News: Anyone wishing to register as a new member on the forum is strongly recommended to use a "proper" email address - following recent spam/hack attempts on the forum, all security is set to "high", and "disposable" email addresses like Gmail, Yahoo and Hotmail tend to be viewed with suspicion, and the application rejected if there is any doubt whatsoever
 
Recent Articles: Navitron Partners With Solax to Help Create A More Sustainable Future | Navitron Calls for Increased Carbon Footprint Reduction In Light of Earth Overshoot Day | A plea from The David School - Issue 18
   Home   Help Search Login Register  
Pages: [1] 2 3   Go Down
  Print  
Author Topic: panels to battery 40m  (Read 8075 times)
greenhouseparos
Full Member
***
Offline Offline

Posts: 228



« on: August 27, 2011, 10:16:58 AM »

hi
i am installing 20 suntech 190+ad panels in a stand alone system. the panels have to be mounted 40m away from the batteries which is causing me some problems with cable sizing. my current idea is to use 2 morning star 60a mppt chargers with 2 10 panel strings wired for 72v (2 panels series) 5 parrele pairs. this will need 16mm cable for a 3-4% volt drop.
chargers + cable will cost about 1500euro.
if i fitted a inverter directly under the panels and run 220v to the batteries how would i charge the batteries? could i conect to the main inverter stecca 3500xtm  (which has a battery charger) or would i need a seperate charger.
Logged

2660wp array, 1000amp 24v Ops battery bank, 3500XTM Struder24v, 80amp Outback, 750w Wind Turbine, Solar powered water supply
Off Grid and loving it
Justme
Hero Member
*****
Offline Offline

Posts: 3530


« Reply #1 on: August 27, 2011, 10:21:30 AM »

I would look at raising the array voltage by about double to quarter the cable size needed for the same losses. So look at other charge controllers / inverters that can take the higher voltages.
Logged

Navitron solar thermal system
30 x 58mm panel 259L TS
1200watts solar 120vdc
FX80 Solar controller
Victron 12v 3000w 120a
6kva genny
6 x 2v cells 1550amp/h 5C
24 x 2v cells 700amp/h 5C
Total bank 4350 amp/h 5C
billi
Global Moderator
Hero Member
*****
Offline Offline

Posts: 8946



WWW
« Reply #2 on: August 27, 2011, 10:39:56 AM »

stecca   is same as studer-innotec i think   and they have perhaps better information  about "AC-coupling"  and as far as i know you can have a Grid tie inverter connected  , but i think your PV Panel size will exceed the  inbuilt charger capacity (of your stecca 3500xtm )

If you would have a 48 volt system you only need one  MPPT chargecontroller
Billi
Logged

1.6 kw and 2.4 kw   PV array  , Outback MX 60 and FM80 charge controller  ,24 volt 1600 AH Battery ,6 Kw Victron inverter charger, 1.1 kw high head hydro turbine as a back up generator , 5 kw woodburner, 36 solar tubes with 360 l water tank, 1.6 kw  windturbine
billi
Global Moderator
Hero Member
*****
Offline Offline

Posts: 8946



WWW
« Reply #3 on: August 27, 2011, 11:05:59 AM »

Ah  ....  Perhaps a mixed idea would be elegant  

a small Grid tie inverter ( not at the panels  better close to off grid inverter ) and run the high DC Voltage  cables  to him  

this inverter adds then power to your off grid one during the day  and the rest of the panels connected to one MPPT controller to charge batteries directly  

I had a look at your Stecca inverter and they say it can handle 90 A   of AC charge  so about 2300 watt

Perhaps not much more expensive  tumble

have a read here and click on "Partial AC-coupling in Minigrids"


 http://www.studer-innotec.com/?cat=whitepapers  
« Last Edit: August 27, 2011, 11:13:37 AM by billi » Logged

1.6 kw and 2.4 kw   PV array  , Outback MX 60 and FM80 charge controller  ,24 volt 1600 AH Battery ,6 Kw Victron inverter charger, 1.1 kw high head hydro turbine as a back up generator , 5 kw woodburner, 36 solar tubes with 360 l water tank, 1.6 kw  windturbine
greenhouseparos
Full Member
***
Offline Offline

Posts: 228



« Reply #4 on: August 27, 2011, 12:15:15 PM »

I would look at raising the array voltage by about double to quarter the cable size needed for the same losses. So look at other charge controllers / inverters that can take the higher voltages.

using the morningstar 60a i could get the voltage up to 109v 3 strings of 3 but this uses only a total of 18 panels which would mean another controller. do you know any charger makes that can handle larger voltages?
Logged

2660wp array, 1000amp 24v Ops battery bank, 3500XTM Struder24v, 80amp Outback, 750w Wind Turbine, Solar powered water supply
Off Grid and loving it
greenhouseparos
Full Member
***
Offline Offline

Posts: 228



« Reply #5 on: August 27, 2011, 12:17:59 PM »


If you would have a 48 volt system you only need one  MPPT chargecontroller
 
saddly costs prevented a 48v system as the batteries would have doubled.
Logged

2660wp array, 1000amp 24v Ops battery bank, 3500XTM Struder24v, 80amp Outback, 750w Wind Turbine, Solar powered water supply
Off Grid and loving it
Justme
Hero Member
*****
Offline Offline

Posts: 3530


« Reply #6 on: August 27, 2011, 01:12:27 PM »


using the morningstar 60a i could get the voltage up to 109v 3 strings of 3 but this uses only a total of 18 panels which would mean another controller. do you know any charger makes that can handle larger voltages?


Outback FM60 or 80 both do 145v. You can over size the array to controller. The extra amps just dont get captured. I have a theoretical 100amps from my array but have used an 80amp controller.


Quote

 
saddly costs prevented a 48v system as the batteries would have doubled.

Not quite true.

You still need the same total stored energy even though its a 48v bank. So the AH capacity can be 1/4 of the 12v banks.


If you use 3kWh per day & want 3 days autonomy then you need 3 kWh x 3 days x 2 (so you never go below 50%) = 18kWh

18kWh @ 12v = 1500ah or 15 x 100ah 12v bats (not that you should ever use a bank of that many bats)
18 kWh @ 48v = 375ah or 16 x 100ah 12v bats

The only way it can cost more is if you have a total need of less than 2.4kWh (so a 4.8kWh bank) so thats a usage of less than 800wh per day.


edit to add


why not have the bats near the array & have the inverted power travelling the distance?
« Last Edit: August 27, 2011, 01:14:12 PM by Justme » Logged

Navitron solar thermal system
30 x 58mm panel 259L TS
1200watts solar 120vdc
FX80 Solar controller
Victron 12v 3000w 120a
6kva genny
6 x 2v cells 1550amp/h 5C
24 x 2v cells 700amp/h 5C
Total bank 4350 amp/h 5C
camillitech
Hero Member
*****
Offline Offline

Posts: 5417



WWW
« Reply #7 on: August 27, 2011, 04:31:31 PM »

In the grand scale of your considerable investment is 40m of 16mm square really that expensive  Huh http://www.tlc-direct.co.uk/Main_Index/Cable_Index/Armoured_SWA/index.html 178GBP for 16mm as opposed to 65GBP for 4mm   Huh or am I missing something. My wind turbine's 160m from my battery bank and my hydro turbine 470m, the one I'm currently installing is 1000m away  Shocked Think yourself lucky  Grin

Good luck, Paul
Logged

http://lifeattheendoftheroad.wordpress.com/

'Off grid' since 1985,  Proven 2.5kW, Proven 6kW direct heating, SI6.OH, 800ah Rolls, 4.75kW PV ,4xTS45, Lister HR2 12kW, , Powerspout pelton, Stream Engine turgo, 60 x Navitron toobs and a 1500lt store. Outback VFX3048 and 950ah forklifts for backup,
Justme
Hero Member
*****
Offline Offline

Posts: 3530


« Reply #8 on: August 27, 2011, 04:36:22 PM »

You could also do a cost benefit analysis to see if the net gain from the bigger cable is worth the cost.
Logged

Navitron solar thermal system
30 x 58mm panel 259L TS
1200watts solar 120vdc
FX80 Solar controller
Victron 12v 3000w 120a
6kva genny
6 x 2v cells 1550amp/h 5C
24 x 2v cells 700amp/h 5C
Total bank 4350 amp/h 5C
greenhouseparos
Full Member
***
Offline Offline

Posts: 228



« Reply #9 on: August 27, 2011, 05:24:01 PM »

In the grand scale of your considerable investment is 40m of 16mm square really that expensive  Huh http://www.tlc-direct.co.uk/Main_Index/Cable_Index/Armoured_SWA/index.html 178GBP for 16mm as opposed to 65GBP for 4mm   Huh or am I missing something. My wind turbine's 160m from my battery bank and my hydro turbine 470m, the one I'm currently installing is 1000m away  Shocked Think yourself lucky  Grin

Good luck, Paul

no considering the overall costs 200euro more on a 16000euro system is not much. Just exploring options. my wind turbine will also be over 100m from the batteries.
Logged

2660wp array, 1000amp 24v Ops battery bank, 3500XTM Struder24v, 80amp Outback, 750w Wind Turbine, Solar powered water supply
Off Grid and loving it
greenhouseparos
Full Member
***
Offline Offline

Posts: 228



« Reply #10 on: August 27, 2011, 05:31:07 PM »


using the morningstar 60a i could get the voltage up to 109v 3 strings of 3 but this uses only a total of 18 panels which would mean another controller. do you know any charger makes that can handle larger voltages?


Outback FM60 or 80 both do 145v. You can over size the array to controller. The extra amps just dont get captured. I have a theoretical 100amps from my array but have used an 80amp controller.


Quote

 
saddly costs prevented a 48v system as the batteries would have doubled.

Not quite true.

You still need the same total stored energy even though its a 48v bank. So the AH capacity can be 1/4 of the 12v banks.


If you use 3kWh per day & want 3 days autonomy then you need 3 kWh x 3 days x 2 (so you never go below 50%) = 18kWh

18kWh @ 12v = 1500ah or 15 x 100ah 12v bats (not that you should ever use a bank of that many bats)
18 kWh @ 48v = 375ah or 16 x 100ah 12v bats

The only way it can cost more is if you have a total need of less than 2.4kWh (so a 4.8kWh bank) so thats a usage of less than 800wh per day.


edit to add


why not have the bats near the array & have the inverted power travelling the distance?

i have 12 2v opz 1100ah batteries couldnt afford more. siting the batteries and inverternext next to the panels would require building some kind of weather proof construction which would eat up valuable euros.
thanks for the info   




Logged

2660wp array, 1000amp 24v Ops battery bank, 3500XTM Struder24v, 80amp Outback, 750w Wind Turbine, Solar powered water supply
Off Grid and loving it
Justme
Hero Member
*****
Offline Offline

Posts: 3530


« Reply #11 on: August 27, 2011, 06:14:36 PM »


i have 12 2v opz 1100ah batteries couldnt afford more. siting the batteries and inverternext next to the panels would require building some kind of weather proof construction which would eat up valuable euros.
thanks for the info   



But thats the point. With a 48v system you would have only needed cells of about 550ah (I assume you are set up as 24v) . As they would be cheaper each you then have the funds for the extra cells. One way or the other you are going to have to spend extra money compared to an ideal system thats located all in the same spot. Could be on wire, a shed or even in the losses in the system due to bad planning / implementation. A large battery bank will be perfectly ok on a pallet with a cheap tarp / tin roof. Dep on the temps you get you might need some sort of insulation. Mine is outside & uninsulated. Even when its -18c the bank still works within what we need even if its not working at full capacity.

Now that its too late to change the bank V you have to live with it.

As there are not many solutions & all of them cost its now down to which cost / level of performance balance you are happy with.

In your first post you said you were going to install 20x190w panels & use 2 x 60 amp controllers.

Are you sure thats right?

I make 20 x 190w = 3800watts or 158 amps at 24v. That will need 3 x 60 amp controllers not the 2 you are planning on. It will work but you are loosing quite a bit of power / energy. 30 amps at 24v is the same as removing 720 watts of array during peak times. 2 x 80amp FM 80's would be much better & you get the 145v input too so helping on two fronts.
Logged

Navitron solar thermal system
30 x 58mm panel 259L TS
1200watts solar 120vdc
FX80 Solar controller
Victron 12v 3000w 120a
6kva genny
6 x 2v cells 1550amp/h 5C
24 x 2v cells 700amp/h 5C
Total bank 4350 amp/h 5C
billi
Global Moderator
Hero Member
*****
Offline Offline

Posts: 8946



WWW
« Reply #12 on: August 27, 2011, 07:56:13 PM »

Quote
Just exploring options. my wind turbine will also be over 100m from the batteries.

 Roll Eyes not the easiest  to  combine wind and PV  and maintain an expensive battery
What  is your plan, how  to  connect the windturbine ?

The suggested Outback MPPT PV controller  might be helpful  with a windturbine idea

Billi



Logged

1.6 kw and 2.4 kw   PV array  , Outback MX 60 and FM80 charge controller  ,24 volt 1600 AH Battery ,6 Kw Victron inverter charger, 1.1 kw high head hydro turbine as a back up generator , 5 kw woodburner, 36 solar tubes with 360 l water tank, 1.6 kw  windturbine
stephendv
Hero Member
*****
Offline Offline

Posts: 928



WWW
« Reply #13 on: August 27, 2011, 09:34:55 PM »

The midnite solar classic charge controllers can handle up to 250V: http://www.midnitesolar.com/productPhoto.php?product_ID=258&productCatName=Charge%20Controllers&productCat_ID=21

But you'd have to import it from the US, no European distributor is selling them yet, AFAIK.

Logged

http://www.casanogaldelasbrujas.com
2.8kW PV, SMA Sunny Island 5048, 5 PzS 700 battery bank, stinky diesel.
greenhouseparos
Full Member
***
Offline Offline

Posts: 228



« Reply #14 on: August 28, 2011, 01:42:57 PM »

The midnite solar classic charge controllers can handle up to 250V: http://www.midnitesolar.com/productPhoto.php?product_ID=258&productCatName=Charge%20Controllers&productCat_ID=21

But you'd have to import it from the US, no European distributor is selling them yet, AFAIK.



just read your ac coupling article on your link. very interseting.
my problem has arisen for strange reasons. the initial system i planned used 18 suntech 190 pannels. i ordered 22 becuase i need 4 for a bore hole pump. when they arrived at the dealer he had 26 because he had to order a pallet. he offered the extra 4 pannels at cost price (an offer i couldn't refuse). now i am trying to fit the extra 4 into the system with out the costs rising sharply. the original 18 on 2 x 60amp morningstars worked. 18 pannels 2 sets of 9 3 parallel 3 series on the 2 chargers 109v at 15 amps over 40 m = 6 or 10 mm cable. i will use 2 of the extra pannels for water pumping and have 2 left. trying to fit them into the house array seems expensive and not cost efficient. will definatly have a use for them but not for the house array it seems.
Logged

2660wp array, 1000amp 24v Ops battery bank, 3500XTM Struder24v, 80amp Outback, 750w Wind Turbine, Solar powered water supply
Off Grid and loving it