. However I do not fully understand what you mean when you say battery power goes towards the turbine and its dump.
Could you perhaps provide a sketch of your intent so's a definitive (and hopefully correct) answer can be given.
|
|
|
|
|
Logged
|
|
|
|
|
billi
|
 |
« Reply #2 on: November 25, 2011, 12:27:10 AM » |
|
Thanks John
My turbines controller has a dumpelement connected that starts dumping at say 29 volt ,
Also there are 4 kw of PV but much better controllers that charge with temperatur sensors and reach charge voltage upto 31 Volt
I do not want to allow that power from the PV is dumped there at 29 volt as well at the turbines controller and burn out the 2 kw dumpelement
So thats why the diodes
Thanks Billi
|
|
|
|
|
Logged
|
Guinness no Grid comes near
1.6 kw and 2.4 kw PV array , Outback MX 60 and FM80 charge controller ,24 volt 1600 AH Battery ,6 Kw Victron inverter charger, 1.1 kw high head hydro turbine as a back up generator , 5 kw woodburner, 36 solar tubes with 360 l water tank, 1.6 kw windturbine
|
|
|
|
johnrae
|
 |
« Reply #3 on: November 25, 2011, 12:36:10 AM » |
|
Remember that you will lose about 0.7 volts across the diodes so you need to account for that when setting up your turbine charge controller ie battery + 0.7 volts
|
|
|
|
|
Logged
|
|
|
|
|
Antman
|
 |
« Reply #4 on: November 25, 2011, 07:45:23 AM » |
|
Billi
In the diode shown, current will flow from the tag (top right) to the stud (nut) end and johnrae has said.
I am also slightly confused but I think it may result from a typo in the original post.
Did you mean "...so now power power can flow towards the turbine and its dump" or "...so no current can flow towards the turbine and its dump" ? I suspect that the "w" makes a difference which way round the diode is fitted.
I admit to not being involved in wind power but my observation/question would be that if you have two charge sources, one at 29V the other 31V, the 31V will always dominate. Thus the wind will not contibute anything if the PV is generating and holding the batteries at a higher voltage than the wind charge controller will allow. Also how doe the wind charge controller sense the battery voltage? It is possible that by blocking the battery with a diode you could also block the voltage sensing on the controller.
Ignore me if I have the wrong end of the stick!
Regards Antman
|
|
|
|
|
Logged
|
20 x 47mm, 172 litre cylinder, Heat Dump, 15 x Sanyo HIT-H250E, SB4000TL DIY Solar System Support at: http://homepage.ntlworld.com/anthony.cooper267/index.htmlAll support is wholly voluntary and free of charge. I'm not employed by Navitron and have a full-time job so responses may not be same-day
|
|
|
|
billi
|
 |
« Reply #5 on: November 25, 2011, 09:43:16 AM » |
|
Hi Antman you are right " no Power can flow to the turbine " is the idea I admit to not being involved in wind power but my observation/question would be that if you have two charge sources, one at 29V the other 31V, the 31V will always dominate. Thus the wind will not contibute anything if the PV is generating and holding the batteries at a higher voltage than the wind charge controller will allow. I do not use the dump element at the wind turbine , because of this reason Antman I have a AC heater that i use and is switched on by my inverter at say 30 Volt and Wind is then dumped in my house, as well as some PV and this holds the Windturbine as well But now i would like to run a GTI (MPPT range 10.5-30 Volt )in parallel with my charge controller to hopefully increase the performance of the turbine in low wind . And feed that AC 230 Volt into my house directly But i need that Diode that the GTI is not feed from the Battery , but the battery clamps the voltage range down to a secure range for the GTI Something like this here in the drawing ....   Hope this make sense 
|
|
|
|
« Last Edit: November 25, 2011, 10:04:31 AM by billi »
|
Logged
|
Guinness no Grid comes near
1.6 kw and 2.4 kw PV array , Outback MX 60 and FM80 charge controller ,24 volt 1600 AH Battery ,6 Kw Victron inverter charger, 1.1 kw high head hydro turbine as a back up generator , 5 kw woodburner, 36 solar tubes with 360 l water tank, 1.6 kw windturbine
|
|
|
|
Antman
|
 |
« Reply #6 on: November 26, 2011, 04:41:18 PM » |
|
Hi Billi
In the second diagram, the 'triangle' is representing the diode (I assume). Normally the 'point' of the triangle would be the direction of current flow. But confusingly, the arrows point in the opposite direction. This may be contributing to the confusion and hence the lack of knowledgeable replies - hence why I will bump it again.
In a diode - approximate symbol below but drawing with text characters is not easy so allow some imagination and assume the arrow is formed with the ">" being a steeper angle!....
|\ | -------| >|------- |/ | Anode Cathode
Current flows this way >>>>>>>>>> So any voltage applied to the cathode will not appear at the anode terminal.
Hence the confusion in the second drawing.
If I am correct in assuming that you want the wind turbine to charge the batteries but not to be affected by the PV charge controller, then the cathode (arrow tip) of the diode needs to connect to the battery and the anode to the wind turbine busbar. The first drawing is correct in this respect.
But in doing this, I suspect that the wind turbine will no longer contribute to the battery charging when the solar PV is generating because the 30+ volts across the batteries will reverse bias the diode - meaning it cannot conduct with only 29V coming from the wind genny. So presumably the wind dump load would then have to absorb the entire wind turbine output.
As for connecting the diode, I would parallel 2-3 (depends on rating of what you have) so that the total diode continuous current rating is double your peak wind turbine current (for reliability). Mount copper busbars on insulators and connect the diodes to those so that you also have a stout connection for the cable lugs to bolt onto.
Antman
|
|
|
|
|
Logged
|
20 x 47mm, 172 litre cylinder, Heat Dump, 15 x Sanyo HIT-H250E, SB4000TL DIY Solar System Support at: http://homepage.ntlworld.com/anthony.cooper267/index.htmlAll support is wholly voluntary and free of charge. I'm not employed by Navitron and have a full-time job so responses may not be same-day
|
|
|
|
billi
|
 |
« Reply #7 on: November 26, 2011, 05:25:13 PM » |
|
Thank you Antman But in doing this, I suspect that the wind turbine will no longer contribute to the battery charging when the solar PV is generating because the 30+ volts across the batteries will reverse bias the diode - meaning it cannot conduct with only 29V coming from the wind genny. So presumably the wind dump load would then have to absorb the entire wind turbine output.
As for connecting the diode, I would parallel 2-3 (depends on rating of what you have) so that the total diode continuous current rating is double your peak wind turbine current (for reliability). Mount copper busbars on insulators and connect the diodes to those so that you also have a stout connection for the cable lugs to bolt onto.
Antman Yeah , i am aware that the dump of the turbine has to take the power when voltage higher than ca 29 V , but have other ideas as well Will built a busbar for the diodes Thanks
|
|
|
|
|
Logged
|
Guinness no Grid comes near
1.6 kw and 2.4 kw PV array , Outback MX 60 and FM80 charge controller ,24 volt 1600 AH Battery ,6 Kw Victron inverter charger, 1.1 kw high head hydro turbine as a back up generator , 5 kw woodburner, 36 solar tubes with 360 l water tank, 1.6 kw windturbine
|
|
|
|
johnrae
|
 |
« Reply #8 on: November 26, 2011, 07:20:40 PM » |
|
You might also want to consider a charge controller between the turbine and the battery to prevent the possibility of over-charging when it's blowing a 'howler'
|
|
|
|
« Last Edit: November 26, 2011, 07:24:20 PM by johnrae »
|
Logged
|
|
|
|
JohnH
Jr. Member

Offline
Posts: 61
|
 |
« Reply #9 on: December 01, 2011, 11:19:31 AM » |
|
Hi Billi
The diode you have, did this come with the system? I ask because looking at the type letters it looks like a Schottky diode. They have a low forward voltage drop at about 0.2V and hence are used mainly for high speed switching. Their disadvantage is that they have a relatively low reverse voltage and high leakage current. I don't know if it would be suitable for your application.
JohnH
|
|
|
|
|
Logged
|
|
|
|
|
billi
|
 |
« Reply #10 on: December 01, 2011, 11:26:03 AM » |
|
Hi John
No i have not got the Diodes yet . Do you have a better model ?
|
|
|
|
|
Logged
|
Guinness no Grid comes near
1.6 kw and 2.4 kw PV array , Outback MX 60 and FM80 charge controller ,24 volt 1600 AH Battery ,6 Kw Victron inverter charger, 1.1 kw high head hydro turbine as a back up generator , 5 kw woodburner, 36 solar tubes with 360 l water tank, 1.6 kw windturbine
|
|
|
JohnH
Jr. Member

Offline
Posts: 61
|
 |
« Reply #11 on: December 01, 2011, 01:32:11 PM » |
|
Billi I would have thought a standard high current metal stud diode would suffice mounted on a heat sink with mica insulators if needed. Depending on the max forward current, the 25F10, 40HF10 or 70HF10 series diodes which are available from Farnell. JohnH
|
|
|
|
|
Logged
|
|
|
|
fred bloggs
Jr. Member

Offline
Posts: 59
|
 |
« Reply #12 on: December 01, 2011, 02:43:43 PM » |
|
Billi
I have dozens of Industrial Stud diodes upto 300Amps rating, all gathering dust, therefore if you want a couple of them, PM me and I'll shove them in the post (my good deed for the week-FOC). Tell me the maximum rating (current) you are looking for.
Best Regards
Fred
|
|
|
|
|
Logged
|
|
|
|
|
billi
|
 |
« Reply #13 on: December 01, 2011, 04:37:15 PM » |
|
Oh  santa is coming will PM you
|
|
|
|
|
Logged
|
Guinness no Grid comes near
1.6 kw and 2.4 kw PV array , Outback MX 60 and FM80 charge controller ,24 volt 1600 AH Battery ,6 Kw Victron inverter charger, 1.1 kw high head hydro turbine as a back up generator , 5 kw woodburner, 36 solar tubes with 360 l water tank, 1.6 kw windturbine
|
|
|
fred bloggs
Jr. Member

Offline
Posts: 59
|
 |
« Reply #14 on: December 02, 2011, 11:55:41 AM » |
|
Hi Billi  is on its way as per your PM. Best Regards Fred
|
|
|
|
|