andrewindevon
Newbie
Offline
Posts: 44
|
 |
« on: January 29, 2012, 10:45:56 AM » |
|
We own a 6 year old theoretically "low energy" house. It presently has DHW provided by a small (0.7 kw) air source heat pump with immersion backup. Space heating is provided by a separate Air to Air heat pump (0.7 kw) working through a MHRV system. Without boring everyone with the details we are using large quantities of electricity, house is fairly cold and want to replace the DHW system and supplement or replace the ASHP side of the MHRV. Floor area is about 220 m^2 volume about 450m^3. Room in roof design with lots of windows. Average annual electric consumption has been about 10,000 kWh costing £1,400 with a green electric tariff. The children are growing up fast and I expect out DHW use will rocket as they do! There is no mains gas (at the moment). November last year we fitted a 3.6kw PV system to a south facing out building. There is a large unshaded east roof, a somewhat shaded west roof and a part shaded large south facing dormer. At the moment the space heating is off (trying to save money and it's pretty useless anyhow) giving room temperatures of about 15c with an outside air temp of 3 c and overcast skies. The lounge is a pleasant 19c with a 5 kw woodburner that's been on for the last 3 hours.
We've had some ideas as to what to change but I'd be interested in peoples ideas..so what would you do?
To get gas connected to the house would be about £2,500. The MHRV and it's ducting is undersized for the house so quite a bit of wall is coming down to replace the ducting.
|
|
|
|
|
Logged
|
|
|
|
|
Ted
|
 |
« Reply #1 on: January 29, 2012, 11:18:09 AM » |
|
Replace the 5kW WBS with a bigger one with back boiler and run rads and DHW from it. Integrate with solar thermal for summer DHW with immersion backup. I assume you are also the poster at http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=8095&page=1#Item_0 - if so, have you sorted the air-tightness out? Getting rid of drafts is #1 priority. WBS will need a dedicated air supply.
|
|
|
|
|
Logged
|
Volunteer moderator 6kW Proven turbine, 20 Navitron tube solar, GSHP, WBS, Rayburn wood central heating
|
|
|
|
Richard Owen
|
 |
« Reply #2 on: January 29, 2012, 01:20:13 PM » |
|
If you had plentiful and easy access to wood, I'd be tempted to put in a RHI compliant wood batch boiler rather than a WBS with back boiler. Big thermal store to store hot water.
If you don't have easy and plentiful access to wood, I'd pay to have gas put in and use the most efficient condensing boiler I could find.
I'd make sure I had a hot water storage system that was solar thermal compatible. Which means that combi boilers are out unless you can find one that will take a hot water input.
Once you've chosen how to heat your water, you could then put a water jacket heater on the MVHR to boost heating.
|
|
|
|
|
Logged
|
44 Yingli 230Wp panels feeding into 2x Solar Edge SE5000 inverters .20x 58mm SE, 20x 58mm SW, Solar Thermal feeding 320l thermal store. 10kW heat pump. 300W of Hydro Power .
|
|
|
|
spaces
|
 |
« Reply #3 on: January 29, 2012, 02:00:58 PM » |
|
Having sorted draughts (does the entrance let in bucketfuls of cold air directly from outside whn in use?), heat your water with solar if the south-facing outbuilding is close by - I assume your house's south facing roof is heavily shaded - and with wood. If you want to live 'green' then 15-16C should be acceptable if there is a wood stove emitting some bone-warming radiation. Woolly jumpers and log-splitting are the best sort of central heating.
|
|
|
|
|
Logged
|
|
|
|
|
Baz
|
 |
« Reply #4 on: January 29, 2012, 02:21:59 PM » |
|
If you are using 10k kWh per year I think that you need to find the hidden cable your neighbours are using to tap into your electricity.
|
|
|
|
|
Logged
|
|
|
|
|
dhaslam
|
 |
« Reply #5 on: January 29, 2012, 02:45:23 PM » |
|
It doesn't sound good that the woodstove is only bringing the living room to 19C. My living room is 21C today with the stove and underfloor heating off. Is it possible that the insulation was not properly installed?
|
|
|
|
|
Logged
|
|
|
|
|
HalcyonRichard
|
 |
« Reply #6 on: January 29, 2012, 03:28:49 PM » |
|
Hi Andrewindevon, It seems your costs are about average for a combined utility bill. I would try to find out what is used on space heating, water heating and electrical applainces/lighting.
For example the average electrical consumption in the UK is 10 kWh/day or 3650 kWh per year. If your home is the same then over 1/3 of your bill is still going to be there if you use gas or wood. This would mean your water and heating is costing you £ 889 per year.
If your heat pumps run at an average COP of 3 (another guess) and the cost of gas is 1/3 that of electricity then the cost for gas and electricity will be the same(at 100% efficiency).
To install a gas boiler and radiators will cost at least £ 2,500. Add the gas connection cost @ £2,500 and it will cost you £5,000 before you can make any savings at all - that is if gas saves anything at all.
My personal feeling is to use wood if you can obtain it cheaply. Then look into a Central heating and hot water version of an efficient WBS. You could keep the heat pump(s) as backup or protection when you are not there for any period of time.
It would also be interesting to know the power used by th MHRV and how efficient it is. Does it run all the time ?
A 220 m2 house is quite large so even if it is well insulated I would expect larger than average heating requirements.
Regards Richard
|
|
|
|
|
Logged
|
Laws are for the guidance of wise men and the obeyance of fools - Richard Burton upon Trent
|
|
|
|
martin
|
 |
« Reply #7 on: January 29, 2012, 03:36:06 PM » |
|
"If your heat pumps run at an average COP of 3" -  - average? - peak, perhaps............
|
|
|
|
|
Logged
|
Unpaid volunteer administrator and moderator (not employed by Navitron) - Views expressed are my own - curmudgeonly babyboomer! - http://www.farmco.co.uk
|
|
|
andrewindevon
Newbie
Offline
Posts: 44
|
 |
« Reply #8 on: January 29, 2012, 09:05:24 PM » |
|
Yeah that's me... I'd rather not bring that discussion into this one, different emphasis. There's no water at the end of the building with the WBS and no simple way of getting any there unfortunately. No cheap wood, all bought in from the usual sort of sources. Things I have considered so far... Do nothing, as long as the outside temp is above 0c then an internal temp of 15c is not too bad and the lounge heats up quickly. Pros cheap! Cons: as the children get older they will want to sit in their rooms and will probably insist on ( or sneak in) fan heaters! Running costs. Just had to bung on electric underfloor heating to dry some boots after being for a walk in the sleet. Log gassification boiler to thermal store. (seperate DHW cylinder for Solar thermal) Pro: Low carbon, in line with concept when building the house. RHPP of £950, possible RHI. cons: cost (about 15-25K depending on model used and amount of work) certainty of fuel supply quality. Issues of exhaust particulate. RHPP is looking fairly unlikely. Resale of the house... Gas boiler to solar thermal equipped cylinder Pro: simple tech understood by every plumber in the town, low cost of boiler/water tank con: Cost of connecting gas to the house About £2K. Goes way against the "green" plan when building the house. Some other Heat pump tech; pro - green electric , con  never ever buying one of them again. Add another wbs (or pellet boiler) to the north end of the house (the end with the water) and from there to a DHW cylinder/rads. Pro - simpleish con: No obvious place for a stove, pellet stoves expensive. I don't know what the COP is,but in the winter I suspect its less than 1... which is depressing!
|
|
|
|
|
Logged
|
|
|
|
|
regen
|
 |
« Reply #9 on: January 29, 2012, 09:32:26 PM » |
|
If you are going to buy all your wood then in the long run i think you would be better off moving to gas for the main heating system. Wood is great if you can get it for free, have plenty of dry storage space and actually enjoy collecting it. However wood burners are dusty, require constant attention, purchased wood is not always reliable and installation with a flue etc will be more than a gas boiler. The gas boiler can probably be arranged so that it only tops up when the other heat scources are not sufficient. What ever you go for you will probably need a hot water cylinder and rads.
Good luck
Regen
|
|
|
|
|
Logged
|
|
|
|
|
Baz
|
 |
« Reply #10 on: January 29, 2012, 11:15:17 PM » |
|
Given awkwardness of wbs and gas how about a GSHP with borehole instead of surface loop. Will give a better COP. You mentioned a lot of windows so how about some internal DIY thermal shutters. Also have a look at how the MHVR is working and if it is taking cold air from unheated rooms and pulling warm air from the rest of the house into those rooms unnecessarily. The rooms you are not heating may be still taking out a lot of heat from other rooms so if the internal walls are stud you could insulate them.
|
|
|
|
|
Logged
|
|
|
|
|
dhaslam
|
 |
« Reply #11 on: January 29, 2012, 11:25:12 PM » |
|
I don't think that MHVR is very effective at transferring heat. When I run the condensing dryer in the utility room that puts out over 1 kW of heat I cannot detect any temperature rise in the other rooms. Air just isn't much use at transferring heat. If you add a new boiler to supplement the heat into the ventilation system it probably wouldn't be very efficient.
How many rooms have electric underfloor heating? Could this be used with off peak electricity?
|
|
|
|
|
Logged
|
|
|
|
|
HalcyonRichard
|
 |
« Reply #12 on: January 30, 2012, 08:01:35 AM » |
|
Hi Andrewindevon, I would check and measure the system you have. If it's not performing try to find out why. If you look at :- http://www.genvex.dk/uploads/GB_GE_PREMIUM_1_1L(2).pdf. The bottom graph for the L version suggests a COP of 4 @ 10 C and a COP of 2 @ -5C or about 3 on average for a temperature range of -5C to 10C. I would try and heat the whole house to the same temperature any differential heating will cause condensation problems. If there are any rooms not heated then keep them sealed from the rest of the house by keeping the doors shut. Really the information needed is how much energy is needed to heat the house in kWh/year. Then work out the costs for various options. A very good point about the ease of use and maintainence of various systems. As for being green - this is your home and familly you must do what is right for you and your situation. Regards Richard
|
|
|
|
|
Logged
|
Laws are for the guidance of wise men and the obeyance of fools - Richard Burton upon Trent
|
|
|
|
qeipl
|
 |
« Reply #13 on: January 30, 2012, 09:06:15 AM » |
|
Andrew,
As others have said I think you need to work out how much electricity each bit of your installation is guzzling.
Space heating should be easy - your summer bills will show what's being used when no heating's required.
Separating DHW from everything else might involve a bit of guesswork but will give you an idea.
I have an ASHP DHW cylinder that also does 70m^2 of UFH which appears to be very economical to run, but I've heard of some versions that are a nightmare because the immersion 'back-up' is kicking in regularly. If the capacity of the cylinder is too small for the usage pattern then the immersion heater is on a lot of the time to make sure recovery times are short. This could be a major contributor to your high electricity consumption but you won't know for sure until you work out how much each bit of your system is consuming.
When you have some numbers you can then start to consider the options.
Malcolm
|
|
|
|
|
Logged
|
Take 3 minutes to find out where money comes from, why that means we will all end up in debt, and what we can do to fix the problem… http://www.positivemoney.org.uk
|
|
|
|
billi
|
 |
« Reply #14 on: January 30, 2012, 12:01:17 PM » |
|
I would say as well ,to have a closer look into the details of the system , if 10,000 kWh for a whole year is all..... for all electricity needs ....then i do not find this too frightening First question should be ,how to improve the existing system in my opinion .......... like is it possible to pree-warm the incoming air from outside to the heatpumps with a soil-type heat-exchanger , or a solar hot air collector , .....perhaps Perhaps a hot air Wood burner could be integrated .... or a masonry stove can be integrated in the Heatrecovery system to spread heat in all rooms   I cant see the point of redo all,and replace with something else before not finding out the problems or how to improve But perhaps i have missed something Billi
|
|
|
|
|
Logged
|
Guinness no Grid comes near
1.6 kw and 2.4 kw PV array , Outback MX 60 and FM80 charge controller ,24 volt 1600 AH Battery ,6 Kw Victron inverter charger, 1.1 kw high head hydro turbine as a back up generator , 5 kw woodburner, 36 solar tubes with 360 l water tank, 1.6 kw windturbine
|
|
|
|