From some of the comments made about ER G83 it appears that many see it as as another piece of government bureaucracy infringing on their "right" to do as they see fit with "their" mains supply. If I want to connect more than the 16A a phase without the agreement of the DNO then why shouldn't I? I have a 60, 80, 100 amp fuse at the supply terminal. Where's the problem? Ministers and Civil servants who know FA telling us what we can and can't do! Oh dear, maybe I shouldn't have written this...... I'm beginning to believe it... YES...YES... I can...I can See the light!
Some time later, medication and a blown light bulb...
How many of us stop for a moment to look at the bigger picture? Consider how lucky we are to have a technical document like G83 and the legal framework in place to Force a DNO to accept a SSEG connection. G83 deserves better, a lot better. Just think what position would we be in without it?
Only a few years ago we had G77 for inverters, this was hard fought for, far from perfect and not in force for long.
Before this G59 ruled. Formal application which is chargeable together with witness testing which is also chargeable. The cost of this stopped the overwhelming majority of small schemes from progressing further than an idea.
Distributed generation especially micro has changed a lot over the last 10 years, DNO's are having to adapt to accommodate these changes and the associated costs. It is not difficult to understand why, relatively few people in these large organisations fully understand what is required of them. Training schools now teach DNO engineers the requirements of G83, for example the WPD school in Taunton.
http://www.sei-energy.co.uk/Project_View?pid=28 There are many different connection situations that G83 needs to accommodate. Below is an example using data from an actual PV installation.
Rated capacity 2900W PV. DC.
AC output on a summer day. 250V. 10.2A 2555W.
Now consider the same location with 3.8kW PV installed. 16A output and low consumer demand.
What is the likelihood of voltage rise in excess of ESQCR limit?
[Firstly refer to ERG831/1.]
2. Scope. Connection Agreements are a legal document supporting SSEG connection and are considered out of scope of G83 doc.
5.1 Connection Procedure.
The DNO may NOT refuse to accept connection providing compliance with ESQCR 22. (We will consider the installation complies)
Under terms of ESQCR 26 the DNO may require a SSEG to be disconnected if it interferes with the quality of supply to others.
[Secondly refer to ESQCR.]
ESQCR 27 Declaration of phases, frequency and voltage at supply terminals
(6) Every distributor shall ensure that, save in exceptional circumstances, the characteristics of the supplies to consumer's installations connected to his network comply with the declarations made under paragraph (1).
(1) Before commencing a supply to a consumer's installation, or when the existing supply characteristics have been modified, the supplier shall ascertain from the distributor and then declare to the consumer -
(a) the number of phases;
(b) the frequency; and
(c) the voltage,
at which it is proposed to supply electricity and the extent of the permitted variations thereto.
(2) Unless otherwise agreed in writing between the distributor, the supplier and the consumer (and if necessary between the distributor and any other distributor likely to be affected) the frequency declared pursuant to paragraph (1) shall be 50 hertz and the voltage declared in respect of a low voltage supply shall be 230 volts between the phase and neutral conductors at the supply terminals.
(3) For the purposes of this regulation, unless otherwise agreed in writing by those persons specified in paragraph (2), the permitted variations are -
(a) a variation not exceeding 1 per cent above or below the declared frequency;
(b) in the case of a low voltage supply, a variation not exceeding 10 per cent above or 6 per cent below the declared voltage at the declared frequency;
[Lets now look for guidance on the above ESQCR SI. This is Law and as so the final interpretation is a matter for the courts.]
Following taken from DTI Engineering Inspectorate. Guidance on ESQCR.
27 (2) Distributors should note that the declared values and tolerances are an absolute requirement, and any variation beyond the voltage limits (apart from exceptional circumstances) without the agreement of the consumer would be treated by DTI as a breach of this regulation.
26 (1)This regulation permits distributors to challenge consumers in circumstances where their installations are unsafe or are causing unacceptable electrical interference on the distributors network. Duty holders should note that the provisions of this regulation may be applied to consumers installations and to other installations or networks.
The ampere limit before DNO involvement is in part, such that the DNO's stay within Law. Remember that if your under 16A phase sseg causes a problem, ESQCR gives the DNO power to act, even though you were within the recommendation to connect.
Already been said, anything over 16A a phase is treated as a 5.1.2 stage 2 connection. Discuss the project with DNO at earliest opportunity, an application form found in appendix 2 should be submitted. No hard questions to answer unless you have difficulty in spelling your name. A site layout plan and a copy of the circuit diagram needs to accompany the form. The DNO has a section to say yes/no for permission and if no comment on the reason.
G83 1/1. is the self installers friend. MCS to qualify for FIT is your enemy.