News: Anyone wishing to register as a new member on the forum is strongly recommended to use a "proper" email address - following recent spam/hack attempts on the forum, all security is set to "high", and "disposable" email addresses like Gmail, Yahoo and Hotmail tend to be viewed with suspicion, and the application rejected if there is any doubt whatsoever
 
Recent Articles: Navitron Partners With Solax to Help Create A More Sustainable Future | Navitron Calls for Increased Carbon Footprint Reduction In Light of Earth Overshoot Day | A plea from The David School - Issue 18
   Home   Help Search Login Register  
Pages: [1]   Go Down
  Print  
Author Topic: Change Frequency of Generator AC Output - Possible?  (Read 3162 times)
Eleanor
Hero Member
*****
Offline Offline

Posts: 2574



« on: January 02, 2013, 06:53:41 PM »

We have a small back up petrol generator which worked quite happily for a year charging batteries via the Victron MultiPlus. A couple of months ago the Victron started ignoring the generator output and refused to charge. Having fiddled about I found that the frequency was outside the range the Victron will accept ie > 65Hz. I've enabled "Accept wide input frequency range (45-65 Hz)" in VE configure but I can't see any way of getting it to accept more than 65Hz. So, to the question : can I do anything to reduce the frequency by a few Hz? It must have been lower in the beginning for it to have worked. Thanks.  tumble
Logged

I'm doing this for free, please be nice to me surrender
"Very few batteries die a natural death ... most are murdered" stir
guydewdney
Hero Member
*****
Offline Offline

Posts: 4321



« Reply #1 on: January 02, 2013, 07:08:59 PM »

Tweak the spring that holds the throttle open, inthink they will generally need shortening to lower the rpm
Logged

Pic of wheel on day 1
7.2kW Waterwheel and 9.8kW PV
marshman
Hero Member
*****
Offline Offline

Posts: 948


WWW
« Reply #2 on: January 02, 2013, 09:43:35 PM »

Before doing anything check that your generator doesn't have a lever on it somewhere which sets the frequency. My old Honda 650W genny has a level to set it to either 50 or 60Hz. Basically it just speeds the engine up 20% to give 60Hz. If it has it is possible that it has got knocked over to the 60Hz position.

If not then as guy says try shortening the spring on the throttle or bending the governor lever.

Roger
Logged

3.15kWpk (15xSharp ND210)/SB3000. & 3.675kWpk (15 x Suntech 245WD)/SB4000TL, 10kW GSHP driving Wirsbo underfloor heating from 1200m ground loops. 10' x 7' solar wall (experimental). Clearview 650 Wood Burning Stove. MHRV - diy retrofit. Triple glazing.
johnrae
Hero Member
*****
Offline Offline

Posts: 764


« Reply #3 on: January 02, 2013, 10:29:51 PM »

If the governor is driven by air from the cooling fan then check there isn't debris interfering with the air flow.  Low flow of air is the equivalent of the engine running slow, hence the governor opens up which increases speed and therefore frequency.   If you can beg or borrow a hand-held tacho unit you could check engine speed.  For 50hz it will be either 1500 or 3000 RPM.
Logged
Eleanor
Hero Member
*****
Offline Offline

Posts: 2574



« Reply #4 on: January 02, 2013, 11:04:20 PM »

Thanks, a few things to go on there and it sounds like it can be sorted out.
I'll look at air flows - I've already cleaned the filter but there could be something lurking somewhere else horror and then go for the tweaking genuflect
Logged

I'm doing this for free, please be nice to me surrender
"Very few batteries die a natural death ... most are murdered" stir
billi
Global Moderator
Hero Member
*****
Offline Offline

Posts: 8944



WWW
« Reply #5 on: January 02, 2013, 11:43:47 PM »

I know  Roll Eyes..... perhaps its not the solution (longterm), in my case it worked fine to apply a second load to the second outlet/socket of the generator to get him "loaded " first and push down the Volt towards something the Victron will accept ..... it seems to me , that once accepted by the Victron it works better and voltage of the generator does not climb up towards out of range

My wife was not sure that everything was alright with me , those days , when i went out at night  to the generator shed with her hairdryer  whistlie



Other scenario i know very well , is Victron allows to connect the Genny , but Voltage fluctuates too much cause internal charger of the Victron draw too much or too quick  and kicks him (her?) out and back in , then i switch on the hairdryer  in the house (just on low power) , that balances the Genny , until the Victron finds his balance as well, to keep the Genny running  more smooth , for charging


Sure if the Genny worked before , there can be some other problems ,   but Generators and Billi  have a long affair , and will probably not marry in a lifetime  whistlie

Regards Billi
« Last Edit: January 02, 2013, 11:47:33 PM by billi » Logged

1.6 kw and 2.4 kw   PV array  , Outback MX 60 and FM80 charge controller  ,24 volt 1600 AH Battery ,6 Kw Victron inverter charger, 1.1 kw high head hydro turbine as a back up generator , 5 kw woodburner, 36 solar tubes with 360 l water tank, 1.6 kw  windturbine
Eleanor
Hero Member
*****
Offline Offline

Posts: 2574



« Reply #6 on: January 03, 2013, 12:10:09 AM »


My wife was not sure that everything was alright with me , those days , when i went out at night  to the generator shed with her hairdryer  whistlie

Regards Billi

At least I'm not the only weirdo in town as that's what I did to try and slow it down. Great minds think alike  Grin
Logged

I'm doing this for free, please be nice to me surrender
"Very few batteries die a natural death ... most are murdered" stir
Eleanor
Hero Member
*****
Offline Offline

Posts: 2574



« Reply #7 on: January 03, 2013, 12:21:59 AM »

On a more serious note I'm fairly convinced that the frequency is the problem as the Victron doesn't even try to connect although the voltage is within limits. I expect the Victron is objecting to being connected to a cheapo generator and would prefer a Lister  Grin
Logged

I'm doing this for free, please be nice to me surrender
"Very few batteries die a natural death ... most are murdered" stir