Ivan, Martin & List,
I posting in this section - but feel free to move to a more appropriate section.
Lead acid batteries are commonly used in off-grid ystems for power storage and buffering. Batteries have a charge/recharge efficiency of around 66%, and with some inverters running atpoor efficiency at low load, the losses soon mount up, meaning that a larger battery pack might be needed.
Here are some of my observations from my set-up, partly as a record of my developments but also so that others my benefit from my observations.
As some of you know I have acquired a load of old Hawker SBS 40 sealed lead acid batteries, that are now wired up and powering my 5kW pure sinewave inverter.
Yesterday I decided to do a battery indurance test, using a 500W halogen flood light as the test load. I was re-arranging my workshop/engine shed and the extra lighting was most useful on such a dull day. The floodlight presented a very stable 472W load.
I wanted to confirm that the battery pack was of sufficient capacity to power the household during peak times and during the night.
My inverter is about 10 years old and was salvaged from an emergency lighting system. Unfortunately it has a fixed overhead power drain on the batteries, which means at low output the overall efficiency can be very low.
My reason for using it was that it was cheap, bombproof up to 5kW and produces very good quality sinusoidal power. This is ideal for smoothing out the lumpy power that is generated by the Lister, and the battery acts as a substantial store of power.
After 12 hours of running the inverter and floodlight load, the battery had reached 90V or a nominal 1.66V per cell. The battery current to the inverter remained in the range of 8.4A to 9.4A during the 12 hour test.
My batteries consist of 4 parallel strings of 9 batteries, so the discharge current through each string was between 2.1A and 2.35A.
At the end of the 12 hours I went through the batteries to identify which were good and which were at a reduced voltage. Most were still in the spread of 11.0V to 11.9V, but some had dropped as low as 9.0 to 9.5V and one pour mite was down at 7V.
I have concluded the following:
1. If you have a mixed bunch of 2nd hand batteries, separate out the weaker ones and put them in the one string - these can then be given a more rigorous charge until their capacity is satisfactory.
2. 3/4 of the batteries had substantial capacity remaining, and it is likely that the pack would have better overall performance if the weaker batteries were removed and I ran on 3 strings rather than 4.
3. The inverter efficiency is fairly poor when running a 472W load. Between 850W and 940W was being drawn continuously from the pack during the duration of the test.
4. The pack was placed on charge overnight and the charger is drawing about 1150W from the mains. 11.6kW has already been consumed in just over 10 hours. It is likely that the bulk charge will take around 12 hours before the charger reaches its float voltage and reduces the current.
5. Some figures (for the record)
Battery Pack 36 SBS 40 sealed lead acid monoblocks, ex-telecom/standby arranged as 4 strings of 9 batteries.
Temperature in battery shed 20 C
Float Voltage 124V
Initial On-load voltage 111V (when drawing 2.1A per string).
Test Load 472W halogen flood light
Power into Inverter (111V x 8.4A) = 932.4W
Power from Inverter = 472W
Inverter efficiency (472/932.4) = 50.6%
Energy drawn from inverter in 12hrs 0mins 5.66kWh
Energy drawn from batteries (estimated) = 10.67 kWh
Energy needed to recharge pack tofloat voltage = 12 hrs x 1150W = 13.8kWh
Efficiency of battery charging process = (10.67/13.

= 77.3% - to be confirmed at end of charge cycle
Conclusions.Lead acid batteries provide useful storage but not without substantial losses in the charge/discharge process. An inverter and battery bank could be used for time-shifting power from cheap-rate night tariff, to daytime use, if the inverter is a high efficiency unit.
The inverter losses are considerable and need to be investigated. Mains cooling fans could be replaced with dc fans to reduce losses at low load.
There is a strong argument to distribute low voltage dc around an off-grid household, to avoid inverter losses.
A smaller, more efficient inverter could be used for light loads, such as office PC, lighting circuits, with the larger unit wired into the kitchen ring main for occasional use of kettle, washer, dishwaster etc.
There is a strong case to keep the fridge/freezer on grid power, switching only to inverter power during grid failure.
As the batteries will be recharged from the Lister using a direct dc feed, this will avoid some of the transformer losses. However the estimate of 2kWh of power per litre of veg oil will have to be lowered to almost 1 litre per kWh of clean inverter power. These losses clearly affect the overall efficiency of the electrical generation side of the Lister CHP system, suggesting that there will be a greater percentage of waste heat - for home heating, at the expense of fuel burned.
I would be interested hearing from anyone else running a battery/inverter system in the 3kW to 5kW range, for their experiences of inverter losses.
Ken