News: Anyone wishing to register as a new member on the forum is strongly recommended to use a "proper" email address - following recent spam/hack attempts on the forum, all security is set to "high", and "disposable" email addresses like Gmail, Yahoo and Hotmail tend to be viewed with suspicion, and the application rejected if there is any doubt whatsoever
 
Recent Articles: UPDATE ON DECC APPLICATION FOR LEAVE TO APPEAL TO THE SUPREME COURT | Yingli Green Energy's PV Module Ranks No.2 in TUV Rheinland Energy Yield Test | Navitron Solar Showers at Glastonbury for Year 5!
   Home   Help Search Login Register  
Pages: 1 2 3 4 [5] 6   Go Down
  Print  
Author Topic: circulating pump - advice needed  (Read 12591 times)
SteveH
Hero Member
*****
Offline Offline

Posts: 1079



« Reply #60 on: August 08, 2008, 04:24:00 PM »

This is not a centrifugal pump, the DAB rep termed it as....an inline water circulator.

 In this case: IWC (inline water circulator) = Pump

 The Dab VA 55/130 CIRCULATOR has an impeler & the cutaway picture from the specification sheet (Click here) clearly shows it is of centrifugal design...

How does this affect the response to my previous question ?

 It doesn't... You've just been "Techno babbled" by Dab....  Grin
Logged

Preveli, South Crete.
deeside70
Newbie
*
Offline Offline

Posts: 21


« Reply #61 on: August 08, 2008, 08:24:25 PM »

steve h
thanks once again.
she sounded so convincing,when she returned to the phone after putting me on hold, while she asked a colleague.
i should have guessed.
well and truly .... techno babbled .  - nice phrase.
regards
noel
Logged
northern installer
Hero Member
*****
Offline Offline

Posts: 1503


« Reply #62 on: August 08, 2008, 08:45:57 PM »

being picky perhaps,but right both ways,the dab circulator is a centrifugal pump in principle,but termed a circulator as its design would not allow it to 'pick up and pump' to coin a phrase,it needs a closed circuit;anyone who has tried to use an old circulator as a pump will be aware of the somewhat disappointing results!  chocolateteapot
Logged

"government scrappage scheme still available on Tardis trade ins (dont ask how we get around the deadline...)"
SteveH
Hero Member
*****
Offline Offline

Posts: 1079



« Reply #63 on: August 08, 2008, 10:09:24 PM »

 Point taken NI...  I take it they have no suck ... Grin

 Noel, you should have no concern about it acting as a generator wile water is circulating through the unpowered pump.... Wink
Logged

Preveli, South Crete.
northern installer
Hero Member
*****
Offline Offline

Posts: 1503


« Reply #64 on: August 08, 2008, 10:12:05 PM »

No sucking good at all for anything other than circulating Grin
Logged

"government scrappage scheme still available on Tardis trade ins (dont ask how we get around the deadline...)"
Alan
Guest
« Reply #65 on: August 09, 2008, 07:45:03 AM »

Hello Noel

As per Mr Steve H post, no appreciable resistance would be added to the pump loading on top of friction losses. No electrical problems.

Regards

Alan
Logged
deeside70
Newbie
*
Offline Offline

Posts: 21


« Reply #66 on: August 26, 2008, 10:04:58 PM »

steveH/alan
hi, thanks again for the advice.
fitted the 12 volt motor vehicle water pump in line last night and connected the PV panel to the pump using the
capacitor recommended.
got up early this morning, waiting for the sun to hit the solar and PV panels.(PV sits just above solar)
the system works really well ....so far.
i spent most of the day listening to the sound of the pump changing speed,matching the cloud cover at that time.
i had reservations about the 6 watt PV panel being too weak,but it seems fine.
only time will tell.
regards
noel
Logged
billi
Global Moderator
Hero Member
*****
Offline Offline

Posts: 5405



« Reply #67 on: August 26, 2008, 10:28:43 PM »

Quote
i spent most of the day listening to the sound of the pump changing speed,matching the cloud cover at that time.

Thats like music  isnit  , what a harmony  Grin solar electricity and solar thermal ,

billi
Logged

Guinness no Grid comes near

1.6 kw and 2.4 kw   PV array  , Outback MX 60 and FM80 charge controller  ,24 volt 1600 AH Battery ,6 Kw Victron inverter charger, 1.1 kw high head hydro turbine as a back up generator , 5 kw woodburner, 36 solar tubes with 360 l water tank, 1.6 kw  windturbine
deeside70
Newbie
*
Offline Offline

Posts: 21


« Reply #68 on: March 08, 2009, 05:41:20 PM »

hi all

The system worked well with the 12v motor and capacitor and PV panel up to the end of October.
Then nothing until around 20th Feb  --- gloomy short winter days. I need an alternative for next winter as this is an old stone farmhouse.
I have a wood burner without backboiler  and i intend to fit a  22mm copper tube loop inside the lower part of the 125mm stainless steel chimney, to use the heat from the top of the fire, to run a thermosiphon system which would link into my 2 tank system.
Q.   Could i safely run this circuit into the solar panel circuit near the tanks -  i have a 3 way diverter valve? This would mean using the pressure control valve and expansion vessel and 3 way valve in conjunction with solar clrcuit.
The alternative would have to be an independent circuit  with valve and vessel, 3 way diverter, control and 2 retro fit coils.   Expensive !!
Regards
Noel
Logged
martin W
Hero Member
*****
Offline Offline

Posts: 548


what do you mean my snoring is too loud!


WWW
« Reply #69 on: March 21, 2009, 07:50:08 AM »

hi Deeside....

from what I've read and been told, the general rule of thumb with a WBS heting water is there must not be any valves or anything on the WBS circuit as it is an 'uncontrolled heat source'. Basically the WBS must go directly to and from the cylinder, you are allowed put 'heat leak' rads into the circuit via injector 'T's. to dump excessive heat form the WBS once the wate ris up to temp. I'd look on the Solids part of the forum.


Just to sum this thread up, could you post what you actually bought and did to replace / supliment your 240volt navitron circulator witha 12volt lower wattage one...

cheers.

Logged

Woodstove Newbie since Feb 2011 Tongue (yes it's finally off the pallet)
Solar Water Heating since 17th March 2009
Chicken Owner - Self sufficient in chicken c*@p, boy watch those tomatoes grow. 
Now an allotment wannabie Tongue
deeside70
Newbie
*
Offline Offline

Posts: 21


« Reply #70 on: November 12, 2009, 05:48:48 PM »

hi martin/all
i sited the photovoltaic solar panel immediatly above the 20 tube panel.
the 12v electric motor/pump was placed in-line with and just after the 240v pump on the return,connected to the copper pipe with motor vehicle hose and jubilee clips.
the capacitor was placed across  the two wires from the cell, just above the motor. the system was earthed.
this system has worked well, no problems for 18 months now.

photovoltaics....Sunshine solar panel CIGS 6W - 12V £34.65 on e bay Solar panels.
motor.............Solar water pump panel.....AUDI 12v ,brush-less water pump  £55.00 ebay
capacitor.........RSH Services......£0.55   sales@rshelectronics.co.uk
rubber hose.....any motor factor......around £10.00/metre

cheers,noel
Logged
SteveH
Hero Member
*****
Offline Offline

Posts: 1079



« Reply #71 on: November 12, 2009, 10:27:14 PM »

 Hi Noel,

 Thanks for reporting back... I'm really pleased that your solar powered system is working well.

 Defiantly a plus point for the KISS approach... nice to know the advice was appropriate... & keep posting updates.

 Steve...
Logged

Preveli, South Crete.
Contadino
Full Member
***
Offline Offline

Posts: 228


« Reply #72 on: November 20, 2009, 05:35:20 PM »

This thread is interesting.

I've been running an El Cid 5 watt circulation pump from a 10 watt PV module for 4 years with no problems.  There's a diff temp controller in the mix which is self-powered from the same PV panel (i.e. the panel tops up the controller batteries each morning when the flat panel is still cold.)

You may say that my primary temperatures are lower because I'm using a FP collector, but with daytime temperatures hitting 45º in summer I doubt that argument stands up.

However, with the benefit of hindsight, I'd say that if I was opting for a tube system in the future, I'd have to think hard about whether to use a PV circulating pump.  Somehow you'd have to match the water and PV panel efficiencies - which would be beyond my abilities with tubes.  That said, I doubt I'd ever switch from FP to tubes.
Logged
martin W
Hero Member
*****
Offline Offline

Posts: 548


what do you mean my snoring is too loud!


WWW
« Reply #73 on: November 22, 2009, 09:57:11 AM »

Just had another thought on this system.. 12volt pump and 240v pump in series...

Could the 12volt pump just run due to the amount of sunlight hitting the PV panel. then if it wasnt 'man' enough to push enough water though the solar vacuum tubes the controller on the 240v pump (TDC3) would then switch the 240v pump on as well to drop the vacuum tube panel temp.

Does that make sense.

would the 12volt pump run when the vacuum panel was actually colder than the hot water cylinder? Or would this never be an issue.
Logged

Woodstove Newbie since Feb 2011 Tongue (yes it's finally off the pallet)
Solar Water Heating since 17th March 2009
Chicken Owner - Self sufficient in chicken c*@p, boy watch those tomatoes grow. 
Now an allotment wannabie Tongue
deeside70
Newbie
*
Offline Offline

Posts: 21


« Reply #74 on: November 26, 2009, 05:14:09 PM »

hi martin
morning dew on the photovoltaic panel usually prevents the two panels from kicking in simultaneously, so the 240v pump is activated until the 12v motor kicks in.

it does not matter if the panel temperature is colder than the cylinder --this is usual in the morning start-up.
the pv panel will run the 12v motor as soon as the sun hits it. hence the reason for placing the pv panel immediately above the solar panel.
the sun hits the two panels simultaneously therefore they kick in together - dew permitting.
when clouds appear, they both slow down production. sun reappears and off they both go again.
perfect.

regards
noel