News: Anyone wishing to register as a new member on the forum is strongly recommended to use a "proper" email address - following recent spam/hack attempts on the forum, all security is set to "high", and "disposable" email addresses like Gmail, Yahoo and Hotmail tend to be viewed with suspicion, and the application rejected if there is any doubt whatsoever
 
Recent Articles: Navitron Partners With Solax to Help Create A More Sustainable Future | Navitron Calls for Increased Carbon Footprint Reduction In Light of Earth Overshoot Day | A plea from The David School - Issue 18
   Home   Help Search Login Register  
Pages: 1 [2]   Go Down
  Print  
Author Topic: Batteries not fully charged by FM80 or Mastervolt Mass Combi  (Read 11165 times)
Scatter
Newbie
*
Offline Offline

Posts: 6


« Reply #15 on: November 12, 2013, 01:11:03 PM »

Many thanks once again everyone!

Thanks to Tinbum's post I found something that looks quite similar:

http://www.varta-automotive.com/en-gb/products/commercial-vehicles/promotive-black/720-018-115

Yes those caps do come off as it turns out. I'm a bit pssd off with myself for not checking this out properly a while ago - I saw the label saying maintenance free and assumed that they couldn't be standard lead acids so I parked it until now while I got on with getting to grips with the rest of the boat's systems. Not a good idea as it turns out! Ah well, chalk it up to experience I guess.

So I'll give them a clean, top up the cells with deionised water charge them up as much as I can and then get the Mastervolt to do an equalisation charge. It's a 12V system so I take it I should simply halve the values given in Dave's post (so 14.8V absorption and 13.8V float) and set the Outback accordingly. If equalisation freshens them up then we'll then look at nursing them through the winter and buying replacements next year but if it doesn't we might see if we can bring that forwards.

Dave, any particular brands of forklift batteries that you recommend?
Logged
DaveSnafu
Full Member
***
Offline Offline

Posts: 247


« Reply #16 on: November 12, 2013, 02:38:02 PM »

Sorry, yeah I always think in 24v.
 All it means is the batteries are on the way out, you need to run em a bit hotter, so they see it through till morning, they will use more water being run at a slightly higher voltage and gas a bit more, so need good ventilation and topping up more often, put a light directly over them so you can get a good look inside for topping up.
The traction cells I have recently bought are made by eternity, the ones we have at home in wales were made by chloride about 15-20 years ago, depending on how old they were before we bought them, we have had them nearly 10 years, they are elderly but keep soldering on.
Logged

Proven wt2500,24v batteries,running house,navitron solar thermal integrated tank, 10 x 210w eclipse italia pv, wbs,
camillitech
Hero Member
*****
Offline Offline

Posts: 5413



WWW
« Reply #17 on: November 12, 2013, 09:27:15 PM »

I have wrecked plenty of those Varta batteries Scatter, they're great for use in boats that are cruising but won't last a year cycled deeply and not charged fully. Trojan's are fine too, I look after a bank of those and they're doing OK after three years. The Rolls are what I plan to buy for my new house after seeing how well they preform at an 'off grid' property nearby. There's nothing wrong with forklift cells, it's what I use at the moment and have been doing so for seven years. However I feel that they are just the wrong shape, especially for a boat, they are after all designed to act as a counterweight as well as an energy storage medium.

Good luck, Paul
Logged

http://lifeattheendoftheroad.wordpress.com/

'Off grid' since 1985,  Proven 2.5kW, Proven 6kW direct heating, SI6.OH, 800ah Rolls, 4.75kW PV ,4xTS45, Lister HR2 12kW, , Powerspout pelton, Stream Engine turgo, 60 x Navitron toobs and a 1500lt store. Outback VFX3048 and 950ah forklifts for backup,
splyn
Full Member
***
Offline Offline

Posts: 225


« Reply #18 on: November 13, 2013, 12:07:16 AM »

Scatter,

Quote
I haven't done a formal power audit but know that our demand is pretty low (I work in energy efficiency so aim to cut my energy demand as far as possible). LED lighting throughout, very efficient fridge and TV, a laptop and that's about it.  We're averaging about 0.6kWh generation per day at the moment and got 1.1kWh today. That really should come close to covering our demand I think but I should sit down and add it all up to make sure.

When you do, don't forget to take into account the inefficiencies in the batteries and inverter (I assume the -6kWh is the output from the charger). You might easily lose 30% or 40% (or even more) of the PV output; see http://windandsunpower.com/Download/Lead%20Acid%20Battery%20Efficiency.pdf

"Peliminary results agree well with established general understanding that the charge efficiency of flooded lead-antimony batteries declines with increasing state-of-charge, and that charge efficiency is a non-linear function of battery state-of-charge. These tests indicate that from zero SOC to 84% OC the average overall battery charging efficiency is 91%, and that the incremental battery charging efficiency from 79% to 84% is only 55%. This is particularly significant in PV systems where the designer expects the batteries to normally operate at SOC above 80%, with deeper discharge only occurring during periods of extended bad weather. In such systems, the low charge efficiency at high SOC may result in a substantial reduction in actual available stored energy because nearly half the available energy is serving losses rather than charging the battery. "
...
"Charge efficiencies at 90% SOC and greater were measured at less than 50% for the battery tested here, requiring a PV array that supplies more than twice the energy that the load consumes for a full recovery charge. Many batteries in PV systems never reach a full state of charge, resulting in a slow battery capacity loss from stratification and sulfation over the life of the battery."

If the batteries are in poor shape then their charge efficiency will be even worse. However from what you've said it doesn't sound like your batteries spend much time above 79% SOC so perhaps the low incremental charge efficiency at higher states of charge won't be much of an issue....  whistlie

I couldn't find any efficiency graphs for the inverter, but it is specified at >= 90% efficiency above 100VA. I guess your typical load is quite low so I would expect the efficiency to be around 90% at loads around 100VA, dropping sharply for lower loads. Efficiency might drop for loads with a poor power factor as well, but the best way to determine your actual power use would be to measure the current and voltage going into the Mastervolt.

I see that the inverter consumes between .5 and 9W depending on the mode - 9W is 216Wh/day so a big chunk out of .6kWh/day generation. If you can't live with the inverter in its lowest power mode (which switches on every 2.5 secs to check for a load), it may be worth trying a low power (say 100W or so?) inverter in parallel to supply low loads and operating the Mastervolt in its lowest power mode. Whether you can get a small inverter with acceptable efficiency is another matter and there's also the issue of the stability of the system when the load increases to the point when the Mastervolt decides to kick in. You'd have to experiment and so how it behaves.

The FM80 charger manual includes efficiency curves for different input voltages - looks like you could easily get 5% better efficiency by having the panels in parallel if you haven't already done so. Might also be worth experimenting with?

Splyn
Logged
Scatter
Newbie
*
Offline Offline

Posts: 6


« Reply #19 on: November 13, 2013, 05:35:38 PM »

Cheers Splyn, most helpful. I was idly wondering what the round trip efficiency was - not particularly encouraging for winter charging from PV!

I topped up the cells and tried to do an equalisation charge once the Mastervolt was indicating it was in float mode. I flick the dip switch and the five indicator lights flash as they should to indicate equalisation mode but it drops out of equalisation mode after just a few minutes. I've tried twice and no joy Sad

When it was in equalisation mode the voltage was varying between about 13.4V and 13.9V, certainly not the gradual increase up towards 15.5V indicated in the manual.
Logged
splyn
Full Member
***
Offline Offline

Posts: 225


« Reply #20 on: November 14, 2013, 01:50:06 PM »

Its actually going to be worse than the Sandia labs test results show - the efficiency graphs are the coulometric efficiency (ampere hours out / ampere hours in) not energy efficiency. The difference in charge and discharge voltage will cost another 5 to 10% of those precious kWhs that charge the batteries.

If the batteries are cold in the winter then another few % could be lost on top.

Have you considered selling them to Billi as a dump load?  ralph

Splyn
Logged
billi
Global Moderator
Hero Member
*****
Offline Offline

Posts: 8943



WWW
« Reply #21 on: November 15, 2013, 01:38:53 AM »

Quote
from zero SOC to 84% OC the average overall battery charging efficiency is 91%
pretty good , isnt it ...

Second hand refurbished forklift batteries .... here http://store.bluebatt.com/Zellen-Pz-TOP-refurbished_1

new cells from Poland http://www.bater.pl/promocje/
Logged

1.6 kw and 2.4 kw   PV array  , Outback MX 60 and FM80 charge controller  ,24 volt 1600 AH Battery ,6 Kw Victron inverter charger, 1.1 kw high head hydro turbine as a back up generator , 5 kw woodburner, 36 solar tubes with 360 l water tank, 1.6 kw  windturbine
Justme
Hero Member
*****
Offline Offline

Posts: 3530


« Reply #22 on: November 15, 2013, 08:51:36 AM »


Second hand refurbished forklift batteries .... here http://store.bluebatt.com/Zellen-Pz-TOP-refurbished_1

new cells from Poland http://www.bater.pl/promocje/

I wonder exactly what "refurbished" means?
Logged

Navitron solar thermal system
30 x 58mm panel 259L TS
1200watts solar 120vdc
FX80 Solar controller
Victron 12v 3000w 120a
6kva genny
6 x 2v cells 1550amp/h 5C
24 x 2v cells 700amp/h 5C
Total bank 4350 amp/h 5C
billi
Global Moderator
Hero Member
*****
Offline Offline

Posts: 8943



WWW
« Reply #23 on: November 15, 2013, 12:59:09 PM »

no idea  in detail , just  a link to second hand forklift batteries supplier  that are tested to provide

"92-100% Kapazität.: geprüft (mit Prüfbeleg) "    (92-100% capacity)

 **refurbished
Sehr gute gebrauchte Zelle max. 5 Jahre alt, wenig Ladezyklen. Gereinigt und durch unser patentiertes Regenerationsverfahren aufbereitet. Inkl. Belastungstest (Kapazitätstest).  (max 5 years old , little cycles ,  regeneratad , incl. load test )

Seller was answering lots of questions on a German PV Forum and sounded ok ,  thats why  i linked it here





Logged

1.6 kw and 2.4 kw   PV array  , Outback MX 60 and FM80 charge controller  ,24 volt 1600 AH Battery ,6 Kw Victron inverter charger, 1.1 kw high head hydro turbine as a back up generator , 5 kw woodburner, 36 solar tubes with 360 l water tank, 1.6 kw  windturbine
nowty
Hero Member
*****
Offline Offline

Posts: 800



« Reply #24 on: November 19, 2013, 10:03:06 PM »

I wonder exactly what "refurbished" means?

They wipe the tops down with an oily rag.  hysteria
Logged

11kW+ of PV installed and 56+ MWh generated.
Lithium battery storage of 50+ kWh.
Hot water storage of 15+ kWh.
Heat storage of 15+ kWh.
6kW Ground source heatpump.
EV BMW i3 (another 30+ kWh's of storage).
260,000+ litres of water harvested from underground river.
Home grown Fruit and Veg.
Pages: 1 [2]   Go Up
  Print  
 
Jump to:  

Powered by MySQL Powered by PHP Powered by SMF 1.1.20 | SMF © 2013, Simple Machines
SMFAds for Free Forums
Simple Audio Video Embedder
Valid XHTML 1.0! Valid CSS!