« Reply #15 on: February 01, 2010, 01:06:18 PM » |
|
We had 132kWh from the PV in Jan 2010 so about 400kWh from the solar thermal.
Attached is a typical trace for the Solar thermal system in January with a clear sky heating 80 m2 of floor in the house alongside our heat pump. The heat pump comes on at 05.30 and heats the floor and the 500lt storage tank. By about midday the solar panels are contributing well and heat the solar storage tank to 40C when the heat pump goes off and stays off for about 5hours. The heat pump switches off at 21.00hrs. The house is at 22C all day. The heat pump draws about 2.5kW. The outside temperature was between 0 and 5C all day.
|
|
|
|
alex2504
Newbie
Offline
Posts: 9
|
 |
« Reply #16 on: February 01, 2010, 09:09:30 PM » |
|
i installed system in october and since mid december i haven't had anything from solar hot water, is this normal for scotland aberdeenshire?
20 tubes, 140 litres
|
|
|
|
« Last Edit: February 01, 2010, 09:11:14 PM by alex2504 »
|
Logged
|
20 x 46mm Thermal and 140ltr vented, south facing.
|
|
|
|
dhaslam
|
 |
« Reply #17 on: February 01, 2010, 09:14:15 PM » |
|
The frosty days in December and January have been very good but did you have a lot of snow? Also what pipe size and length do you have?
|
|
|
|
|
Logged
|
|
|
|
alex2504
Newbie
Offline
Posts: 9
|
 |
« Reply #18 on: February 01, 2010, 09:30:46 PM » |
|
10mm pipes, 19metres
looking at controller, system hasn't been on since mid december, was concerned that the cold weather has done some damage even though i have sufficient anti freeze
|
|
|
|
« Last Edit: February 01, 2010, 09:47:50 PM by alex2504 »
|
Logged
|
20 x 46mm Thermal and 140ltr vented, south facing.
|
|
|
solarcycle
Newbie
Offline
Posts: 19
|
 |
« Reply #19 on: February 02, 2010, 04:47:35 PM » |
|
I'm in Perthshire and the sunny days we've had recently result in a tank of around 42'C top to bottom. I have a twin cylinder setup though with 60 47mm tubes initially feeding 180l.
Are your tubes 47mm or 58mm? If 47mm you are likely to be underpowered as its assumed around 5litres per tube. An extra 10 or 20 tubes would be useful but you'll need some form of heat dump.
|
|
|
|
|
Logged
|
|
|
|
|
dhaslam
|
 |
« Reply #20 on: February 02, 2010, 05:06:51 PM » |
|
Even if the pump isn't running the controller should be showing temperature readings. Is another source heating the bottom of the cylinder?
|
|
|
|
|
Logged
|
|
|
|
alex2504
Newbie
Offline
Posts: 9
|
 |
« Reply #21 on: February 03, 2010, 07:49:56 AM » |
|
solarcycle, Tubes are 47mm x 20 on a 140litre tank.
dhaslam, I am seeing temperatures on the controller. On the panel temp I am seeing very little increase in temperature over the past 6 weeks only 2 or 3 degrees over the ambient, starting to wonder if there could be air in the panel manifold causing this as i don't have an automatic bleeder on the panel.
|
|
|
|
|
Logged
|
20 x 46mm Thermal and 140ltr vented, south facing.
|
|
|
|
langstroth2
|
 |
« Reply #22 on: February 03, 2010, 09:22:12 AM » |
|
alex2504 Even on a dull day when there's no pumping the panel temperature should be quite a few degrees above ambient for a good part of the day, assuming they're not covered in snow. e.g. at the moment it's dull, 9am; ambient 3.7C, panels at 9.6C; yesterday also very dull; peaked at about 32C (no pumping).
I wonder if either: - panel sensor not installed properly in manifold sensor pocket? - air lock in manifold as you suggest? - less likely, but tubes not fully pushed into manifold?
|
|
|
|
|
Logged
|
|
|
|
|
dhaslam
|
 |
« Reply #23 on: February 03, 2010, 10:13:04 AM » |
|
If you could get the pump running, I'm not sure how to do this, it might get it started. If it is an air bubble it would probably go to the top of the panel again but at least it would narrow down the problem.
|
|
|
|
|
Logged
|
|
|
|
|
Greenbeast
|
 |
« Reply #24 on: February 03, 2010, 10:32:33 AM » |
|
well the TDC3 has manual mode, where you can trigger the pump manually.
|
|
|
|
|
Logged
|
|
|
|
alex2504
Newbie
Offline
Posts: 9
|
 |
« Reply #25 on: February 03, 2010, 12:11:05 PM » |
|
Have previously left running in manual mode on pump speed 3 for a couple of hours, very little air was released from bleed point
|
|
|
|
|
Logged
|
20 x 46mm Thermal and 140ltr vented, south facing.
|
|
|
|
Greenbeast
|
 |
« Reply #26 on: February 03, 2010, 12:12:34 PM » |
|
i assume the air valve is the highest point in the system?
|
|
|
|
|
Logged
|
|
|
|
alex2504
Newbie
Offline
Posts: 9
|
 |
« Reply #27 on: February 03, 2010, 12:19:42 PM » |
|
No the air valve isn't on the highest point. the highest point is outside at the panel.
|
|
|
|
|
Logged
|
20 x 46mm Thermal and 140ltr vented, south facing.
|
|
|
|
Greenbeast
|
 |
« Reply #28 on: February 03, 2010, 12:43:03 PM » |
|
Well that's where the air will be if there is any. Why many people fit air bleed valves higher than the panel
|
|
|
|
|
Logged
|
|
|
|
alex2504
Newbie
Offline
Posts: 9
|
 |
« Reply #29 on: February 03, 2010, 05:39:06 PM » |
|
well how silly do i feel..... Temp probe had falling out of manifold and has been like that for over a month.
|
|
|
|
|
Logged
|
20 x 46mm Thermal and 140ltr vented, south facing.
|
|
|
|