News: Anyone wishing to register as a new member on the forum is strongly recommended to use a "proper" email address - following recent spam/hack attempts on the forum, all security is set to "high", and "disposable" email addresses like Gmail, Yahoo and Hotmail tend to be viewed with suspicion, and the application rejected if there is any doubt whatsoever
 
Recent Articles: Yingli Green Energy's PV Module Ranks No.2 in TUV Rheinland Energy Yield Test | Navitron Solar Showers at Glastonbury for Year 5! | Lights go on in Sierra Leone
   Home   Help Search Login Register  
Pages: 1 [2]   Go Down
  Print  
Author Topic: Oil boiler fault  (Read 7546 times)
pottsiwebber
Full Member
***
Offline Offline

Posts: 167



« Reply #15 on: November 05, 2008, 01:17:50 PM »

My burner whistled / squealed for a while before stopping. It turned out to be the old drive shaft coupling which was slowly eating the "keys" on the plastic part of the coupling allowing it to slip over the metal part attached to the drive end which was causing the squealing sound until it stopped driving the pump all together.
Logged

"If it aint broke you can probably still fix it!"

15kW Kostrzewa Pellet / Wood / Grain boiler
4kW Stovax WBS (2kW to room, 2kW back boiler)
216ltr Navitron thermal store
Navitron solar this spring
Cliff top
Jr. Member
**
Offline Offline

Posts: 93



« Reply #16 on: November 06, 2008, 09:54:50 AM »

Sassen fassen rassen grrrrr Angry

still cycling.

Getting closer though... May be the controller faulty....I can see the controller bimetallic going across and back as it cycles.
I am now working on the assumption that the flame detection cct is meant to hold the bimetallic at a certain temp stopping it going back to oil solenoid cutoff. New sensor and connection cable checked means it can only be the controller at fault.

Will rig up some wiring at work today to check it out.
Logged

Glass half full...half empty....As an engineer it's obvious the glass is twice as big as it needs to be
Cliff top
Jr. Member
**
Offline Offline

Posts: 93



« Reply #17 on: November 19, 2008, 04:35:31 PM »

To follow up on this for future reference:

Controller was at fault.  Replacement was actually worse! Still awaiting another to try again.

Anyway after running through how the TF830 actually works, established the cause of the problem is the C shaped spring on the 3rd (oil solenoid) contact. It requires enough spring power to flick the contact closed against the magnetism of the photosensor relay coil/plates which hold it closed until the flame goes out. Due to age the spring was a bit weak. Opened the C out a little and bingo it works...well most of the time. The whole thing is just a bit clockwork really.
Logged

Glass half full...half empty....As an engineer it's obvious the glass is twice as big as it needs to be