« on: January 17, 2012, 10:50:34 PM » |
|
The electrical system in our house is split between two consumer units. One unit has all the heavy circuits and is fed direct from the mains, the second unit has the lighting circuits and two power sockets and is fed through a change over switch either from the mains or an emergency power supply(600w pure sine wave inverter from 24v battery bank). When our PV system was installed I had them link it in to the consumer unit side of the change over switch, the theory being if the mains went off while PV was producing switching to the inverter would provide a 'mains' and the PV would continue generating to give us an enhanced emergency supply and save on depleting the batteries. The other day, one of the few sunny days we have had the last two months, we lost the mains supply so no PV generation! Switch to emergency supply and the PV inverter springs back to life but will not connect, it repeatedly went through its test routine but at the end of the routine gave the message Grid Fault W003. While going through the routine it gave the following messages in turn 1. Vgrid 227v - in range. 2. Fgrid 49.9Hz - in range. 3. Measuring Ris0 - 20 with the ohms symbol. The inverter is a Power One Aurora 3.6. Can anyone tell me what this means and if there is a way to get this inverter to connect to the emergency supply or is my theory up a gum tree?
merkland.
|
|
|
|
|
Logged
|
200w wind turbine grid tied, 1x175w PV grid tie or to batteries, 2x55w PV to batteries, 24vx440ah battery bank. 3.5Kw grid tie (14xSanyo 250w facing 160degrees at 80 degrees inclination, Aurora 3.6 inverter), 2xflat panel water heating (for over 30 years )
|
|
|
|
GavinA
|
 |
« Reply #1 on: January 17, 2012, 10:57:57 PM » |
|
gum tree I'm afraid.
Your back up inverter and grid circuit is far too small for the grid connect inverter, so any time it might try to connect it'd push the voltage right up and disconnect immediately. Well, something like that anyway.
|
|
|
|
|
Logged
|
at home | 80 tubes, 2 tanks direct PV powered SWH + 5 x Yingli 185Wp solar PV panels.
|
|
|
|
BruceB
|
 |
« Reply #2 on: January 17, 2012, 11:07:27 PM » |
|
I suspect Gavin is right as the W003 message is "grid fail wrong grid parameters" so the voltage and/or frequency are going out of range when it tries to connect
|
|
|
|
|
Logged
|
|
|
|
|
ecogeorge
|
 |
« Reply #3 on: January 17, 2012, 11:15:36 PM » |
|
Your grid tie inverter is trying to connect to the grid , -(in this case a pure sine wave inverter) . Unfortunately this will not work as your sine wave inverter is NOT the grid !! Out of my depth here but all related to "islanding" I think  But if you purchased a cheap chinese grid tie inverter (search this forum  ) I believe they will connect  runs to increase house fire insurance.!! rgds George. Edit to add http://en.wikipedia.org/wiki/Islanding
|
|
|
|
« Last Edit: January 17, 2012, 11:20:21 PM by ecogeorge »
|
Logged
|
|
|
|
|
Pat_
|
 |
« Reply #4 on: January 17, 2012, 11:31:07 PM » |
|
The error message suggests that Riso (isolation resistance) is way too low and this is the reason it won't connect. In practice, as said, the emergency power supply doesn't look anything like the infinite voltage source of the grid, which would hold the voltage correct. In fact if you supplied the emergency power supply backwards with the full current capability of the PV inverter it would pull its voltage up very high and do a lot of damage.
|
|
|
|
|
Logged
|
|
|
|
|
billi
|
 |
« Reply #5 on: January 17, 2012, 11:36:03 PM » |
|
Merkland , perhaps it would work , if you grant , that the power from the Grid tie Inverter is absorbed in the house ?
Perhaps you try it again , when not too sunny , and having a big load connected to one of your (off grid ) sockets
The other idea i have is, purchase a MPPT charge controller and switch the DC power cables going into the Grid tie inverter over to the MPPT charge controller to charge the batteries
There are some controllers that can handle high DC Voltage
Or get a big off grid inverter /charger
All the best
Billi
|
|
|
|
« Last Edit: January 17, 2012, 11:39:36 PM by billi »
|
Logged
|
Guinness no Grid comes near
1.6 kw and 2.4 kw PV array , Outback MX 60 and FM80 charge controller ,24 volt 1600 AH Battery ,6 Kw Victron inverter charger, 1.1 kw high head hydro turbine as a back up generator , 5 kw woodburner, 36 solar tubes with 360 l water tank, 1.6 kw windturbine
|
|
|
|
AlanM
|
 |
« Reply #6 on: January 17, 2012, 11:45:08 PM » |
|
Hi think it would/could work but you need the power from the gti to go somewhere. I am building an off-grid with a gti pv array using a victron multi. This will be the "grid" that the gti sees but can also take the power from the gti and backfeed it through the charger into the bank. If your gti sees the inverter as grid and tries to input power then prob overloading it. Maybe would work if loads matched the gti output to prevent overload, but output would prob fluctuate and your load matching would have to keep up.
Alan
|
|
|
|
|
Logged
|
|
|
|
|
Iain
|
 |
« Reply #7 on: January 18, 2012, 07:24:31 PM » |
|
Hi Somewhere in the depths of my memory is something about the grid impedance having to be correct as well as voltage and frequency. Not sure but someone else might know. Iain
|
|
|
|
|
Logged
|
1.98kWp PV (11 x Sharp 180 and SB1700) 20 x 65mm Thermal and 180ltr unvented 6000ltr rainwater storage Plymouth
|
|
|
|
Laurence
|
 |
« Reply #8 on: January 18, 2012, 11:29:00 PM » |
|
Yes, I am afraid you are going to have a hard time convincing your GTI inverter that the AC from your local 500W inverter is "real" mains, and these GTI inverters are designed to trip out and sulk at the merest sniff of trouble.
Grid impedance is likely the key, here (assuming you've got frequency and voltages OK). The inverter will measure grid impedance by trying to "push" the incoming power source from (say)230V to 230.1V, and seeing what happens. The real mains, being a very low impedance source, will hardly budge. The GTI inverter will sense this. Your local mains, unless and probably even if, fully loaded, is going to fly up, when your GTI inverter pokes it. At that point, the GTI inverter smells a rat; it will pull the power and sit back, like it is designed to do.
Remember that the GTI inverter is probing the mains all the time in this way; even if you could present it with a low impedance load for a brief period, something will eventually switch off, the generated AC mains voltage will shift, and your inverter will back off again.
|
|
|
|
|
Logged
|
4KWP on SW roof 16 x Sanyo HIT250 panels Sunny Boy SB4000TL Inverter Sunny Beam Monitor Sunny Delight at making own Juice
|
|
|
|