« on: January 21, 2012, 06:12:44 PM » |
|
I have a 24v battery bank using 12 x 2v opz 1000ah batteries. It is being charged with an 80amp outback charger connected to a 2660w array. The batteries have been charging for about a month now without any load being connected to them. Water levels are good.
I have read on other posts that a 100% charge voltage is 25.4v yet I have only ever measured 25.2v.
Questions: Should they be 25.4v? If they should how can I get them to this voltage? i.e. what is the charging procedure? What would a good equalization charge voltage and duration be?
paul
|
|
|
|
|
Logged
|
|
|
|
|
billi
|
 |
« Reply #1 on: January 21, 2012, 06:31:08 PM » |
|
Hi Paul
temperature will also have an influence .....how cold are your batteries , this time of the year ?
I do not think , that anything is wrong, but do you use a temp sensor with the outback controller ? And did you adjust the charging Volts in the controller to match your batteries ?
My outbacks are charging until 29.6 Volts are reached and at this Volt the batteries boil /simmer the voltage is hold and only the amps decrease , but this is for normal rated temperature of the battery (i think it is 20°) , now in winter cause my battery is cold , the temp sensor connected to the charge-controller lifts this 29.6 V setpoint up to 30.5 and over , depending on battery temp
Billi
|
|
|
|
« Last Edit: January 21, 2012, 07:04:39 PM by billi »
|
Logged
|
Guinness no Grid comes near
1.6 kw and 2.4 kw PV array , Outback MX 60 and FM80 charge controller ,24 volt 1600 AH Battery ,6 Kw Victron inverter charger, 1.1 kw high head hydro turbine as a back up generator , 5 kw woodburner, 36 solar tubes with 360 l water tank, 1.6 kw windturbine
|
|
|
greenhouseparos
Jr. Member

Offline
Posts: 64
|
 |
« Reply #2 on: January 21, 2012, 07:09:19 PM » |
|
Billi
yes i got the temp sensor wired up and i checked the menu of the charger and it has agjusted the charge voltage. i am in Greece not far from Roger and we are experiancing some low temps about 5-6. the batteries are inside a basement but there is no door so it does get cold inside.
what is the adjustment in the charging voltage to match the batteries?
Paul
|
|
|
|
|
Logged
|
|
|
|
|
Justme
|
 |
« Reply #3 on: January 21, 2012, 08:31:26 PM » |
|
Are you using more energy than you are collecting?
If so then the bats wont ever get fully charged.
Your array is also under sized for the bank size. (assuming the bank has been sized for a sensible load size)
|
|
|
|
|
Logged
|
Navitron solar thermal system 30 x 58mm panel 259L TS 1200watts solar 120vdc FX80 Solar controller Victron 12v 3000w 120a 200w (250w peak) 12v turbine as a tester 6kva genny 6 x 2v cells 1550amp/h 5C 24 x 2v cells 700amp/h 5C Total bank 4350 amp/h @12v
|
|
|
|
guydewdney
|
 |
« Reply #4 on: January 21, 2012, 10:22:29 PM » |
|
"month now without any load being connected to them. "
|
|
|
|
|
Logged
|
|
|
|
|
billi
|
 |
« Reply #5 on: January 21, 2012, 10:30:20 PM » |
|
Paul you can adjust voltage setpoints ....see page23 in the manual ,but sure you should do this according to the battery manufacturer recommendation
If the batteries are not new , surely a equalizing charge is a good idea at 31 Volt
|
|
|
|
|
Logged
|
Guinness no Grid comes near
1.6 kw and 2.4 kw PV array , Outback MX 60 and FM80 charge controller ,24 volt 1600 AH Battery ,6 Kw Victron inverter charger, 1.1 kw high head hydro turbine as a back up generator , 5 kw woodburner, 36 solar tubes with 360 l water tank, 1.6 kw windturbine
|
|
|
|
Justme
|
 |
« Reply #6 on: January 21, 2012, 10:36:59 PM » |
|
"month now without any load being connected to them. "
Ok Ok so I missed it lol
|
|
|
|
|
Logged
|
Navitron solar thermal system 30 x 58mm panel 259L TS 1200watts solar 120vdc FX80 Solar controller Victron 12v 3000w 120a 200w (250w peak) 12v turbine as a tester 6kva genny 6 x 2v cells 1550amp/h 5C 24 x 2v cells 700amp/h 5C Total bank 4350 amp/h @12v
|
|
|
greenhouseparos
Jr. Member

Offline
Posts: 64
|
 |
« Reply #7 on: January 21, 2012, 10:45:24 PM » |
|
definetly no loads connected. i did a 4 hr 30v equalising charge yesterday just to give them a stir.
i have been trying to contact the manufactures for a couple of days now to get their view but no answer.
will try again monday
|
|
|
|
|
Logged
|
|
|
|
|
Eleanor
|
 |
« Reply #8 on: January 21, 2012, 10:51:06 PM » |
|
Paul, are they OPzS cells? The Manufacturer should be able to provide brief Operating Instructions which include information regarding rest voltages and SGs for fully charged cells. I’d get a hydrometer as soon as possible and become familiar with using it. Measure the SG of each cell when you think they are fully charged and reference the values (at 20°C) to what the manufacturer says they should be when they are fully charged. I’d probably start to get concerned if the cells aren’t receiving a full charge at least once a week. Undercharging is something that can easily creep up on you without you realising. Hopefully you have a secondary means of charging if the PV isn’t enough? Again, the recommendations for the voltages and time intervals for Equalisation will be in the Operating Instructions which the Manufacturer or Supplier should be able to provide. Once you’ve used them for a while you’ll get a feel for when they need equalising or you may just decide to do it monthly or whatever the recommended interval is. At the moment I’d focus on getting to know the bank and making sure it gets a good regular charge  PS The above was written before your last reply
|
|
|
|
|
Logged
|
I'm doing this for free, please be nice to me  "Very few batteries die a natural death ... most are murdered" 
|
|
|
|
|
|
|
greenhouseparos
Jr. Member

Offline
Posts: 64
|
 |
« Reply #11 on: January 22, 2012, 07:58:51 PM » |
|
they are from Sunlight which is a Greek company. and they are water filled. adjusted the charger voltage set points this morning (increasing both abso and float charge) and we had a full cloudless day of brilliant sunshine. voltage after sunset 25.2v. will look for hydrometer and hope tomorrow i can find somebody at their desk
|
|
|
|
|
Logged
|
|
|
|
|
rogeriko
|
 |
« Reply #12 on: January 22, 2012, 08:11:39 PM » |
|
After charging 25.2 volts is full. Only during charging will you see any higher voltages. What were the volts at 2 o'clock this afternoon?
|
|
|
|
|
Logged
|
|
|
|
|
eabadger
|
 |
« Reply #13 on: January 23, 2012, 09:16:17 AM » |
|
I always thought 25.4v was normal on forklift batteries, our 1000aphr set rests at that. I have found this brilliant link for forklift batteries charging, chemistry etc. answered a lot of my questions. Make sure you read all the pages. http://evbatterymonitoring.com/WebHelp/Battery_Book.htm#Section_3.htmSteve
|
|
|
|
|
Logged
|
1440w PV main array at 24v, excide 2v 1000a forklift cells, 320w PV secondary array at 12v. Enfield 1944 ex RAF 5.6kw diesel genset, Lister AC1 28v diesel charging set at 2.8kw. soon to be 1kw wind turbine.
|
|
|
|
billi
|
 |
« Reply #14 on: January 23, 2012, 10:46:56 AM » |
|
Again , i am not sure about the resting Voltage of traction batteries ...... perhaps its higher than for the OPzS Paul is having http://www.hoppecke.com/content/download/302/1943/file/Installation_Instructions_for_stationary_batteries_en1008.pdfPerhaps the Voltage is lower for the OPzS cause much more electrolyte in the cells than in the PzS traction ones ? Billi
|
|
|
|
|
Logged
|
Guinness no Grid comes near
1.6 kw and 2.4 kw PV array , Outback MX 60 and FM80 charge controller ,24 volt 1600 AH Battery ,6 Kw Victron inverter charger, 1.1 kw high head hydro turbine as a back up generator , 5 kw woodburner, 36 solar tubes with 360 l water tank, 1.6 kw windturbine
|
|
|
|