« on: November 25, 2012, 09:32:38 AM » |
|
I wonder , what would happen , if i connect a MPPT charge controller available upto 600 Volt Voc in parallel to a Gridtie Inverter to a say 4000 Watt PV ? So the Gti is connected to the utility Grid to feed in , and the MPPT charger connected to the Battery of a (semi) offgrid house ....
Would it work , that once the battery is full the GTI would start more and more to feed the Grid or would the GTI use all power to feed the grid and the charge-controller gets nothing ?
Or is this a total nuts idea ?
Thanks Billi
|
|
|
Logged
|
1.6 kw and 2.4 kw PV array , Outback MX 60 and FM80 charge controller ,24 volt 1600 AH Battery ,6 Kw Victron inverter charger, 1.1 kw high head hydro turbine as a back up generator , 5 kw woodburner, 36 solar tubes with 360 l water tank, 1.6 kw windturbine
|
|
|
clockmanFR
|
 |
« Reply #1 on: November 25, 2012, 05:38:37 PM » |
|
Billi my hearty,
Go on Billi make our Day.
Please do try.
Oh yes, and to-days topical comment, "Ensure a responsible adult is present".
|
|
|
Logged
|
Everything is possible, just give me TIME.
|
|
|
billi
|
 |
« Reply #2 on: November 25, 2012, 06:45:13 PM » |
|
 sure i am on a "mission impossible " , to try to figure out future Grid/off Grid/ FiT harvesting ideas ....  Actually , for fact , i am crazy ! to even spent one minute of thoughts about this ..... But my feeling , tells me , that FiT payments in Europe will be limited or knocked out in the near future for us small producers , sure for those people that have their 20-25 years contract agreed today , its fine .... But for newcomers , it might be be not beneficial any-more to install a PV on their roof and feed the Grid only Will sleep over it Not now , but later  Billi
|
|
|
Logged
|
1.6 kw and 2.4 kw PV array , Outback MX 60 and FM80 charge controller ,24 volt 1600 AH Battery ,6 Kw Victron inverter charger, 1.1 kw high head hydro turbine as a back up generator , 5 kw woodburner, 36 solar tubes with 360 l water tank, 1.6 kw windturbine
|
|
|
pdf27
|
 |
« Reply #3 on: November 25, 2012, 07:34:27 PM » |
|
|
|
|
Logged
|
|
|
|
billi
|
 |
« Reply #4 on: November 26, 2012, 02:29:06 AM » |
|
sure , but not too impressed ,
What the world needs (for households) is a self supply first and a FiT for export
Some countries differ to the FiT of the UK
|
|
« Last Edit: November 26, 2012, 02:36:19 AM by billi »
|
Logged
|
1.6 kw and 2.4 kw PV array , Outback MX 60 and FM80 charge controller ,24 volt 1600 AH Battery ,6 Kw Victron inverter charger, 1.1 kw high head hydro turbine as a back up generator , 5 kw woodburner, 36 solar tubes with 360 l water tank, 1.6 kw windturbine
|
|
|
stephendv
|
 |
« Reply #5 on: November 26, 2012, 08:23:26 AM » |
|
Would it work , that once the battery is full the GTI would start more and more to feed the Grid or would the GTI use all power to feed the grid and the charge-controller gets nothing ?
I think the problem will be the MPPT algorithms which will get very confused, imagine if the charge controller MPPT has found Pmax at 50V and is drawing current from the panel, now the GTI does its MPPT sweep, where is it going to find Pmax- might be at a different voltage completely because the charge controller is already drawing current from the panel. For what you want to do, I think an AC coupling idea with some clever relay switching based on battery SoC will be easier to achieve.
|
|
|
Logged
|
|
|
|
Justme
|
 |
« Reply #6 on: November 26, 2012, 08:30:06 AM » |
|
Outback inverter chargers do exactly what you want.
You can set the export (sell) to what ever you want.
|
|
|
Logged
|
Navitron solar thermal system 30 x 58mm panel 259L TS 1200watts solar 120vdc FX80 Solar controller Victron 12v 3000w 120a 6kva genny 6 x 2v cells 1550amp/h 5C 24 x 2v cells 700amp/h 5C Total bank 4350 amp/h 5C
|
|
|
billi
|
 |
« Reply #7 on: November 26, 2012, 08:47:43 AM » |
|
For what you want to do I want to help Germany  , because its so hard there to setup a battery based PV and as well simple export the surplus ... So many Battery -Grid tied ideas come on the market , but all have one in common - very pricey- , ok the Nedap powerrouter seems to be ok isch Yes Justme , i saw that, but are these exporting Outback Inverter/chargers available in 230 Volt 50 hz ? Thanks
|
|
|
Logged
|
1.6 kw and 2.4 kw PV array , Outback MX 60 and FM80 charge controller ,24 volt 1600 AH Battery ,6 Kw Victron inverter charger, 1.1 kw high head hydro turbine as a back up generator , 5 kw woodburner, 36 solar tubes with 360 l water tank, 1.6 kw windturbine
|
|
|
nowty
|
 |
« Reply #8 on: November 26, 2012, 02:17:44 PM » |
|
To reply to "stephendv"
"For what you want to do, I think an AC coupling idea with some clever relay switching based on battery SoC will be easier to achieve."
That is pretty much what I do, I have got both on grid GTI and off grid (AC coupled) systems which automatically switch house circuits via a big relay based upon night / day and battery state of charge.
I have mainly done it this way because I have more PV than 4kw without permission from the DNO to connect to the grid so I have to have my PV excess capacity as off grid.
If I had permission to add more PV to the grid I would probably switch it all to the grid and find ways of diverting surplus grid power to batteries and hot water heating. The immersun is an obvious choice for water heating and I am sure it would not be that difficult for another immersun type device to be invented to charge batteries.
|
|
« Last Edit: November 26, 2012, 02:23:03 PM by nowty »
|
Logged
|
11kW+ of PV installed and 56+ MWh generated. Lithium battery storage of 50+ kWh. Hot water storage of 15+ kWh. Heat storage of 15+ kWh. 6kW Ground source heatpump. EV BMW i3 (another 30+ kWh's of storage). 260,000+ litres of water harvested from underground river. Home grown Fruit and Veg.
|
|
|
sbchapman
|
 |
« Reply #9 on: November 26, 2012, 04:03:33 PM » |
|
Nowty - I am in a similar situation to you. The only difference is that I have export meter and called my FIT provider to check the metering procedure with installation of personally installed additional (non MCS) microgeneration. I was told in no uncertain terms that anything I added, if not FIT registered should not even be connected to AC. If it was fitted by a MCS certified company and registered for FITs they would only meter export from one installation - which begs the question, when everyone is on export meters (which WILL happen eventually with SmartMeters) how do they differentiate between different contributions of different technologies?
So for the moment I was wondering about running a standalone DC battery charging setup, with an inverter on a timer to meet demand when the PV isn't generating. Is yours "smart" i.e. meets demand that would come from the grid even during the day? I suspect the financials don't make it worthwhile for me as I'll only save the differential between imported and exported units, and as exported rates should rise inline with energy costs (or at least FIT rates?) the differential would stay approximately the same ... or have I got my assumptions wrong?
Steve
|
|
|
Logged
|
Thermal: 4x Schott ETC16 PV: 3.9 kWp (20xSchott Mono Perform 195Wp) Boilermate Thermal Store SMA SB400TL-20 Clearview Pioneer 5kW Woodwarm 9kW Windsmithy Arthur 6kW 1 anemometer (sadly no turbine)
|
|
|
Justme
|
 |
« Reply #10 on: November 26, 2012, 04:28:25 PM » |
|
Check the Outback International range.
|
|
|
Logged
|
Navitron solar thermal system 30 x 58mm panel 259L TS 1200watts solar 120vdc FX80 Solar controller Victron 12v 3000w 120a 6kva genny 6 x 2v cells 1550amp/h 5C 24 x 2v cells 700amp/h 5C Total bank 4350 amp/h 5C
|
|
|
nowty
|
 |
« Reply #11 on: November 26, 2012, 05:54:38 PM » |
|
Steve - I fully understand your FIT provider saying that you cannot connect any additional non FIT system to AC as long as they mean the “AC grid”. That makes sense as even without DNO issues you would be being paid for metered export from both a registered and non registered installation.
If however they mean you cannot have any non MCS installations whatsoever on the same site as a site registered for FIT, then I would be ripping my off grid installation out pronto. I wonder if any of the senior guys on here could clear that up.
To answer your query about whether my system is “smart”. Its only smart in that load circuits are switched to it at 4pm until 8am (GMT) but only if the battery is at 90%+ charged. And it disconnects if the charge gets less than a pre-set value of between 60% and 80% depending upon time of year. The number of circuits I switch are also dependant on the time of year, more in summer less in winter.
For example at the moment its winter so minimum circuits (lighting and central heating pump), it will use around 4 units (kwh’s) per day which is the amount my batteries can store from 100% down to 80%. I choose 80% this time of year because the most my off grid PV can deliver on a sunny day is about 5 units, just enough to get back from 80% to near 100%.
In summer I have additional loads, TVs, sky boxes, computers, internet, fridges and that bumps up the usage from 4pm to 8am to around 10 units. In summer my off grid PV generates from 5am to 7pm (BST) the AC coupling powers about 3 units worth with the other 7 coming from the batteries. I choose a battery cut off of 60% because 100% down to 60% is about 8 units. In summer the average daily generation is around 15 units or so which is more than enough to get the batteries back to 100%, in fact they are usually in float by early afternoon.
And of course during the day 8am to 4pm everything is switched to the grid where its powered by the grid backed up with my normal FIT registered 4kw GTI.
One thing I find is that I waste tons of potential off grid power in summer as the PV generation backs off generation as the batteries fill up. As I already have an Imersun on the grid tie heating water, I just have no use for the lost power. Maybe an electric car is needed !
|
|
|
Logged
|
11kW+ of PV installed and 56+ MWh generated. Lithium battery storage of 50+ kWh. Hot water storage of 15+ kWh. Heat storage of 15+ kWh. 6kW Ground source heatpump. EV BMW i3 (another 30+ kWh's of storage). 260,000+ litres of water harvested from underground river. Home grown Fruit and Veg.
|
|
|
sbchapman
|
 |
« Reply #12 on: November 26, 2012, 09:30:02 PM » |
|
Nowty - thanks for the response. Just to clear things up ... They're not saying I cant install anything, just that anything I install should not be AC connected and therefore with the potential to export. As you rightly point out, if it did, I would be exporting from a non-FIT registered installation. So I believe your setup is OK if you manually enable the battery system at nightime, provided the battery system cannot produce sufficient power to export if local demand is low. (That was my take anyway) So the only way I see it working for me is charging batteries, which I could then use to offset grid demand, ideally at any time but realistically like you have setup, at nighttime. This is why I was interested in "smart" switching. Regarding your summer config and wasted energy, I guess you could investigate a DC immersion, however if you are on deemed export right now and have an immersun there is problably no justifiable benefit. I found it interesting that you limit the loads off battery in Winter due to the inability to charge the battery the next day - I'd not really thought about that  I just expected to use as much as possible within the realms of maintaining battery life/condition, even if it meant the battery couldn't be fully recharged next day. Steve
|
|
« Last Edit: November 26, 2012, 09:39:59 PM by sbchapman »
|
Logged
|
Thermal: 4x Schott ETC16 PV: 3.9 kWp (20xSchott Mono Perform 195Wp) Boilermate Thermal Store SMA SB400TL-20 Clearview Pioneer 5kW Woodwarm 9kW Windsmithy Arthur 6kW 1 anemometer (sadly no turbine)
|
|
|
nowty
|
 |
« Reply #13 on: November 26, 2012, 11:08:04 PM » |
|
OK, sounds like I assumed correct that your FIT provider ONLY was against another unregistered system being connected to the AC grid, not to an off grid AC system.
To clarify I don’t manually enable my battery system, it is fully automated on a timer and SOC of the battery. If its night and there is a good battery level, selected circuits are switched with a heavy duty double pole relay. The grid AC live and neutral are disconnected and the battery system AC live and neutral are switched in, so there is no possability of exporting any power back to the grid. If the battery gets low, or fails, or is daytime again, or I manually switch it off for maintenance the relay simply drops out and returns circuits back to the grid. And this happens so quick there is hardly a light flicker and computers, internet, etc run normally.
There is some one off manual intervention throughout the year to set the battery % SOC cut off level and selection of circuits (via extension lead plug and sockets) to balance the load verses the average available PV power available. Also I have a boost facility from the grid to give extra charge to the batteries but I only use this for emergencies or doing the occasional equalisation charge.
|
|
« Last Edit: November 26, 2012, 11:14:59 PM by nowty »
|
Logged
|
11kW+ of PV installed and 56+ MWh generated. Lithium battery storage of 50+ kWh. Hot water storage of 15+ kWh. Heat storage of 15+ kWh. 6kW Ground source heatpump. EV BMW i3 (another 30+ kWh's of storage). 260,000+ litres of water harvested from underground river. Home grown Fruit and Veg.
|
|
|
sbchapman
|
 |
« Reply #14 on: November 26, 2012, 11:38:39 PM » |
|
Can you briefly explain how you do the automated / timed switching - and where does the SunnyIsland fit in? I vaguely remembered an earlier post of yours, and searched, finding this: http://www.navitron.org.uk/forum/index.php?topic=16866.30However it mentioned your Victron Multiplus....? Thanks
|
|
|
Logged
|