That's a bit startling, not to say disappointing; won't the MPPT60 limit the current without letting the smoke out even just as far as the glass?
The fuse is an in-line one (not inside the charge controller).
The Tristar does limit the current (to any value you program or a default of 60A). The recorded surge was 1960W, which was about 74A. The Tristar was bouncing off the 60A limiter when the fuse went. The other controller was doing just over 14A (just shy of its 15A limiter) with only a pair of Sharp 170W panels (340Wp). It recorded delivering 376W (110% of PV nominal rating) at the moment the fuse went pop.
The problem is one of the fuse I used being a bit undersized at 60A. If you run a fuse at its rated current, it will eventually blow (especially if it is subjected to surges which cause thermal shocks to the metal in the link). I should have used a 70A fuse but they don't make one in this type (60A is the biggest). I suppose I could reduce the current limit on the controller to 55A, but if the fuse blows once in every two years, then it's not such a big deal. Nothing else on the circuit gets even remotely warm, as I used 20mm
2 cable or fatter throughout and 100A switch gear.
It's pretty rare that the array hits 60A for more than a few seconds, so I'd figured that it wouldn't spend enough time at the limit for it to be an issue.
Fuses get "old" as well... Putting the new one in, I noticed that it didn't get warm today, with the power of the sun. Also the Tristar got to the absorption Voltage before the other controller and started blinking sooner. I put this down to the old fuse slowly degrading with heat, causing its resistance to increase, so it drops more Voltage and heats up more and so on until it finally blows. The flexing of the link with heat will also cause the resistance of the metal to change over time, as micro fractures in the metal cause it to conduct less well, reducing the fuse effective rating.
In the other controller which limits at 15A, I used a 20A fuse and haven't had a problem. The 20A fuse also has a link that is apparently gold plated... maybe to prevent surface oxidation from heating. The 60A one had a plain grey looking link.