News: Anyone wishing to register as a new member on the forum is strongly recommended to use a "proper" email address - following recent spam/hack attempts on the forum, all security is set to "high", and "disposable" email addresses like Gmail, Yahoo and Hotmail tend to be viewed with suspicion, and the application rejected if there is any doubt whatsoever
 
Recent Articles: Navitron Partners With Solax to Help Create A More Sustainable Future | Navitron Calls for Increased Carbon Footprint Reduction In Light of Earth Overshoot Day | A plea from The David School - Issue 18
   Home   Help Search Login Register  
Pages: [1] 2   Go Down
  Print  
Author Topic: Voltage settings for forklift batts  (Read 7268 times)
stephendv
Hero Member
*****
Offline Offline

Posts: 928



WWW
« on: December 13, 2010, 07:29:45 AM »

Phase 1 of my off-grid install is done  Grin  gen + batts + inverter, no solar yet.  Now I'd like to setup the charger to give my batts the longest life possible, while still not wasting too much diesel.  The Sunny Island has 2 charge modes, "boost" and "full".  Basically it uses the boost charge most often to bring the battery from 60% State of Charge to 85% state of charge, and then only uses the "full" charge once every 14 days (configurable) to bring the battery up to 95% state of charge.  So using these 2 charge modes I can set the absorb voltage and absorb time independently. 

The battery distributor (but not the manufacturer) has recommended 2.4V for absorb because it's the "standard".  But the victron multiplus manual has some specific settings for traction batts as opposed to the regular OPzS.  For "Tubular plate traction batteries in semi-float mode" they recommend 2.45V and for "Tubular plate traction batteries in cyclic mode" they recommend 2.5V.

Since I'll only be discharging to 60% SoC, does that qualify as "semi-float mode" ?  What do the other traction batt users use for absorb voltage?

As for the absorb time, I noticed that when I charged the batts yesterday the generator was only really working hard for the first 5 minutes, then the rest of the 2 hour absorb time was spent only outputting 700W or so as absorb current tapered off.  To reduce runtime, I'm thinking of using 2 hours for absorb in the "boost" mode, and 3 hours for "full" mode, so it'll only do a full absorb every 14 days.  Reasonable?



* P1140869.jpg (102.51 KB, 799x531 - viewed 780 times.)
Logged

http://www.casanogaldelasbrujas.com
2.8kW PV, SMA Sunny Island 5048, 5 PzS 700 battery bank, stinky diesel.
billi
Global Moderator
Hero Member
*****
Offline Offline

Posts: 8944



WWW
« Reply #1 on: December 13, 2010, 08:43:43 AM »

Hi

My absorb voltage varies  from 2.45 to  2.55 Volt  depending on the temp of the battery/weather

The temp-sensor of the solar  charge controller adjust that

In an "only" generator set up one should really fully charge from time to time

I am allays surprised how much more AH (after the Battery monitor says 100% charged)  the PV can push into the battery on a sunny day


Billi

Logged

1.6 kw and 2.4 kw   PV array  , Outback MX 60 and FM80 charge controller  ,24 volt 1600 AH Battery ,6 Kw Victron inverter charger, 1.1 kw high head hydro turbine as a back up generator , 5 kw woodburner, 36 solar tubes with 360 l water tank, 1.6 kw  windturbine
stephendv
Hero Member
*****
Offline Offline

Posts: 928



WWW
« Reply #2 on: December 13, 2010, 08:45:54 AM »

My absorb voltage varies  from 2.45 to  2.55 Volt  depending on the temp of the battery/weather

The temp-sensor of the solar  charge controller adjust that

Hi Billi, yes mine does temperature compensation too, but what is your programmed absorb setting in the multiplus?
Logged

http://www.casanogaldelasbrujas.com
2.8kW PV, SMA Sunny Island 5048, 5 PzS 700 battery bank, stinky diesel.
rogeriko
Hero Member
*****
Offline Offline

Posts: 1425



WWW
« Reply #3 on: December 13, 2010, 09:00:11 AM »

I have installed many Sunny Islands and I would just leave the charging settings at standard for flooded batteries. The generator will bring the batteries up to 80% quickly and then gently charge the rest, very slowly. If fuel consumption is an issue this is where solar/wind comes in to play. Charge the batteries to 80% with the generator and then let the panels do the rest. Dont forget the Sunny Island needs a current shunt if you connect panels or wind (ebay 200a 50mv or 60mv) SMA want 90 pounds for this.
Logged

stephendv
Hero Member
*****
Offline Offline

Posts: 928



WWW
« Reply #4 on: December 13, 2010, 09:21:19 AM »

Hi Rogeriko,

Yes, solar is the eventual plan but for the next 6 months I'm going to be running purely on the gen+battery and wouldn't like to damage them with too high an absorb voltage.  The default in the SI is 2.55V which is the highest I've seen in any inverter/charger, it's also the default for all FLA types because the sunny island makes no distinction between different FLA types.  The victron has 2 specific settings for traction batteries which gives me more confidence that there's are more correct than the default in the SI.

I already have the current shunt installed  Smiley ready for the Tristar MPPT when I do the solar part of the install next year.
Logged

http://www.casanogaldelasbrujas.com
2.8kW PV, SMA Sunny Island 5048, 5 PzS 700 battery bank, stinky diesel.
Stuart
Hero Member
*****
Offline Offline

Posts: 665


Engineer ..... at large


« Reply #5 on: December 13, 2010, 09:24:52 AM »

Worth reading through this excellent article for the theory http://batteryuniversity.com/learn/article/charging_the_lead_acid_battery

Stuart
Logged

8kw woodburner, Big piles of wood, 20 tube solar panel, custom tanks, back up gas boiler, North walls internally insulated
1968 landy that runs on anything and a currently wild meadow garden.

Nr. Tow Law
Justme
Hero Member
*****
Offline Offline

Posts: 3530


« Reply #6 on: December 13, 2010, 09:50:41 AM »

I think you are headed for trouble.

Only (almost) fully charging every 2 weeks & then absorbing for 2 or 3 hours is madness.

Bat life reduction would be a given.

I would not call 60% SOC semi float when you 50% SOC is full deep cycle.

A full recharge cycle will take more like 8 to 12 hours MINIMUM.

YES it costs in genny run hours & fuel. But get your other stuff online & correctly sized & then its only for in the winter and poss odd weather periods / extra heavy use.

I would ALWAYS use the bat makers charge specs.

Do not use the Victron adaptive charging its pants & reduces charge absorb times far to much.
Logged

Navitron solar thermal system
30 x 58mm panel 259L TS
1200watts solar 120vdc
FX80 Solar controller
Victron 12v 3000w 120a
6kva genny
6 x 2v cells 1550amp/h 5C
24 x 2v cells 700amp/h 5C
Total bank 4350 amp/h 5C
stephendv
Hero Member
*****
Offline Offline

Posts: 928



WWW
« Reply #7 on: December 13, 2010, 10:46:49 AM »

Unfortunately the manufacturer hasn't responded about the correct voltages yet, the manual just says that all charging procedures that conform to DIN 41773 and DIN 41774 are acceptable. 
And in another section: charging is complete when the density of the electrolyte and the voltage remain constant for more than 2 hours.  So I guess I could experiment with different absorb times and keep measuring SG and then add another 30 mins to be safe.  How long do think is an appropriate time between full charges?
Logged

http://www.casanogaldelasbrujas.com
2.8kW PV, SMA Sunny Island 5048, 5 PzS 700 battery bank, stinky diesel.
Justme
Hero Member
*****
Offline Offline

Posts: 3530


« Reply #8 on: December 13, 2010, 05:00:50 PM »

Time between full charges is a compromise. You should use it & then recharge straight away.
The longer you leave it the less time the bats will live. I try to do it weekly ish. When the charge is about 1% of bank cap at 5c I call it a day.

You dont need or want the victron charger settings to stop the charge, use the VS to turn the genny off when conditions are met.
Logged

Navitron solar thermal system
30 x 58mm panel 259L TS
1200watts solar 120vdc
FX80 Solar controller
Victron 12v 3000w 120a
6kva genny
6 x 2v cells 1550amp/h 5C
24 x 2v cells 700amp/h 5C
Total bank 4350 amp/h 5C
The Slow Old Man
Newbie
*
Offline Offline

Posts: 36


I couldn't be more chuffed with our wind turbine


« Reply #9 on: December 20, 2010, 09:06:53 PM »

Hi Justme
What settings are you using for your victron if not the adaptive mode?

Brian
Logged

The person who never made a mistake never made any thing
Justme
Hero Member
*****
Offline Offline

Posts: 3530


« Reply #10 on: December 20, 2010, 09:33:15 PM »

I'll just plug it in & see cos it was set up a while ago.


 tumble tumble tumble


Right

Charger settings

Fixed mode
Absorb 14.7v (that contains an adjustment for the accuracy of the Victron & losses in the 120mm2 cable & connectors)
Float 13.8v (but if its in float you should be turning the genny off unless you are using the bulk of the power for a job that you dont want to power via the inverter)
Absorb time 5 hours
Repeat absorb 1 day (but is subject to the genny being on)
repeat absorb 1/2 hour (but in reality never happens)
charge current 120amps
Battery type (personal settings
I dont set the stop after 10 hour bulk as the genny would not be on for that long often & even from as flat as I take it it could not still be in bulk after that amount of time

I also manually force an EQ charge every now & then when I am going to have the genny on for a long time anyway.
Logged

Navitron solar thermal system
30 x 58mm panel 259L TS
1200watts solar 120vdc
FX80 Solar controller
Victron 12v 3000w 120a
6kva genny
6 x 2v cells 1550amp/h 5C
24 x 2v cells 700amp/h 5C
Total bank 4350 amp/h 5C
The Slow Old Man
Newbie
*
Offline Offline

Posts: 36


I couldn't be more chuffed with our wind turbine


« Reply #11 on: December 20, 2010, 09:53:46 PM »

Hi Justme
Interesting so what about the bulk charge? you say that the absorption charge is five hours at 14.7V does the current decrees over this time?

Brian
Logged

The person who never made a mistake never made any thing
billi
Global Moderator
Hero Member
*****
Offline Offline

Posts: 8944



WWW
« Reply #12 on: December 20, 2010, 10:05:10 PM »

I was on adabtive , but as far as i know , that over rights your time stings , so on fixed as well

Here the help page from the victron software VE configure


Regards Billi

Quote
  See also   |Where?

Charge curve
With this setting one can choose between three different charge curves:

 

Fixed
Adaptive
Adaptive + BatterySafe
 

The Fixed charge curve will have a fixed absorption time

The Adaptive and Adaptive + BatterySafe curves derive the absorption time from the Bulk time. The maximum absorption time of these charge curves is determined by the absorption time setting.

 

The Adaptive + BatterySafe curve has a special regulation in the absorption phase. The absorption phase will start when the voltage reaches 14.4V (for a 12V battery) regardless of the specified absorption voltage. During the absorption phase the voltage will increase with a fixed ramp until the voltage reaches the absorption voltage or until the calculated absorption time is over. In the latter case the absorption phase will end before the absorption voltage is reached.

 

Please refer to the manual for a more detailed description of the charge process.

 


Logged

1.6 kw and 2.4 kw   PV array  , Outback MX 60 and FM80 charge controller  ,24 volt 1600 AH Battery ,6 Kw Victron inverter charger, 1.1 kw high head hydro turbine as a back up generator , 5 kw woodburner, 36 solar tubes with 360 l water tank, 1.6 kw  windturbine
Justme
Hero Member
*****
Offline Offline

Posts: 3530


« Reply #13 on: December 20, 2010, 10:13:18 PM »

Hi Justme
Interesting so what about the bulk charge? you say that the absorption charge is five hours at 14.7V does the current decrees over this time?

Brian

I dont understand what you mean, "what about the bulk charge"

The definition of bulk is that the batteries are taking ALL the current (amps) that the charge source can supply at the rising voltage without hitting the point where the absorb set voltage is reached. So its in bulk till the bat charge voltage reaches 14.7v. The current during that time does go down slowly (but as the V is rising the total "power" in is very similar). Then once the fixed V stage starts (thats the absorb stage) the V stays constant at your set point whilst the current (amps) lowers. On my 1550amph 5c bank if I keep the genny on for a long time I can get it as low as 5amps but I more normally stop at 25 or 15amps. Which is about 1% of bank capacity.
Logged

Navitron solar thermal system
30 x 58mm panel 259L TS
1200watts solar 120vdc
FX80 Solar controller
Victron 12v 3000w 120a
6kva genny
6 x 2v cells 1550amp/h 5C
24 x 2v cells 700amp/h 5C
Total bank 4350 amp/h 5C
Outtasight
Hero Member
*****
Offline Offline

Posts: 886



WWW
« Reply #14 on: December 22, 2010, 11:53:32 PM »

I think you are headed for trouble.
Only (almost) fully charging every 2 weeks & then absorbing for 2 or 3 hours is madness.
Bat life reduction would be a given.
I would not call 60% SOC semi float when you 50% SOC is full deep cycle.
A full recharge cycle will take more like 8 to 12 hours MINIMUM.

Absolutely!  Car batteries spend their life in semi-float mode (discharged a few times a day by 1% at most, and then immediately put on float charge).  UPS batteries spend almost their whole 5 year life in float mode.  Any off-grid usage will be definitely cyclic / deep-cyclic mode.

Under-charging does more damage than over-charging.  Under-charging causes rapid, cumulative, and permanent loss of capacity from sulphation whereas over-charging causes excessive gassing (water consumption) and positive grid corrosion.  You can limit the damage of over-charging by keeping the water topped right up, as that causes less of the positive terminals to be exposed above the water line.  The pure water reforming on the positive bits of the terminals causes the lead to slowly dissolve away, as well as some other undesirable side reactions below the water line.  The more the cell gasses, the more corrosion occurs.

I also cut absorption at about 1% of bank capacity current (5A going into my 500Ah bank).  For cyclic use, you should use the upper end of the range of the specified float Voltage too.  When you're done with the absorption phase, you'll still only be maybe at ~90% SoC.  The last 10% takes AGES at the float Voltage (more hours than you've probably got before the next discharge cycle), so they recommend increasing the float Voltage a bit.  It allows the cells to fill up a bit faster than at the lower "standby" float level (that you'd use for batteries in a UPS that can be on float for months) but doesn't cause loads of gassing, like it would if you left them on the absorption limit for a few hours.  You can't force the last few % in... It has to be coaxed in.  Bad news when you have to run a generator to do it.  Maybe you could switch to a much smaller generator for the "final push"? 

It may even be worth having a small, cheap 100Ah battery as a "sacrificial buffer battery" that allows the main bank to continue float charge (using a small 250W inverter / charger) after you've switched off the generator.  This buffer battery can supply the small float current to the much bigger (much more expensive) battery, to trickle in the last 50Ah to get it as close to 100% as possible every day.  The cheapo battery will cycle 50% or more per day and will die at regular intervals of maybe every 120 days.  You'd have to weigh the quarterly cost of a 70 battery against the cost of running the diesel generator for the extra hours (fuel, wear and tear, servicing costs). You'd also extend the life of the main bank by minimising the cumulative capacity loss from not charging it to 100% every day.  But then again, a couple of years of blowing money on cheapo "consumable" batteries would needle you into buying those solar panels and the Tristar...

Doing the equalisation charge should be done only after a normal absorption phase and after the battery has had time to cool down a bit and then it should be started only under manual control and supervision (you wouldn't leave a chip pan, on full gas, unattended, now would you?).  The EQ Voltage will cause a LOT of gassing and quite a bit of water loss, so check the water before starting the cycle and after finishing it.  EQ charging also runs the risk of cell thermal runaway in extreme cases, not to mention the risk of all that gas. 
Logged

http://solarbodge.blogspot.com/
3.58kWp & 800Ah LiFeYPO4 off-grid(ish). See 'Cobbled together PV in W.Sussex' (in "Show Us Yours")