News: Anyone wishing to register as a new member on the forum is strongly recommended to use a "proper" email address - following recent spam/hack attempts on the forum, all security is set to "high", and "disposable" email addresses like Gmail, Yahoo and Hotmail tend to be viewed with suspicion, and the application rejected if there is any doubt whatsoever
 
Recent Articles: Navitron Partners With Solax to Help Create A More Sustainable Future | Navitron Calls for Increased Carbon Footprint Reduction In Light of Earth Overshoot Day | A plea from The David School - Issue 18
   Home   Help Search Login Register  
Pages: [1] 2   Go Down
  Print  
Author Topic: Recomends please... Meter/store data, between 48vDc and 3.7kw Inverter.  (Read 8544 times)
clockmanFR
Hero Member
*****
Offline Offline

Posts: 3584



WWW
« on: August 10, 2013, 09:45:43 AM »

I know about the watt meters, but when the Inverter is fully loaded its drawing nearly 80amps, so the watt meters need to be robust.

I would like to know, with a bit more accuracy, what is coming out of my 1300ah batteries. I know what's going in to them and I know what kw's is coming out of the Inverter at 240vAc.

Any recommendations Please.

Thanks.
 
Logged

Everything is possible, just give me TIME.
biff
Global Moderator
Hero Member
*****
Offline Offline

Posts: 11964


An unpaid Navitron volunteer who lives off-grid.


« Reply #1 on: August 10, 2013, 10:15:01 AM »

I think that 10 minutes max @ 80 amps would finish your batteries C/M.
                                 3.8kw on sealed lead acids would murder them unless you had the same or more coming in and even then they are being stretched to the max.That load would still be 32 amp if running at 120vdc,Massive.  ( I think)
                                                                            Biff
Logged

An unpaid Navitron volunteer,who has been living off-grid,powered by wind and solar,each year better than the last one.
Tinbum
Hero Member
*****
Offline Offline

Posts: 1178


« Reply #2 on: August 10, 2013, 10:26:29 AM »

I'm sure there's plenty out there to do the job. I would suggest something based on measuring the voltage across a shunt for the DC side.
Logged

85no 58mm solar thermal tubes, 28.5Kw PV, 3 x Sunny Backup 5048, 3x Sunny Island 5048, 2795 Ah (135kWh) (c20) Rolls batteries 48v, Atmos wood gasification boiler, Brosley wood burner, 2000lt buffer tank and 250lt DHW
biff
Global Moderator
Hero Member
*****
Offline Offline

Posts: 11964


An unpaid Navitron volunteer who lives off-grid.


« Reply #3 on: August 10, 2013, 11:09:54 AM »

There is a duel push buttom meter on fleabay(red or blue)
                           It comes with shunt and instructions,200amp and 200volt.I think they were around 20.00 each but I did pay 30 bout 2 years ago.Then I got 4 of them for 50.00 complete with heavy duty shunts and clear instructions.
     Some of these little meters look the same but the wiring is the opposite and the innards are slightly different.You really need to follow the instruction carefully.If you go through the online specs and fitting instructions you will see the warnings about this same thing.
             Biff
Logged

An unpaid Navitron volunteer,who has been living off-grid,powered by wind and solar,each year better than the last one.
w0067814
Full Member
***
Offline Offline

Posts: 239


« Reply #4 on: August 10, 2013, 01:55:09 PM »

I think that 10 minutes max @ 80 amps would finish your batteries C/M.
                                 3.8kw on sealed lead acids would murder them unless you had the same or more coming in and even then they are being stretched to the max.That load would still be 32 amp if running at 120vdc,Massive.  ( I think)
                                                                            Biff

Are clockman's batteries on their last legs then? 80 amps is only 0.06C and looking at a comparable battery size datasheet I see that they could handle 80 amps for 12 hours, and 52 amps for 20 hours sustained. 3.8kw is about 5hp, which is nothing for a forklift, so I'd expect to see far more current than that in every day situations.
Logged
clockmanFR
Hero Member
*****
Offline Offline

Posts: 3584



WWW
« Reply #5 on: August 10, 2013, 02:21:52 PM »

Biff, When its sunny I get 3kw, soon to be 5kw. And if its windy then I get 3kw.

Even in ambient light I am still getting 500w.

Thanks then will have a go at the ones with shunts.

Just that the batteries seem to absorb about 25% so with a data meter I should be able to give some real figures.
Logged

Everything is possible, just give me TIME.
camillitech
Hero Member
*****
Offline Offline

Posts: 5415



WWW
« Reply #6 on: August 10, 2013, 03:35:31 PM »

Any use CM http://www.eltime.co.uk/product.php/41/DIN%20Rail%20Mounting%20kWh%20Meters.html Hugh uses them http://scoraigwind.co.uk/2011/11/kestrel-e400i-wind-turbine-on-scoraig/

Cheers, Paul
Logged

http://lifeattheendoftheroad.wordpress.com/

'Off grid' since 1985,  Proven 2.5kW, Proven 6kW direct heating, SI6.OH, 800ah Rolls, 4.75kW PV ,4xTS45, Lister HR2 12kW, , Powerspout pelton, Stream Engine turgo, 60 x Navitron toobs and a 1500lt store. Outback VFX3048 and 950ah forklifts for backup,
biff
Global Moderator
Hero Member
*****
Offline Offline

Posts: 11964


An unpaid Navitron volunteer who lives off-grid.


« Reply #7 on: August 10, 2013, 06:46:53 PM »

Woo,
       80 amps just seems a massive draw to me.Thats all.I am used to much smaller amps and its a bit of a shock.There is also the fact that we dont drain or batteries down dead,We dont go below 12.4 and that means we only take about 12,5% or about that.If you start going below this you are killing the batteries and they will give up very quickly.So you are hardly likely to get the figures you are quoting unless you let the battery go to the bottom, Grin fight
                      Biff
Logged

An unpaid Navitron volunteer,who has been living off-grid,powered by wind and solar,each year better than the last one.
w0067814
Full Member
***
Offline Offline

Posts: 239


« Reply #8 on: August 10, 2013, 08:27:28 PM »

To be honest I don't think a bank of that capacity would even notice 80 amps presuming voltages are observed.

... Now if you really want to murder a battery you do what we do at work. We have 4 battery banks each 384v 80Ah. Weighs about 5 tons. Combined draw is a shade under 300 amps. stir

Tim
Logged
camillitech
Hero Member
*****
Offline Offline

Posts: 5415



WWW
« Reply #9 on: August 10, 2013, 08:43:35 PM »

To be honest I don't think a bank of that capacity would even notice 80 amps presuming voltages are observed.

... Now if you really want to murder a battery you do what we do at work. We have 4 battery banks each 384v 80Ah. Weighs about 5 tons. Combined draw is a shade under 300 amps. stir

Tim

That's nothing, this is what we have at work,



800v 700kwh and seven tons  Cool
Logged

http://lifeattheendoftheroad.wordpress.com/

'Off grid' since 1985,  Proven 2.5kW, Proven 6kW direct heating, SI6.OH, 800ah Rolls, 4.75kW PV ,4xTS45, Lister HR2 12kW, , Powerspout pelton, Stream Engine turgo, 60 x Navitron toobs and a 1500lt store. Outback VFX3048 and 950ah forklifts for backup,
biff
Global Moderator
Hero Member
*****
Offline Offline

Posts: 11964


An unpaid Navitron volunteer who lives off-grid.


« Reply #10 on: August 10, 2013, 08:45:54 PM »

Aweeee well,
             And there was me thinking I had arrived with my 2 ton of lead acid  Roll Eyes.
                                                                              Biff
Logged

An unpaid Navitron volunteer,who has been living off-grid,powered by wind and solar,each year better than the last one.
clockmanFR
Hero Member
*****
Offline Offline

Posts: 3584



WWW
« Reply #11 on: August 10, 2013, 09:46:07 PM »

eye eye Paul, well scrag my cat for dem der lovely batts.

Will look at meter, thanks.

Biff my 12v batts never ever go below 12.35v or 49.40v, I now have a master auto LVD, (Low Voltage Disconnect), Also have EricW's circuit that recognises when batts have gone to float mode, and diverts extra power on the 240vac side of the inverter to heat water or the under floor heating. It also switches the load off if the voltage goes below battery holding voltage of 52.00v .

This now means very minimal use of the Wind turbine dump loads.
Logged

Everything is possible, just give me TIME.
clockmanFR
Hero Member
*****
Offline Offline

Posts: 3584



WWW
« Reply #12 on: August 10, 2013, 10:03:58 PM »

Eltime stuff is good and have used them in the past for my panel amp meters.

Have been looking at this type, http://www.ebay.co.uk/itm/Turnigy-130A-Watt-Meter-and-Power-Analyzer-in-stock-from-UK-with-fast-dispatch-/281106316902?pt=UK_ToysGames_RadioControlled_JN&hash=item41733dfe66

Any one got any recommendations?

But have heard about the insides melting when power is really on.  sh*tfan
Logged

Everything is possible, just give me TIME.
camillitech
Hero Member
*****
Offline Offline

Posts: 5415



WWW
« Reply #13 on: August 11, 2013, 07:50:00 AM »

Eltime stuff is good and have used them in the past for my panel amp meters.

Have been looking at this type, http://www.ebay.co.uk/itm/Turnigy-130A-Watt-Meter-and-Power-Analyzer-in-stock-from-UK-with-fast-dispatch-/281106316902?pt=UK_ToysGames_RadioControlled_JN&hash=item41733dfe66

Any one got any recommendations?

But have heard about the insides melting when power is really on.  sh*tfan

Morning CM,

But have heard about the insides melting when power is really on

yes I heard of more than one chap who wrecked a wind turbine with one of those  Cry

Cheers, Paul
Logged

http://lifeattheendoftheroad.wordpress.com/

'Off grid' since 1985,  Proven 2.5kW, Proven 6kW direct heating, SI6.OH, 800ah Rolls, 4.75kW PV ,4xTS45, Lister HR2 12kW, , Powerspout pelton, Stream Engine turgo, 60 x Navitron toobs and a 1500lt store. Outback VFX3048 and 950ah forklifts for backup,
rogeriko
Hero Member
*****
Offline Offline

Posts: 1425



WWW
« Reply #14 on: August 11, 2013, 09:37:27 AM »

Don't use those Turnigy types. Any more than 20a sustained and they melt. There are plenty of models with an external shunt. http://www.ebay.co.uk/itm/Bogart-TriMetric-2025-A-Solar-Battery-Monitor-Meter-500AMP-Shunt-Cable-/300943365845?pt=LH_DefaultDomain_0&hash=item46119f56d5
Logged