Hi Boris
To control my excess energy during the summer, I have used Antmans solution where once the store reaches 65C, relay 2 on the Re-sol controller operates a relay that does 3 functions
First it operate the CH pump, then it sets the 3 way DHW / CH diverter valve to mid position, and finally it inhibits the boiler firing so basically the boiler coil removes the excess from the store and dumps it into the rads around the house.
I only installed the system myself late this year (Early September) so I shall see how the system performs in 2012, (Even this year during that week in late september when we had 5 days of lovely sunshine the system performed really well and the boiler did not come on at all to heat the DHW) and if necessary if the house becomes too warm, I have as plan B, a two position diverter valve already fitted in the solar circuit so if necessary I can add an external heat exchanger to dump the excess to the outside.
Lastly the reason for going for a 25 58 tube collector to a 150l store was that due to the position on the garage roof, As I have a PV array on the main room I have a shading issue.
See
http://www.navitron.org.uk/forum/index.php/topic,15186.msg170073.html#msg170073So from around 2.30 mid summer, the collector starts to become shaded and is fully shaded by around 6.00, so I went for an oversize collector to collect as much thermal heat as possible from sunrise to around 2.30 then the system will start to collect less from this time onwards
See
http://www.navitron.org.uk/forum/index.php/topic,14405.msg161451.html#msg161451for more on my shading issue
Interestingly in the winter on sunny day the shading issue is far less and the panel is fully exposed to around 4.00 due to the sun being lower in the sky.
Best and kindest regards Al.