Welcome to the Solar Forum Control/Electrical FAQThis section of the Solar Forum FAQ covers the
Solar Controllers and
electrical aspects of a solar installation.
It can also be found on the Wiki section of the website at
http://www.navitron.org.uk/pmwiki/pmwiki.php?n=SolarThermal.SolarThermalControlsAndElectricalAspectsFAQ
For the Solar Forum
Plumbing FAQ please see
http://navitron.org.uk/forum/index.php?topic=276.msg1526#msg1526 or on the Wiki at
http://www.navitron.org.uk/pmwiki/pmwiki.php?n=SolarThermal.SolarPlumbingFAQThe FAQ has being split due to maximum post length being reached, thus preventing additions
It is intended to
supplement the FAQ on the
Navitron website see
http://www.navitron.org.uk/faqdetail.php?id=5 and is based on common questions and discussion threads within the Forum.
There is also plenty of information on the Solar section of the website see
http://www.navitron.org.uk/page.php?25 including downloadable files.
Please note: This topic is
locked to prevent it becoming an eternal thread, as it is intended to be an FAQ only. It will be updated whenever suitable topics arise.
What are the differences between the solar controllers?The Resol
DeltaSol A is a basic solar controller with one output to control the solar pump and supplied with two sensors. Simple setup with adjustable DeltaT setting and selectable freeze-protection only.
The
DeltaSol Ax adds adjustable maximum and minimum temperature operating limits and a manual operation switch (useful for setting up and testing).
The
DeltaSol B/1 is a basic digital controller with one output to control the solar pump and is supplied with two sensors (for manifold and lower cylinder sense).
The
DeltaSol BS/3 is a higher specification controller including:
- an additional relay output to control the Heat Dump option should the system reach maximum temperature (e.g. when on holiday),
- a Freeze Protection function (controller will prevent manifold from freezing by running solar pump when necessary if antifreeze is not used),
- supplied with additional sensor to monitor the
upper cylinder temperature,
- an optional fourth sensor can be fitted to monitor
Return pipe temperature.
The
DeltaSol BS/4 is similar to the BS/3 but incorporates variable speed control on the solar pump output.
The
DeltaSol BS/Pro controller has two relay outputs allowing
either:
a) Heat dump control as per BS/3 model,
ORb) Independent pump control of East-West facing panels.
The
DeltaSol ES can cope with East-West panels, Heat Dump with virtually any system you could want. Also has RS232 and VBus interfaces. Uses similar user-friendly programming as the BS/3 and BS/4.
The
DeltaSol M does everything except tie your shoe laces - but you may spend as long programming it as installing the system itself

The new
Navitron TDC3 has all the functionality of the Resol BS/4 with several additional functions including automatic Anti-Legionella protection. Additional parameters are used to program the functions and setpoint temperatures hence there are fewer direct equivalents of program parameters when compared to the Resol controllers in the table.
The table below attempts to compare and illustrate the major differences between the Resol range and Navitron TDC3 controllers together with the common control parameter names and values.
It should be noted that Resol products are under continuous development and parameter values can be subject to change between shipments.
| Controller model | A | Ax | B/1 | BS/3 | BS/4 | BS/Pro | ES | M | TDC3 |
| Digital display | No | No | Yes | Yes | Yes | Yes | Yes | Yes | Yes |
| No. sensors possible | 2 | 2 | 2 | 4 | 4 | 4 | 10 | 12 | 3 |
| No. sensors supplied | 2 | 2 | 2 | 3 | 3 | ? | ? | ? | 2 |
| No. relay outputs | 1 | 1 | 1 | 2 | 2 | 2 | 10 | 12 | 2 |
| Variable pump speed | No | No | No | No | R1 | R1-2 | R1-3 | R1-4 | R1 |
| Manual relay control | No | Yes | Yes | HND | HND | HND | HND | Yes | Yes |
| Operation hours counter | No | No | Yes | Yes | Yes | Yes | Yes | Yes ? | Yes |
| DeltaT on setting | Yes | Yes | DO | DTO | DTO | DTO | DTO | Ton | ** |
| DeltaT on range | +2 to 16K | +2 to 16K | +2 to 10K | +1 to 20K | +1 to 20K | +1 to 20K | +1 to 20K | +1.5 to 20K | 0-99 degC |
| DeltaT off setting | Fixed | Fixed | DF | DTF | DTF | DTF | DTF | Toff | ** |
| DeltaT off range | 1.6K | 1.6K | +1 to 9K | +0.5 to 19.5K | +0.5 to 19.5K | +0.5 to 19.5K | +0.5 to 19.5K | +1.0 to 19.5K | 4-20 degC |
| Freeze protection | Yes | Yes | No | OCF / CFR | OCF / CFR | OCF /CFR | OCF / CFR | Yes | Yes |
| - Freeze prot range | Fixed 4C | Fixed 4C | - | -10 to 10C | -10 to 10C | -10 to 10C | -10 to 10C | Fixed 4C | -25 to +10C |
| Collector abs max shutdown | No | No | CL | EM | EM | EM | EM | Tcolnot | Yes** |
| Shutdown limit range | | | 110-200C | 110-200C | 110-200C | 110-200C | 110-200C | 110-200C | 60-150C |
| Max Store temp | No | Preset | SX | SMX | SMX | SMX | SMX | Tspmax | Yes** |
| - Max Store value range | - | 20 to 90C | 2 to 85C | 2 to 95C | 2 to 95C | 2 to 95C | 2 to 95C | 4 to 95C | 0-99C |
| Min Collector temp | No | Preset | CN | OCN / CMN | OCN / CMN | OCN / CMN | OCN / CMN | ? | TminS1 |
| - Min Coll value range | - | 20 to 90C | -10 to 90C | -10 to 90C | -10 to 90C | -10 to 90C | +10 to 90C | ? | 0-99C |
| Dual East-West panels | No | No | No | No | No | Yes1 | Yes | Yes | Yes |
| Thermostat function | No | No | No | AHO / AHF | AHO / AHF | AHO / AHF1 | AHO / AHF | Yes | Yes |
| Heat Dump control range | - | - | - | 0 to 95C | 0 to 95C | 0 to 95C | 0 to 95C | ? | 0-99C |
| Heat Quantity Balancing 2 | No | No | No | Yes | Yes | Yes | Yes | Yes | Yes |
| Re-cooling function | No | No | FN2 | OREC | OREC | OREC | OREC | Yes | Yes |
| Collector cooling function | - | - | FN3 | OCX / CMX | OCX / CMX | OCX / CMX | OCX / CMX | Tcolmax | ** |
| - Coll cooling range | - | - | - | 100 to 190 C | 100 to 190C | 100 to 190C | 100 to 190C | 80 to 160C | 60-150C |
| Language selection | N/A | N/A | En | En/Ge/It | En/Ge/It | En/Ge/It | En/Ge | En | En |
| Controller model | A | Ax | B/1 | BS/3 | BS/4 | BS/Pro | ES | M | TDC3 |
Note
1: Not simultaneously
Note
2: With optional flowmeter(s)
Note ** The TDC3 controller uses additional programming parameters and is different to program from the Resol controllers
The temperature sensor cable is not long enough!The Platinum Resistance Thermometer (PRT) temperature probes used are simple resistive devices. They can be readily extended using any twin flex or bell-wire. It is best to use screw-terminal blocks (choc-blocks) with the built-in wire protectors to prevent damage to the wires.
How hot will the water get?Using a dedicated solar controller such as the
Resol BS/3 allows accurate control of the water temperature circulating around the system and maximises the efficiency of the system.
The controller monitors the temperature difference between the panel manifold and the lower cylinder sensor.
The circulating pump is triggered when the difference exceeds the
DTO setting (say 6 degrees)
The pump will stop once the difference drops below the
DTF setting (say 4 degrees).
This means that if the cylinder (base) temp is 25C then the pump will start to run when the manifold temp reaches 31C.
As the water circulates and gives off its energy to the stored water the temperature in the cylinder will rise and the circulating water will drop.
Once the difference drops below 4 degrees then the pump will stop.
Therefore the actual cylinder temperature achieved will depend on the amount of solar radiation received by the panel on a given day and the volume of DHW used by the household in the meantime.
Do I need a Heat Dump?OK - so this is the controversial one and has been the subject of much debate on the Forum - just put
Heat Dump into the
Search box....

The usual recommended cylinder temperature is 60-65 degrees C for a conventional DHW system. However a well designed solar system has the potential to exceed this during summer months - especially, and most importantly, when the householder is away for any length of time, e.g. on summer vacation.
If a solar system is designed so as to never exceed 65 deg C cylinder temperature under any circumstances (without a Heat Dump) then its performance will be marginal and it is unlikely to result in the expected fossil-free summer months of DHW production.
It has been confirmed that the
Navitron supplied cylinders are guaranteed by the manufacturer to withstand and be functional to 95 degrees C. (Note: Do not assume that other manufacturers will automatically offer a similar guarantee!)
In theory[/i], this negates the need for a
Heat Dump on a correctly sized system. However,
anyone who installs a system that is 'permitted by design' to operate at elevated temperatures
must install a
Thermostatic Mixing Valve (TMV) on the outlet of the cylinder. This is
essential to prevent a virtually guaranteed scalding injury that would result from skin contact with DHW at elevated temperatures. Anyone who doubts the wisdom of doing this should refer to the
Thermostaic Mixing Valve Association website at
http://www.tmva.org.uk/. A professional installer should be aware that there would be little chance of a defence in court for scald injury claims resulting from an inadequately controlled solar system (since a competent installer should know that a well-designed solar system is potentially capable of producing dangerously high DHW temperatures under high insolation conditions.)
That said, you need to decide what temperature you are prepared to accept as stored water. Consider also that where the cylinder is permitted to operate at elevated temperatures, the solar loop will be DTO degrees hotter. This may have implications on long term reliability of components especially the pump.
It may well be that you prefer to dissipate the significantly excess thermal energy via another route such as a dedicated Heat Dump or existing CH radiator(s).
The maximum cylinder temperature can be set in the controller using the
SMX setting (on BS/3) which could be reached on days where there is no water drawn off (the occupants are on holiday for example). Before this point, there is a need to reduce the temperature of the stored water - via a heat dump.
For the Heat Dump control functions to work (and be accessible from the keypad) the BS/3
System Mode must first be set to "
Arr 2".
If you are running the Heat Dump using
AHO and
AHF parameters,
SMX needs to be set to a value of at least
AHO + DTO - this is to allow the solar loop to continue loading the cylinder/store whilst the Heat Dump is operating.
AHO should ideally be 0.5
higher in value than
AHF e.g. AHO= 68.0, AHF=67.5
How do I wire it all up?The electrical wiring must conform to BS7671 IEE 17th Edition and Part P of the Building Regulations. If the Heat Dump is incorporated utilising the boiler coil with the boiler inhibited via a relay, it is
essential that both boiler and solar systems are supplied from the
same socket or DP switch-fused spur. This is to prevent electrical danger arising from only one 'half' of the linked system being isolated during maintenance work.
This method is easy to implement with boilers having a common-neutral connection between boiler and system pump. Many modern condensing boilers have complex control electronics with the system pump electronically controlled and fed direct from the boiler control PCB. Modification of most of these is not recommended! However the Alpha CDR models are known to be compatible and generic system schematics are available to suit.
Examples of a standardised set of wiring schematics for the common S-Plan, S-Plan+ and Y-Plan heating systems schemes and components can be downloaded in Excel format from:
http://homepage.ntlworld.com/anthony.cooper267/index.html and include information on how to incorporate the
Heat Dump. A new file covering S-Plan based system schemes covering the Alpha CDR range of modern condensing boilers is now included.
Note: I contacted Vaillant earlier in 2011 with a view to adding the EcoTec Plus to the compatible wiring schematics but they failed to respond to my email!