News: Anyone wishing to register as a new member on the forum is strongly recommended to use a "proper" email address - following recent spam/hack attempts on the forum, all security is set to "high", and "disposable" email addresses like Gmail, Yahoo and Hotmail tend to be viewed with suspicion, and the application rejected if there is any doubt whatsoever
 
Recent Articles: UPDATE ON DECC APPLICATION FOR LEAVE TO APPEAL TO THE SUPREME COURT | Yingli Green Energy's PV Module Ranks No.2 in TUV Rheinland Energy Yield Test | Navitron Solar Showers at Glastonbury for Year 5!
   Home   Help Search Login Register  
Pages: [1]   Go Down
  Print  
Author Topic: G83/2 question - 50kW PV installation  (Read 898 times)
Ivan
Administrator
Hero Member
*****
Offline Offline

Posts: 1221


« on: November 30, 2011, 08:58:09 PM »

Does the DNO have to witness switch-on for a 50kW installation under G83/2. I'm working on a couple of projects where the DNO engineer has been quite helpful and has volunteered his services to witness switch-on (at considerable cost) - is this necessary, or at DNO's discretion, or is this optional from my point of view?
Logged

Navitron Member of Staff
www.epogee.co.uk - Solar PV & Solar Thermal Training / MCS
guydewdney
Hero Member
*****
Offline Offline

Posts: 3124



WWW
« Reply #1 on: November 30, 2011, 09:04:01 PM »

dont you mean G59?
Logged

Lynch Mill wedding venue www.lynchmill.co.uk
Pic of wheel on day 1
7.2kW Waterwheel and 9.8kW PV
GavinA
Hero Member
*****
Offline Offline

Posts: 1190

Solar PV & water heating installer


WWW
« Reply #2 on: November 30, 2011, 09:11:41 PM »

Does the DNO have to witness switch-on for a 50kW installation under G83/2. I'm working on a couple of projects where the DNO engineer has been quite helpful and has volunteered his services to witness switch-on (at considerable cost) - is this necessary, or at DNO's discretion, or is this optional from my point of view?
discretionary, type tested kit should be acceptable. If none type tested and you've no experience testing the protection settings then getting an expert such as the guys from G59 testing.co.uk (erm I think) to do the testing for you could be more cost effective and the DNO should accept that without needing to witness it, unless you're really confident in what you're testing for.

On the other hand, having a friendly dno engineer might be worth the cost in the long run.
Logged

at home | 80 tubes, 2 tanks direct PV powered SWH + 5 x Yingli 185Wp solar PV panels.
Ivan
Administrator
Hero Member
*****
Offline Offline

Posts: 1221


« Reply #3 on: November 30, 2011, 10:41:43 PM »

Guy, there is a concession for installations above 16A per phase but under 74A (ie 50kW into 3phase) where you are allowed to certify under G83 with a few minor changes to the settings of the inverters.

Gavin, The installation is 3 x SunnyBoy Tripower 17000s which have g59 certificate (for what it's worth). Does it therefore need testing of any sort? If these are G59, do they still need their settings altered? What would you suggest?
Logged

Navitron Member of Staff
www.epogee.co.uk - Solar PV & Solar Thermal Training / MCS
GavinA
Hero Member
*****
Offline Offline

Posts: 1190

Solar PV & water heating installer


WWW
« Reply #4 on: November 30, 2011, 11:48:43 PM »

Just tell them they're type tested to G59 protection settings SMA inverters, and you have no intention of conducting further tests of the protection settings so there's nothing to be witnessed beyond the standard ac and dc insulation resistance tests etc.

slight fly in the ointment would be if they actually wanted you to use the G83 settings with just one part adjusted, as has been the case with some G83/1/2 applications. I'm not entirely clear whether this would require a new test certificate for the new settings, or if it would be covered under the original type test cert, but as it was agreed to be done as a stop gap measure to ease the process, I can't see the logic in requiring a seperate test.

I do think the witnessing is a discretionary thing still though, so the DNO could probably insist on it, but I'm not 100% on this - I think it's in either the G59 guidance or possibly the more detailed version in a table, and it varies with the system's size. type tested g59 inverters weren't an option for what I was looking at when we went through this, so I'm not 100% sure what the situation is. Not really my speciality tbh.
Logged

at home | 80 tubes, 2 tanks direct PV powered SWH + 5 x Yingli 185Wp solar PV panels.
Other-Power
Sr. Member
****
Offline Offline

Posts: 366


« Reply #5 on: December 04, 2011, 09:08:49 PM »

In my experience, G83 stage 2 means log in with grid gaurd and change over frequency to 51.5 Hz.  Commision the install and tell your DNO what you have done.

G59 is a lot more work your DNO could/probably will ask for a representative to come and check the settings and this costs a lot, I would push to connect under G83 stage 2.

Cheers

Jon

Logged