These type of statements from 'knowledgeable' people only serve to confuse readers who don't have a full understanding of the technicalities.
dominator99 - you are guilty of the very crime you are trying to expose.
CT's pick up the weak alternating magnetic field surrounding the conductor induced by the current flow. That is used to generate an alternating voltage that is proportional to the current flow. With two conductors, if the AC in both is in phase, then the magnetic field will be doubled. If the AC in each is 180deg out of phase, the net magnetic field will be (almost) zero (or cancelled). (assuming equal absolute current flow in each case)
CT's
are sensitve to the direction of current flow, the voltage waveform they produce could be used to calculate the direction of the instantaneous current flow. More importantly, however, they are not sensitive to power flow - for that you need to know the relative phases of both current and voltage.
In a power monitor, the electronics take the output of the CT which is a voltage waveform proportional to current flow, integrate over time to produce a current consumption, then assume a 240V voltage, and produce a power figure. They do not attempt to indicate direction of power flow - I agree they are incapable of doing that from just the CT output.
Hopefully I haven't confused anybody, and am happy to be corrected if I've misunderstood anything.