News: Anyone wishing to register as a new member on the forum is strongly recommended to use a "proper" email address - following recent spam/hack attempts on the forum, all security is set to "high", and "disposable" email addresses like Gmail, Yahoo and Hotmail tend to be viewed with suspicion, and the application rejected if there is any doubt whatsoever
 
Recent Articles: Yingli Green Energy's PV Module Ranks No.2 in TUV Rheinland Energy Yield Test | Navitron Solar Showers at Glastonbury for Year 5! | Lights go on in Sierra Leone
   Home   Help Search Login Register  
Pages: 1 2 [3] 4 5   Go Down
  Print  
Author Topic: Willis solarsyphon  (Read 8868 times)
Billy
Hero Member
*****
Offline Offline

Posts: 1330



« Reply #30 on: November 20, 2008, 08:23:25 PM »

I know nothing, but what if....

the larger column of colder, denser water (relativity) in the tank is pushing down (gravity) into the HE or W syphon with a much smaller pipe size.

Could this be anything to do with hydraulic jack principal and mechanical advantage and not exclusively the hot water rising  You see what I'm getting at or am I perhaps firmly in lah lah land.   wackoold wackoold

What think the brains out there.

Be brave, shoot me down, my shoulders are broad.  surrender

Just a thought.

Billy the Barge

 Grin Grin Grin
Logged

Navitron 24vx300watt windy thing, 20x47mm toobs,24v Rolls @458ah C5, Victron MultiPlus 3kw inverter/charger, WBS with boiler.
KLD
Hero Member
*****
Offline Offline

Posts: 1340


« Reply #31 on: November 20, 2008, 09:50:41 PM »

Billy,
the diameter of the vessels should have nothing to do with the relative buoyancies.
Try this as a more intuitive experiment: take one small diameter tube and one barrel, connect the two with a length of tube on their bottom ends, and fill with water. The water level will be the same in both pipes. (Well, except for the case when the small diameter is so small that capillary forces distort the picture. But enough of that:-)
The only parameter determining the outcome of this experiment is the density of the water.
If you were to lower the density of the water in one compartment, say by heating it (were did that sun go?), then its level would rise.

Now, if you install an overflow from one vessel to the next, the rising level would yield a flow into the colder vessel, thereby heating it. Eventually, both vessels are back at the equal, but higher temps (and slighty expanded volume; where did the F&E tank connection go?  ;-)
In other words, the average density in each vessel determines, whether at all and which way round the water flows. (As Wookey has pointed out earlier.)

Klaus
Logged
Billy
Hero Member
*****
Offline Offline

Posts: 1330



« Reply #32 on: November 20, 2008, 10:38:57 PM »

Klaus,

I've just crashed and burned, when you put it like that,  but thanks.  I think I am getting confused with atmospheric pressure and sealed tubes.  Not that I know anything about that either!  I just happen to have a bucket with a valve and hose tail in the base, will experiment to understand more fully.

The Willis caught my I as I have just ordered some of Ivan's tubes.  I have a twin coil tank but have them plumbed to other stuff.  The syphon seemed to be the answer to my little problem but I have not got 500mm to spare.   I too am confused as to why the Willis has to be tee'd in at 500mm and how heated warm water finds its way over the hot tank water, but not half as clever as the blokes who used to use a single horizontal pipe for flow and return for gravity heating in the old New York blocks.  I reckon that is extreme stratification and why doesn't the boundary mix, I guess it does to some extent.

Wish I had your lots brains,

Billy the Barge

 Grin Grin Grin
Logged

Navitron 24vx300watt windy thing, 20x47mm toobs,24v Rolls @458ah C5, Victron MultiPlus 3kw inverter/charger, WBS with boiler.
lightfoot
Hero Member
*****
Offline Offline

Posts: 1508


« Reply #33 on: November 20, 2008, 11:42:08 PM »

Hi Klaus,

Sorry, I may be misreading your post some how (it's getting late Grin) - But......

Billy,
the diameter of the vessels should have nothing to do with the relative buoyancies.
Try this as a more intuitive experiment: take one small diameter tube and one barrel, connect the two with a length of tube on their bottom ends, and fill with water. The water level will be the same in both pipes. (Well, except for the case when the small diameter is so small that capillary forces distort the picture. But enough of that:-)

Correct and also, the static pressure (which in a open system is relative to the hight (head) of the water level above a given datum) will be the same in each too.


If you were to lower the density of the water in one compartment, say by heating it (were did that sun go?), then its level would rise.

Now, if you install an overflow from one vessel to the next, the rising level would yield a flow into the colder vessel, thereby heating it. Eventually, both vessels are back at the equal, but higher temps (and slighty expanded volume; where did the F&E tank connection go?  ;-)
In other words, the average density in each vessel determines, whether at all and which way round the water flows. (As Wookey has pointed out earlier.)

Klaus

If one of the compartments / vessels was heated, natural convection will cause the hotter, more buoyant water to rise / float on top of the cooler water within the compartment / vessel.  However, discounting any displacement due to the thermal expansion of the water, the actual water level will not rise (if that's what you meant ?). 

If the two compartments / vessels are connected at the bottom (or anywhere below the water level) then in a open system, under steady state conditions and the same static pressure, the water levels will always be the same in both compartments / vessels and/or connecting pipework - regardless of any temperature differences.  As water in a system will always try to maintain the same level. 

(Note: for simplicity, the above discounts any dynamic pump pressure / velocity effects that may occur within a system)

If the two compartments / vessels are also connected at the top as well as the bottom and one of them is heated, then natural convection will again cause the hotter, more buoyant water to rise and induce gravity circulation (thermosyphon) between the two compartments / vessels.  The water velocity / turbulence needs to be kept to a minimum, to avoid mixing / dilution - to promote good stratification.



Billy, As far as hydraulics/jacks go, I think you may have been getting confused with the potential pressure rise caused by displacement of a fluid etc, ie if you try and force 2 ltr of water into a 1 ltr container - then something has got to give (sorry it's maybe not the best analogy - but hopefully you get me drift  Grin)



Lightfoot.
« Last Edit: November 21, 2008, 09:27:20 AM by lightfoot » Logged

Mother Nature is a wonderful housekeeper - but eat her out of house and home and you may just get your marching orders.
KLD
Hero Member
*****
Offline Offline

Posts: 1340


« Reply #34 on: November 21, 2008, 08:10:24 PM »

Lightfoot.

my thinking was as follows:

firstly, I agree that in corresponding tubes the liquid will rise to equal levels. But only as long as the liquid has a homogeneous density, i.e. the density is constant throughout the system. Lets consider the simplest system, in which you have just one tube bent into a u shape. At any given height, the pressure in both arms is identical. This pressure is a result of the mass of liquid above the chosen level, and the section area of the tube. (And the atmospheric pressure, but let's assume that is constant and equal for both arms.)

Now, if you were to replace the liquid in one arm of the U with a different liquid of, say, lower density, then you'd need a larger volume of this new liquid to yield the same mass, and therefore the same pressure at our chosen level.

The lower density could also be achieved by heating the one side of the U. The "thermal expansion" is exactly the increase in volume I'm after Wink As long as it's just a U, i.e the tubes are only connected at their bottom ends, no displacements occur.

Whether the heating of the one arm is even throughout its whole length, or whether there is any part warmer, it's the average density that determines how high the level will rise.

 Smiley
Klaus



Logged
ericw
Hero Member
*****
Offline Offline

Posts: 707


« Reply #35 on: November 22, 2008, 10:20:38 AM »

I think some clue to the answer to the question of whether thermocycling can take place if the temperature in the side arm is lower than the temperature at the top tank connection can be obtained by looking at vastly simplified model.

Consider that the cylinder and HE heated side arm to be a simple 0 shaped loop.

One side representing the side arm is full of warm water.
The other representing the tank has a layer of (perfectly stratified) hot water on top of cold water.

To work out when thermosyphoning can take place you must look at the relative magnitude of the forces at the bottom of the 0
The force from the side arm will be its height multiplied by the density of the warm water
The force from the cylinder side will be the height of cold water multiplied by its density plus the same for the hot water layer.

Interestingly this shows that it is driven not only by the relative densities (temperatures) as expected, but also by the position of the hot-cold interface in the cylinder. When there is only a thin layer of low density hot water then its perfectly possible for the system to thermocycle even though the side arm temperature is lower than the hot water temperature, as the average density in the cylinder can be higher than that in the side arm.

So initially it will thermosyphon at relatively low temperatures but the thermosyphon temperature will increase as the hot-cold interface is pushed further down the cylinder.
Of course in real life there are no nice sharp boundaries and it will work on the average density in the two sides but I believe the principle still holds.

This could also explain why Willis connect their device higher up on the expansion/vent pipe.
Because its in a relatively thin pipe, it only requires a small volume of water to fill it and it will effectively create a much deeper hot layer than would happen in the cylinder alone.
If the theory above is right, this will suppress lower temperature thermosyphoning and so give hotter water at the top of the tank.



Logged
lightfoot
Hero Member
*****
Offline Offline

Posts: 1508


« Reply #36 on: November 27, 2008, 08:30:29 PM »

Hey Klaus,

Having thought about it, you are indeed correct with regards to the water density/level difference when two tubes/vessels are only connected at the bottom.  Have a cigar......I'll go stand in the corner.....where's the Donkey Ears smiley  Grin



Cheers


Lightfoot.
« Last Edit: November 27, 2008, 08:33:47 PM by lightfoot » Logged

Mother Nature is a wonderful housekeeper - but eat her out of house and home and you may just get your marching orders.
wookey
Hero Member
*****
Offline Offline

Posts: 2558


WWW
« Reply #37 on: November 27, 2008, 09:25:03 PM »

I sympathise, lightfoot. I started a post arguing with him then realised half-way through that he was right actually. It's a subtle one because you hardly ever see it in practice.
Logged

Wookey
djh
Hero Member
*****
Offline Offline

Posts: 1167


« Reply #38 on: November 27, 2008, 09:46:49 PM »

this shows that it is driven ... by the position of the hot-cold interface in the cylinder.

This could also explain why Willis connect their device higher up on the expansion/vent pipe.

Brilliant!  Grin  laugh  Grin  laugh  Grin

Now I think I understand it.

Have an applaud.
Logged

Cheers, Dave
Ivan
Guest
« Reply #39 on: November 28, 2008, 11:03:42 PM »

That explains why Wookey's system works well, even though his temperature sensor is connected to the cylinder rather than the side arm heatexchanger, doesn't it?

Does that also mean that you shouldn't connect the cylinder reference temperature sensor to the cylinder, when you are plumbing high into the vent/expansion pipe as per Willis's plumbing recommendations.....which means their temperature sensor recommendations are wrong?
Logged
Brandon
Hero Member
*****
Offline Offline

Posts: 1246



« Reply #40 on: December 03, 2008, 11:02:16 PM »


If the theory above is right, this will suppress lower temperature thermosyphoning and so give hotter water at the top of the tank.



That all makes sense, but on a cloudy day when the top of the cylinder is hot >50c from either the previous days solar or an evening WBS burn for example, then the panels may not reach that temperature, and therefore no energy is had from the panel during the day.

Surely then a slightly raised full body of water is better as it captures energy?
Logged

changing the world, one roof at a time...

"We can't be B&Q astroturfers. That's one conspiracy theory too far. You should cut down on the pot." - Wookey
Ivan
Guest
« Reply #41 on: December 03, 2008, 11:21:29 PM »

Not really an issue with vacuum tubes - the energy they can gain is limited by the amount of sunshine, but the delivery temperature is almost independant. So you can still get a small amount of hot water on overcast days, rather than a greater amount of lukewarm water. Obviously, this doesn't apply to flat plate systems.
Logged
chrispierce
Guest
« Reply #42 on: December 30, 2008, 10:56:38 PM »

We are fitting our first Willis Solar syphon and require clarification. Having read through as many posts as poss on the forum, using TDC3 controller, I am confused where the best place to fit the S2 sensor should go, ie in the insulated jacket of the solarsyphon or in the lower part of the jacket. Secondly does  the 6/4 temp difference still apply. Are there any other settings which would be perculier to using a Willis SS.
Logged
Northbridge
Jr. Member
**
Offline Offline

Posts: 82


....banging on about heat pumps again!


WWW
« Reply #43 on: January 02, 2009, 08:20:24 PM »

I worry about reports of "the customer says they have more hot water".  Compared to what??? the solar hot water system they took out last week?

Cynical I know.... I have had a meeting with our other technical staff and a CHAP FROM OUR CYLINDER MANUFACTURER and our conclusion - do the job right and change the bloody cylinder.  second rate is second rate.  And how much solar do we do?  loads.

It's obvious to a nugget what the shortcoming of these units are, and where they fall over.  If someone can't pay the extra 300 quid over the willis unit price) for a twin coil newark cylinder then send them elsewhere for a second rate job - don't hang YOUR reputation on it.

And happy new year!
Logged

It takes ten acres of willow to run Drax power station for 2hrs 30 mins.
martin
Administrator
Hero Member
*****
Offline Offline

Posts: 10829



WWW
« Reply #44 on: January 02, 2009, 08:26:58 PM »

now the bloke from the cylinder manufacturer would, of course, be totally unbiased...........there are many companies out there who do LOADS of solar installations, every single one of them cr*p........Me? - I'd sooner wait for the independent test results from the setup at Navitron HQ before leaping to possibly uninformed and plain wrong conclusions Wink
« Last Edit: January 02, 2009, 08:28:31 PM by martin » Logged