Thank you Steve.
Ive been a bit 'down' for the last few days and didnt really feel like updating.
Only 5 hours paying work for November, December not looking much better.
Plummin ? hmmmm see below
Never stops 'kin raining ......
Had a few good hot deep baths though -
Ok we are getting close to real time reporting and there's still plenty of opportunity for .........
THINGS TO GO WRONG -
Originally I was going to use temperature probes and a controller, probably another TDC3, to manage the existing CH circuit and extract stored heat.
So a probe like you get with the solar tubes ( well, exactly the same really ) was planned in and set at 1.5m deep, as this seemed to be a good place to make an assessment regarding available heat.
The plan was to only divert the flow through the heatstore on its way back to the oil combi, if heat could be added. So another sensor or two would be required on the pipes before and after the divert, so there would be no chance of burning oil to warm the heatstore.
I know there's arguments for doing an efficient burn with boilers to charge heatstores but if you go back to my opening statement, this project is about becoming independent of oil.
So when the great one at Frotdor suggested that this was possible but ' a bit complicated' I knew I needed a plan B ....
Several long hot baths later ( yes we were cooking water with wood by this time ) and I eventually decided that the KISS principle was probably the best way.
On its way back to the boiler, the CH water would be routed through a 3 way valve then, depending on which port was open, it would either go through the heatstore, back to the boiler cupboard, then through a pump and 'T' into the hot side of the CH circuit beyond the boiler, or it would go through the boiler if the other port was open.
In other words its either CH from the boiler or CH from the heatstore.
Ok that's more action in the boiler cupboard, in an area that's already pretty crowded and I've got to pick up two not very flexible bits of 22mm speedfit pipe, which makes the three way valve the key component.
I've learned that you look for the hardest bit and get it done first then do the next hardest connection, leaving the easiest bit till last.
I often see major projects where they've targeted the easy bit 'to make a show' and I know that we will be struggling to do the hard bits at the end, usually with a deadline looming.
Identify the hard bit and get it done soonest. It will be the key that unlocks the whole job. ( sorry, didn't mean to get up on that little box )
Anyway, I just happened to have a spare three way valve as a result of a previous visit to the 'donut o delite' for tea and teknikal advice and after a bit of research, that involved bare wires and live feeds, I learned that to get the valve to fully open, you join the grey and the white together and energise them. I also discovered that the orange is a switched live that goes live once the valve is fully opened, which made it ideal to use as a feed for the pump.
So that's port A open when there's no power to the valve and water routed through the oil combi, or port B open when the valve is powered up with the pump cutting once its open and the water routed through the heatstore.
So in went the three way valve, the pump and a non return valve on the boiler CH output, in case the new three way valve ever plays up.
Also took the opportunity to put in another half litre of inhibitor as I filled the extended circuit cos I like inhibitor.
Easy enough to fill and flush using the existing CH filling loop but disappointingly difficult to pressure up. Oh dear there's got to be a leak in the new plummin that goes down into the heatstore but how is that possible when I pressure tested all the copper pipe to 5 bar, as I built the circuits up and now I'm only asking for it to hold 1 bar.
Uh - oh, times up. Wife home.
" Yes, all done, just clearing up " .... " so can we use it for heating then ?" " err, not yet, got to balance it all up, hopefully tomorrow " ( if you are not here )
The next day was another wet one but plummin beckoned once more and I had two possible places to access in the hope of finding a leak.
The first one was the top of the heatstore where the heat exchangers connect to the built in pipework using compression fittings, in case I need to remove them )-:
So top off, plastic sheeting off, space blanket off and I cant get the cellotex sheet to move at all and it looks like the small amount of expanding foam I used for the final seal, has continued to expand and the whole sheet is firmly wedged. I ended up using a garden spade to work around the sheet and eventually it released. The foam had apparently come back to life and expanded a bit more as I had lifted the lid before.
Five observations -
The 'water' level in the heatstore was down about 6" from its original fill up level.
There was lots of black flaky deposit, like you get if you plunge red hot copper into cold water, floating on the top.
The copper pipe that was still immersed in the 'water' looked very coppery and new in places.
It stank like a nasty acidic chemical reaction.
The class 'O' Armaflex I had carefully teased onto the cold feed to replace the 'HT' Armaflex, had swollen up and abandoned the pipe and looked like a large dead snake.
Really not good then.
The connections all looked solid and firing up the little electric tyre pump in the boiler cupboard, to identify a leak, showed nothing.
So, time to get the old Subaru fuel pump out and see if there's anything can be pumped out of the insulation layers.
Yup, about 4 buckets full before we started drawing air and its got the same whiff about it as is emanating from the heatstore.
Pretty cold to touch though so not much heat tracking through the insulation.
Bu66ah, that's the GRP layer failed then and no way of knowing if its one leak or if its become porous, cos it doesn't like the hot wet environment but maintained level for three months in summer when the water in the store was cold.
Ok lets try and find that plummin leak -
Moved the big potted bush thingy, stripped down the timber covering on the pipes rising vertically up the outside of the house, cut open the tri iso 10, cut back the HT Armaflex and exposed the speedfit elbows that connected the rising 22mm copper to the horizontal 22mm speedfit plastic that I had to use to bend through the internal wall and there it was bubbling away!
The simplest connection you could get and I had simply failed to push it onto the vertical copper pipe far enough. Also the only fittings that didn't get pressure tested because I had filled and bled all the copper outside the house and didn't want to make a mess testing the two bits of speedfit and the elbow connections.
Well they weren't going to fail were they .......
So connection made good, circuit refilled and bled and pressure tested to 5 bar. Looking good, connected up and filled to 1 bar and the valve opened up to
equalise pressure with the rest of the CH circuit. Sorted. Pump running and warm water going to the radiators. Phew.
Back to the heatstore and all that black flaky stuff had gone, probably knocked down by the rain.
I took the opportunity to put a knuckle bend on the 10mm pipe that I used to pump out the insulation layers and extend it to the outside of the heatstore.
Then topped up the water and put the insulation and cover layers back on.
So was it all just a bad dream ?
Nah, I forgot to put the potted plant back in its corner. Doh ! what a useless twat I obviously am.
Ok, this takes us to about two weeks ago and rather than leave things on a low note I will keep going -
The 12 kw Woodwarm Fireview has been kept going 24/7 and while burning a well filled barrow of dry hardwood a day, is able to keep the house as warm as we would have it normally and supply all the hot water we need.
Which is exactly what I hoped it would do.
It only just held the temp in the kitchen-diner at 18-19c when we had an overnight frost, but generally can just about maintain 20c in this room.
The water in the radiators is only about 45-55c but with constant pumping we can just about get enough heat from the rads to replace the heat being lost.
We drive the woodburner by monitoring the magnetic thermometer stuck on the top boiler. Between 60c and 70c seems to be the magic numbers to keep everything balanced. So quite a lot of the house gets warmed by direct heat from the WBS and the furthest rooms get indirect heat from the heatstore.
Having the CH pickup loop in the bottom two thirds of the heatstore seems to be working ok and around 9.00 in the morning, when I might get round to stoking the fire, the temps in the heatstore will be around 60c for the top third and 55c- 45c for the bottom two thirds, with an obvious step up in temperature above the CH pickup loop.
I will try and write up a few more observations and float a few questions soon as there's still plenty to consider.
In the mean time, I've serviced the 4.5kva diesel genny and am about to build it a permanent shedlet, so it can be accessed and fired up quickly in the event of a power cut. If it ever dries up, I might even dig a 'pit o doom' to shut the exhaust noise down.
A more permanent solution to mains power failure may come from the stream that's rushing past the log shed.
But if anyone knows why the water in the heatstore has gone bad ( pH down 2 units and electrical conductivity way up ) and what I might add to it to neutralise those nasty niffs .........
I would be extremely pleased to hear from them.
Oh yeah and theres the toobs .........
pics -
oh dear