News: Anyone wishing to register as a new member on the forum is strongly recommended to use a "proper" email address - following recent spam/hack attempts on the forum, all security is set to "high", and "disposable" email addresses like Gmail, Yahoo and Hotmail tend to be viewed with suspicion, and the application rejected if there is any doubt whatsoever
 
Recent Articles: UPDATE ON DECC APPLICATION FOR LEAVE TO APPEAL TO THE SUPREME COURT | Yingli Green Energy's PV Module Ranks No.2 in TUV Rheinland Energy Yield Test | Navitron Solar Showers at Glastonbury for Year 5!
   Home   Help Search Login Register  
Pages: 1 [2]   Go Down
  Print  
Author Topic: Grid frequency sensor  (Read 4156 times)
Rooster
Sr. Member
****
Offline Offline

Posts: 408


Dum Spiro Spero


« Reply #15 on: February 22, 2009, 10:58:02 AM »

Real time Graph of the last 60 mins Grid Frequency .....

http://www.nationalgrid.com/uk/Electricity/Data/Realtime/Frequency/Freq60.htm

Its a pity they don't provide a longer timescale.
Logged

Roy
wdh
Full Member
***
Offline Offline

Posts: 151


« Reply #16 on: February 22, 2009, 11:17:51 AM »

GREAT resource!  Smiley

Quote
System frequency will therefore vary around the 50 Hz target and National Grid has statutory obligations to maintain the frequency within +/- 0.5Hz around this level. However, National Grid normally operates within more stringent 'operational limits' which are set at +/- 0.2Hz.


I wonder how it might be possible to use the 15-sec refreshed (text) data on the right of that page as a data source, absent any public API or RSS feed... ?

If the data is available, live, need one measure it for oneself? (Its identical throughout the grid.)
Logged
KenB
Global Moderator
Hero Member
*****
Offline Offline

Posts: 2691


Energy Self Enlightenment


WWW
« Reply #17 on: February 22, 2009, 04:47:32 PM »

List,

Here's a graph of mains frequency from last February 22nd when I last cared to log the frequency variations.

Approximately 5500 readings, every 5.12 seconds (7.8 hours). 

Note how it has excursions from 49.82Hz to 50.22Hz. As I said earlier "wobbles all over the shop".

The realtime data from the National Grid Company website is artificially smoothed, to obscure the wild transitions.  If they admitted to these frequency transients there would be a queue of people trying to sue them for breach of specification.

The ups and downs of the real grid frequency are a real roller coaster ride. Anyone with £10 of equipment can show this to be the case.  Sod the specs,  NGC are generator cowboys riding roughshod over everything.



Ken








* mains_freq.jpg (80.51 KB, 1024x768 - viewed 266 times.)
« Last Edit: February 22, 2009, 04:51:54 PM by KenB » Logged
billt
Sr. Member
****
Offline Offline

Posts: 465


« Reply #18 on: February 22, 2009, 05:58:10 PM »

They wouldn't get anywhere if they did try to sue the supply companies. The frequency tolerance is +/-1%, or +/- 0.5Hz; your extremes are -0.18Hz, + 0.22Hz and those are very brief and well within spec.

The frequency variations are caused by the imperfect matching of supply and demand and as demand is not within the control of the supplying providers the performance seems pretty good to me.

The frequency of the mains supply is unimportant anyway, within the specified tolerances, so I can't see why it seems to upset you!

Logged
wdh
Full Member
***
Offline Offline

Posts: 151


« Reply #19 on: February 22, 2009, 06:25:13 PM »

Seems I'm cross-posting with billt, but There's enough difference to leave it be!


Here's a graph of mains frequency from last February 22nd when I last cared to log the frequency variations.

Approximately 5500 readings, every 5.12 seconds (7.8 hours). 

Note how it has excursions from 49.82Hz to 50.22Hz. As I said earlier "wobbles all over the shop".

The realtime data from the National Grid Company website is artificially smoothed, to obscure the wild transitions.  If they admitted to these frequency transients there would be a queue of people trying to sue them for breach of specification.

The ups and downs of the real grid frequency are a real roller coaster ride. Anyone with £10 of equipment can show this to be the case.  Sod the specs,  NGC are generator cowboys riding roughshod over everything.
Ken, I'm not quite sure where you are coming from here.

You say you have seen variation from 49.82 to 50.22 Hz.

The National Grid say that their own target "operational limits" are 48.80 to 50.22 Hz.

Yout graph indicates that your measurements show that they achieved their target for all but a few (5, 10, maybe 15 seconds) of the near 8 hours you logged. So, of the 5500 readings, was it 1, 2 or 3 of them that were outside NG's target?


The statutory requirement is for 49.50 to 50.50 Hz.
But their "operational limits" are more than twice as tight as the law requires.


Not a single one of your readings indicated that the frequency was even half way to breaching the statutory limit, so I'm not sure why you think there "would be a queue of people trying to sue them for breach of specification".
NG's target is to be in the central 40% of the permitted range.
And in your test, more than 999 times out of 1000 you found them to be within their target range.

To me that isn't "all over the shop" - it is constantly varying, but WELL within the permitted amount of variation.




Quote
NGC are generator cowboys riding roughshod over everything
I don't understand this.
Do you think that National Grid are generating anything?
Do you think that frequency variation is a result of poor generators, or something?

The basis of all of this is that as the load on the grid changes - for example when you put the kettle on - that causes the grid frequencyto change.
The more kettles, the slower the frequency.
So, as the frequency drops, NG have to bring in more generation capacity, which brings the frequency up.
But when you turn your kettle off, up goes the frequency, and they need to disengage a generator.

The grid frequency - of every national grid - varies all the time.
Because all the time there are people turning equipment on and off - and each one makes a small change to the grid frequency.
The frequency does change - all the time. That is the nature of the beast.
The question is as to how well NG manage to match the generator's supply with the highly variable demand from 60 million of us doing our own thing, whenever we please, without EVER thinking if it is OK by the Grid for us to have a pot of tea!


The statisticians (and its their job) reckon that if "stuff" could 'ask the grid' if its OK to turn on now, then the grid could be run more efficiently, with less generating capacity running on standby (that's what cooling towers are about).
And an element of that scheme would be having freezers (for example) not starting while the grid was slow. A few seconds or even minutes wait won't spoil the contents of the freezer, but it would lighten the load at a time when it was just slightly too heavy.

So 'smart' devices, acting with swarm intelligence (so they don't all do exactly the same thing at the same time), would help to stabilise the grid frequency as well as reduce the waste caused by the requirement to have plenty reserve generators "spun up" and ready to contribute within a fraction of a second.


Because vastly most of the grid load is made up of millions of tiny loads, the frequency varies fairly smoothly -- although continually!
One of the difficulties with DIY measurement is screening out electromagnetic 'noise' (from computers, cellphones, allsorts), which get picked up by house wiring and will cause a measurement error - appearing as 'jitter', rapid variation - which the grid (because of its size) can't and doesn't do.
This isn't about 'artificial smoothing' - its a matter of making sure that you are measuring the grid, rather than your local environment!
« Last Edit: February 22, 2009, 06:29:18 PM by wdh » Logged
Ivan
Guest
« Reply #20 on: February 22, 2009, 10:13:58 PM »

It might be worth commenting in this thread, that the National Grid is frequently out-of-spec as far as G83 grid-tie inverters are concerned. Particularly for people living in remote locations, the voltage is often out of spec, and for all people, the frequency and change-of-frequency may also be out of spec on a regular basis.
 
The upshot is, the prevention of grid-feeding of microgeneration power for periods of time. Usually not for long, but in some cases, it can be for hours at a time.
Logged
wdh
Full Member
***
Offline Offline

Posts: 151


« Reply #21 on: February 22, 2009, 10:40:08 PM »

It might be worth commenting in this thread, that the National Grid is frequently out-of-spec as far as G83 grid-tie inverters are concerned. Particularly for people living in remote locations, the voltage is often out of spec, and for all people, the frequency and change-of-frequency may also be out of spec on a regular basis.
 
The upshot is, the prevention of grid-feeding of microgeneration power for periods of time. Usually not for long, but in some cases, it can be for hours at a time.
Ivan, "voltage in remote locations" is surely going to be a matter of the local distribution company (rather than the National Grid) being under-developed.

Can you please point me at a reference or previous discussion regarding the problems with grid-tie inverters?
Logged
wyleu
Guest
« Reply #22 on: February 23, 2009, 07:07:39 AM »

Perhaps this is why we like to measure it.

The relationship between a large company and an individual often starts with that organisation telling us what a wonderful job it does whilst the consumer base complains like crazy about how bad the service is. Given that the tendency in specification of the mains is a widening not a tightening of quality then I think we are perfectly within our rights to question the provision. Whilst it's one of complaining us the companies can, and do, sleep easily, If it becomes enough of us, then perhaps the level of respect accredited to the other end of the wire might be to the benefit of both.
Logged
EccentricAnomaly
Guest
« Reply #23 on: February 27, 2009, 04:07:29 PM »

Regarding http://www.nationalgrid.com/uk/Electricity/Data/Realtime/Frequency/Freq60.htm wdh wrote:

I wonder how it might be possible to use the 15-sec refreshed (text) data on the right of that page as a data source, absent any public API or RSS feed... ?

That data is in an iframe which is fetched from http://www.nationalgrid.com/ngrealtime/realtime/systemdata.aspx so it would be easy to write a script to use wget or curl or whatever to fetch it and extract the data.  I'd use tagsoup and XSLT for the extraction; that combination is a bit of a nuclear nutcracker but something I've used a lot.