thanks for more information CeeBee
yes, I'm the guy M mentioned!
I have a Fronius IG Plus 35V, with an Owl CM160 monitor that displays a constant 113W at night (well, actually reads 0.49A, Owl is set at 230V), or when the inverter is not "producing" (I have the monitor set to read power generation only, sensor inside the CU).
I did some research, and have proved the inverter doesn't "draw" power at night by switching all fuses off on the CU except the inverter one. reading the outside house meter then leaving over night (13) hours, and re-reading. the meter had not moved even 0.01kWh. the Fronius handbook says it draws 0.23W in "night mode".
I'm very interested in your reply, cos since installation just over 2 months ago I have been trying to understand the error in my Owl kWh reading and Gen. meter reading over time.
I have my Owl set to 230V as I read somewhere this "compensates" for the reactive errors in the household, no idea if thats right.
hope you can give me more insight into this so i can understand it fully
your explanation makes perfect sense to me, and is how I have been thinking the error is explained. I can't see how that 0.49A error is there constantly no matter the Current, or sine wave being produced
(which, as others have argued on mse, is the case).
also, i believe the Owl as stated by the manufacturer is less accurate at low current readings, and more accurate at higher ones (below 1A then not specified,1 to 3A then less than 10%,3 to 71A then less than 5%)
after 53 (30 Nov to 21 Jan) days from installation, my Gen meter was reading as near as damn it 300kWh, my monitor reading 420kWh set at 230V.
this was my "fag packet" maths:
assuming 13 hours "nighttime" each day, thats 0.113kW*13*53=78kWh
assuming ? hours no output/very low output during each day, no idea but guess 4? so thats 0.113kW*4*53=24kWh
420-(78+24)=318
318/300*100=6% error
i thought that put my "guess" of 6% error as within the stated error of the monitor by the manufacturer
does this make any sense?

regards
Don