Thanx Desp I could use a beer..
and back to the main story -
Next job was to beef up the heat exchanger array enough to stand it up and transfer it from the shed floor to the pit.
I wonderd If I should heat test the support legs, aka BT duct, cos incoming pressurised hot water could theoretically reach 110deg c and it would be a proper nuisance if the legs faild.
If I lower the heat exchanger array into a dry pit, I can watch it down but if I lower it into a pit nearly full of water, it will get lighter as it goes down and with some careful measurements will give me an indication of volume, complicated only by a deduction for the volume of copper tube, pressed steel and plastic legs. I sort of need to know the volume of water in the circulation circuit so I can sort of calculate how much inhibitor and antifreeze to add, depending on how much protection I think I need.
Probably simpler to fill the circuit using a measuring jug though.
How to surround the pipes that drop cold water to the bottom with that nice pink hi temp foam as I do not need any cold flows running through the top part of the heatstore ? Expanding foam is always entertaining.
Turned out to be nearly impossible to create a former that would allow me to inject expanding foam into it and end up with a uniform thickness of foam around a pipe.
Might have worked for a totally straight pipe before soldering it into the heat exchanger array. I ended up using HT armaflex and clear silicon for jointing.
In order to get the heat exchanger array off the shed floor without it falling apart or breaking a cheap plastic leg, I gave it lots of triangulation and strapping, using stainless steel tying wire ( left over from the last bridge I helped to build ) and some green polyprop chord that I found. I set up a hoist on a beam that just happened to be more or less above the array, chose four sling points and gingerly lifted the assembly up. Amazingly the contraption seemed to be quite robust and rigid so getting it upright was less stressful than I expected.
Once upright, I was able to do a few final checks and with a re-sling to give a vertical lift, I was able to roll a bike trailer under and strap the array on. So far so good.
The assembly looked really lopsided on the bike trailer with the thing looking like it was leaning a lot more than tolerances would allow. I had not checked the geometry of the legs during assembly and had relied on two templates and visual checks.
I ended up jacking up one side of the bike trailer to try and get the bottom of the legs level so I could assess just how far off upright we were. Not as bad as I thought, so I put it down to the very wavy bit of ply that was covering the trailer.
Then I set up lawn protection and positioned the 6 tonne digger ready for the install. Various sources of help were possible, including four fit and strong young chaps travelling back from a gig in Belfast and another friend who had threatened to 'show up on Sunday'.
Another cup of tea and I decided to carry on on the assumption that I might, or might not, get help. So a careful drive from the shed to the end of the house and everything still looks good so I thought that whilst waiting for help to arrive I might as well try and sling the array and see if I could get it nice and level. I was getting a bit braver with the strength of the legs and decided I would have to risk slinging near the top so I could get the slings off once the array was in the pit.
After several minor adjustments on the different length friction tie downs, it all looked quite tidy so I thought that I would offer it up to the hole just to see if it fitted.
Not so easy on your own but I thought that if I tied a bit of rope to an appropriate leg, I could tinker with the rotation from inside the digger cab. last time I tried this trick, I ended up with an overturned 15 tonne Hymac and a completely wrecked shutter but I was only going to check the fit whilst waiting for help ...
Yeah it looks good, perhaps I could fiddle it in without help ?? So after a few nervous moments and several in and out of the cab circuits, I eventually got the whole assembly in the pit with clearances all round just as I had planned. Phew ! Hi Andy, thanks for coming mate, your just in time to help me unsling the tie downs.Yeah.
The next day I slowly filled the pit with some magic water ( didn't want to stress the tank by quick filling ) and noted a small leak in one of the olive/ compression connections in the top radiator. I had left the incoming heat circuit pressured up and on test. It had dropped from 30 psi (2 bar) to 9psi in a week, so I jacked it up to 30 psi and got a spanner onto the well rounded nut to try and nip the fitting up, to seal it. The water was absolutely freezing and my arms went bright red from being immersed.
I bl00dy hate those olive compression fittings, although theyve become a bit more reliable since I listened to Lord Frot and try to ensure the pipe is not rammed fully into the fitting prior to tightening.
I tested the two 10mm tubes that I inserted behind the thermalite blocks in the pit, because now Ive finally stopped dewatering the area around the concrete sections, both layers of waterproofing are under test. The test was simple enough, suck or blow to see if there's any water got to the bottom of the tubes / heatstore. Suck gave a strong taste of styrene and blow felt smooth and un-restricted. So far so good.
Also, I had to organise some reliable underwater temp sensors, cos once its all in the pit I will not want to revisit the plumbing. I found some cheap hand held thermometers with probes on the end of a meter long wire at
www.thermometersdirect.co.uk and ordered 5.
Being curious, I decided to do some heat testing on various types of insulation.
I made a little nest with some aluminium sheet and tinkered with the heatgun to see how stable I could keep the temperature.
It was pretty simple and it was possible to keep the temp to within a couple of degrees as long as nothing moved.
The kebab in the attached pic shows four different types of insulation that seemed quite happy with a temp of 180-190c for about 10 minutes.
From the bottom there's Navitrons HT armaflex, then there's a bit of ordinary black class 'O' armaflex, then a small chunk of fire resistant ( nice 'n pink) expanding foam and at the top there's a chunk of ordinary green expanding foam.
I also had a loose piece of cellotex foam in there for a while but it got away. The HT, class 'O' and the PU foam all seem to be able to withstand a temp approaching 190c for approx half an hour. I felt I should stay below 200c because that is apparently the limit of the thermometer.
The cheap grey B&Q pipe lagging failed at 90c and simply reduced in volume to become a small lump of congealed snot. Polystyrene was not a lot better.
So fired up with the success of this hi tech testing, I went indoors to re-do the hot / warm / cold flow tests on the Toolstation TMV, especially now that the nice lady at ToolStation has explained to me how that yellow cap is not an adjuster, its a lockshield that has to be removed with an allen key ! Well she did have the advantage of a complete boxed TMV with instructions and an allen key (-;
I didnt need to tell her about removing the non return valves though, although they were a bit reluctant to come out .....
This time I was able to tinker with the temp adjuster on the TMV, whilst flowing various temp water through it 'backwards'. The only thing that concernd me a bit, was the possible restriction to the quantity of water that can flow through the valve.
It would appear that this TMV has the potential to act as a thermostatic diverter valve, with the option to vary the divert temp all the way from cold to 62 deg c.
Which is pretty much what I want it to do.