« on: December 09, 2011, 08:25:52 PM » |
|
I am trying to choose the correct equiptment to power my liveaboard barge by solar energy I have little experience with this equiptment and find the range of equiptment avalible a minefield as of now I am planning to install 3No. 24v x 250w Sanyo panels wita a TriStar MPPT 45 controller and a MorningStar TS-RM-2 remote panel Is the above equiptment good quality, has anyone experience with it ? The system will be used to charge two large truck batteries and power the domestic usage onboard Donal
|
|
|
|
|
Logged
|
|
|
|
|
rogeriko
|
 |
« Reply #1 on: December 09, 2011, 08:58:19 PM » |
|
Sanyo panels are not designed for battery charging. Sanyo panels are expensive. MPPT chargers are expensive.
You would be better off buying twice as many normal 29 volt 8 amp chinese panels and a simple charge controller and you would still have money left over for a lot of beers.
3 sanyo panels might give you enough for 1 light bulb. 6 eight amp chinese panels will give you plenty of power, thats all I have and I am off grid. Welcome to the forum
|
|
|
|
|
Logged
|
|
|
|
|
billi
|
 |
« Reply #2 on: December 09, 2011, 11:51:29 PM » |
|
Hi
It is not very clear to me .... are you thinking of 12 or 24 volt ?
|
|
|
|
|
Logged
|
Guinness no Grid comes near
1.6 kw and 2.4 kw PV array , Outback MX 60 and FM80 charge controller ,24 volt 1600 AH Battery ,6 Kw Victron inverter charger, 1.1 kw high head hydro turbine as a back up generator , 5 kw woodburner, 36 solar tubes with 360 l water tank, 1.6 kw windturbine
|
|
|
MrPugs
Newbie
Offline
Posts: 8
|
 |
« Reply #3 on: December 10, 2011, 07:51:14 AM » |
|
The barge is wired for 12v, so it will have to be 12v
|
|
|
|
|
Logged
|
|
|
|
|
martin
|
 |
« Reply #4 on: December 10, 2011, 09:00:11 AM » |
|
Well, there's nothing actually wrong with a 12v system, it's just that many people opt for a higher voltage as the wiring can be lighter gauge - I'd suggest that a mix of 12v and "mains" from an inverter will probably do everything you need. I certainly concur with the comments about panel choice, and going by "what would I do in your shoes", I'd probably opt for some of the "house brand" Yingli panels that are made specifically for charging batteries - I've had some for a few years, they perform very well, and are built like the proverbial brick outhouse - http://www.navitron.org.uk/product.php?proID=133 - the "new" controllers are also worth a look - http://www.navitron.org.uk/product_detail.php?proID=662&catID=127 - you could have 2 or three of them for a large array. The best thing for a system like this is to "start backwards" and firstly work out your likely power consumption (having minimised consumption as far as possible), then size your battery bank and panellage to provide what you need - there's several posts where people have discussed this sort of thing before - I'm sure there's several of us happy to help you too - as every "off-gridder" will tell you, battery choice is of prime importance, and you can rapidly end up with a pile of very dead and unrevivable ones if you get it wrong...
|
|
|
|
|
Logged
|
Unpaid volunteer administrator and moderator (not employed by Navitron) - Views expressed are my own - curmudgeonly babyboomer! - http://www.farmco.co.uk
|
|
|
|
billi
|
 |
« Reply #5 on: December 10, 2011, 09:20:18 AM » |
|
Hi
The morningstar MPPT is as far as i know a very good product , not sure if you need the remote panel , i think you can hook the controller to a laptop
A Outback FM 60 MPPT would be another good choice for the same price , but can handle 800 watt instead of the 600 watt from the morningstar + panel
Like the others said , i would not bother with overpriced PV, when one can get them for starting at 1 GBP per watt ( Navitron)
Roger might have thought you are on 24 Volt
Billi
|
|
|
|
|
Logged
|
Guinness no Grid comes near
1.6 kw and 2.4 kw PV array , Outback MX 60 and FM80 charge controller ,24 volt 1600 AH Battery ,6 Kw Victron inverter charger, 1.1 kw high head hydro turbine as a back up generator , 5 kw woodburner, 36 solar tubes with 360 l water tank, 1.6 kw windturbine
|
|
|
|
rogeriko
|
 |
« Reply #6 on: December 10, 2011, 09:41:03 AM » |
|
Indeed i presumed you would have a 24 volt system, its a lot easier at 24 volts. Cant you just change the bulbs to make a 24 volt system. What 12v equipment do you have?
|
|
|
|
|
Logged
|
|
|
|
MrPugs
Newbie
Offline
Posts: 8
|
 |
« Reply #7 on: December 10, 2011, 10:52:02 AM » |
|
The domestic supply was wired as 12v originaly by me as the starting system was 12v, It would not be a big problim to change
The present AC setup is
1. Shore power through a 4kva isolation transformer 2. 8kva diesel generator
These are wired through a change over switch to a standard domestic distrubution board The nuetral from the transformer and the generator are bonded to the steel hull in one location as are the negatives of the batterys
Todate I have got along fine with shore power and the generator
The DC setup consists of
1. one truck battery for starting the main engine, which is charged by an altonator on the engine 2. one car battery for starting the generator, which is charged by an altonator on the generator 3. Two truck batteries for the domestic supply, which are charged by a standard 220v battery charger that is connected continiously and charges the batteries once there is 220v on the system
The DC load is only lights, radio, navigation equiptment and phone chargers The AC load is battery charging, oil fired boiler and circulating pump, lights, microwave oven, 2 induction hobs, kettle, toaster,tv, laptop When running off shore power the usage is around 6-8kwh per day (metered and paid for by smart card daily)
My intention is to make the vessel self-sufficent for power as much as possible hence the wish to add a PV source
My background is electrical but I have little experience of the PV and am finding it hard to chose the correct kit
So if I take the demand as 8kwh per day with out having made any attempt to reduce the load. What would be a good system to install ? Would a wind generator be of use in the winter ?
Many thanks for the interist and replies
Donal
|
|
|
|
|
Logged
|
|
|
|
|
Billy
|
 |
« Reply #8 on: December 10, 2011, 11:24:19 AM » |
|
Hi Donal You might find (as we did) that wind is very noisy. We have a Navitron 300 which is brill but the resonance in the cabin was such that we had to walk around in ear defenders which didn't please Mrs B. There was no noise outside with the quiet blades on. Ones with a metre blade diameter or so with some good isolation mounts are ok on board. The Navi 300 resides on a land mounted pole now. We get good wind but location is the key so check before shelling out loads of dosh for something that not going to give you very much. I struggle to get below 5 units a day. All the lights are led or low energy, heating is non electric gravity system so no pumps. We have all the normal domestic stuff, TV, PC, WM, DW etc. We have a mix of 240v via inverter and 24v, 12v comes from a 10 amp dropper but doesn't get used much. We have a 24v diesel charging plant rather than a 240v genny. Hot water comes from EV tubes mounted on a turntable so they face the sun when we move. Woodburner is teed into the central heating and tops up the hot water in winter. PV is my next project but space and wave/salt water (and money) may prove a problem.  billy 
|
|
|
|
|
Logged
|
Navitron 24vx300watt windy thing, 20x47mm toobs,24v Rolls @458ah C5, Victron MultiPlus 3kw inverter/charger, WBS with boiler.
|
|
|
MrPugs
Newbie
Offline
Posts: 8
|
 |
« Reply #9 on: December 10, 2011, 06:16:02 PM » |
|
Rodgeriko: You would be better off buying twice as many normal 29 volt 8 amp chinese panels and a simple charge controller and you would still have money left over for a lot of beers. 3 sanyo panels might give you enough for 1 light bulb. 6 eight amp chinese panels will give you plenty of power, thats all I have and I am off grid. Welcome to the forum
Hi Rodger If I convert the barge to 24v could you let me know the panel and controller type that you installed
Hi Billy It is good to hear from another boat man, interisting your experience onboard with the noise level from a wind turbine What type of solar heating did you install on your vessel
Based on a demand of 8kwh per day what size/type of battery bank should I install
Regards Donal
|
|
|
|
|
Logged
|
|
|
|
|
|
|
billi
|
 |
« Reply #11 on: December 10, 2011, 09:56:34 PM » |
|
Roger , just a question ,in hot climates like Greece , when Panels (30 volt ) get realy hot , the voltage will drop significantly, even lower then to get the 24 volt battery fully charged Is that not a problem ? It you see this happening ? Donal we have 4 kw PV and similar consumption as you ( about 8 kwh) , surely too much in summer , but it helps in winter as well , so about 8-9 month 100 % PV power in our house and the rest of the time the PV gets help  Sure we have a windturbine as well but even befor her time this worked out similar We are south coast of Ireland ( so quite good solar conditions) The battery is a second hand forklift battery 1660 ah @ 24 volt since nearly 4 years now Perhaps too big for your boat , but 2-3 kw PV would be good and integrate your Generator for charging , but do not know if you have the space Its crazy cheap now compared to 5 yeas ago when my first Panels were about 3.5 GBP per watt and now only 1 GBP or less Regards Billi
|
|
|
|
|
Logged
|
Guinness no Grid comes near
1.6 kw and 2.4 kw PV array , Outback MX 60 and FM80 charge controller ,24 volt 1600 AH Battery ,6 Kw Victron inverter charger, 1.1 kw high head hydro turbine as a back up generator , 5 kw woodburner, 36 solar tubes with 360 l water tank, 1.6 kw windturbine
|
|
|
|
rogeriko
|
 |
« Reply #12 on: December 10, 2011, 10:10:16 PM » |
|
No even in mid summer when the panels are roasting hot I still get rated output, you see the sun here is stronger so it makes up for the losses. If I water cool a panel in the shade I can easily get 20% more than rated when I put it in full sun for a few minutes.
|
|
|
|
|
Logged
|
|
|
|
|
billi
|
 |
« Reply #13 on: December 11, 2011, 12:34:13 AM » |
|
still i am not sure , and i think its better to work with MPPT and higher Panel voltage ore two or three in series to beef up voltage , looking at these secs as example and the charging voltage (Vmp) of 26.7 Volt only at 800 W/M2 irradiance, 20oC ambient temperature, sounds not enough for me or same when they get too warm the volt drops http://www.kyocerasolar.com/assets/001/5125.pdfI am not convinced that a regular PWM solar charger will be woth the loss on both sides , one side are the losses if there is a bigger gap between battery and PV voltage , the other side is when PV and Battery voltage gets too close , then there are charging losses Perhaps i am too critical  Billi
|
|
|
|
|
Logged
|
Guinness no Grid comes near
1.6 kw and 2.4 kw PV array , Outback MX 60 and FM80 charge controller ,24 volt 1600 AH Battery ,6 Kw Victron inverter charger, 1.1 kw high head hydro turbine as a back up generator , 5 kw woodburner, 36 solar tubes with 360 l water tank, 1.6 kw windturbine
|
|
|
MrPugs
Newbie
Offline
Posts: 8
|
 |
« Reply #14 on: December 11, 2011, 08:04:38 AM » |
|
Hi Billi
I am located just north of you at Terryglass on Lough Derg
The roof of the barge is 50ft by 12ft so I should have enough room I notice a lot of contributers use outback controllers, how have you found these ? Do you have a recomendation of panel size/type Building a proper battery bank in the engine room will be fun
Donal
|
|
|
|
|