A selection of Heat energy out vs electric power in.

Electric energy captured using android Energy Meter app, heat energy captured with an out-of-cert PolluCom E/S

I have also determined that the default controller settings I had were way off. There are settings for flow temperature floor/ceiling - these just act to clip the temperature. The weather compensation setting started out at about 1.7, I now have it at 0.5 (Ambient -2, Room 21 gives about 40C flow) with the room compensation set to 5 at the moment (allowing for a faster ramp up of temperature, then the flow backing off as the room approaches the setpoint) Without this, the room was overheating as it would be calling for a flow limited only be the ceiling until the room stat was reading a degree or two above the setpoint.