« Reply #4 on: August 26, 2009, 07:33:51 AM » |
|
7.9.1. Speed control = OFF
Is that for sure that variable speed won't be used? (I did see other settings related to variable speed pump)
S5 varies, but only at the start/end of each cycle, its pretty constant whilst the pump is on, and whenever the pump is on.
e.g.
25.08.2009,13:38:15,72,57,48,66,518, 0 25.08.2009,13:38:25,72,57,48,66,519, 0 25.08.2009,13:38:35,72,57,48,66,531, 348 25.08.2009,13:38:45,72,57,48,66,542, 392 25.08.2009,13:38:55,70,57,48,66,542, 406 25.08.2009,13:39:05,68,57,48,66,553, 415 25.08.2009,13:39:15,66,57,48,66,566, 413 25.08.2009,13:39:25,65,57,48,66,578, 417 25.08.2009,13:39:35,65,57,48,66,574, 415 25.08.2009,13:39:45,64,57,48,67,577, 412 25.08.2009,13:39:55,63,57,48,68,578, 412 25.08.2009,13:40:05,63,57,48,68,585, 415 25.08.2009,13:40:15,62,57,48,69,577, 173 25.08.2009,13:40:25,62,57,48,70,569, 0 25.08.2009,13:40:35,62,57,48,71,566, 0
Distribution of values for a given day:
360 15 370 19 380 33 390 51 400 339 410 1076 420 98
values range from 30 to 440, other values are all < 10
Is sensor calibration important (its at factory defaults I think):
Offset S1 = -1 (0.5C per step) Offset S2 = -1 " " " Offset S3 = 0 " " " Offset S4 = -1 " " " Offset S5 = -1 (0.1C per step) Offset S6 = -1 (Correction for the VFS sensor)
|