News: Anyone wishing to register as a new member on the forum is strongly recommended to use a "proper" email address - following recent spam/hack attempts on the forum, all security is set to "high", and "disposable" email addresses like Gmail, Yahoo and Hotmail tend to be viewed with suspicion, and the application rejected if there is any doubt whatsoever
 
Recent Articles: Navitron Partners With Solax to Help Create A More Sustainable Future | Navitron Calls for Increased Carbon Footprint Reduction In Light of Earth Overshoot Day | A plea from The David School - Issue 18
   Home   Help Search Login Register  
Pages: 1 [2]   Go Down
  Print  
Author Topic: DC breakers/fuses  (Read 4424 times)
billi
Global Moderator
Hero Member
*****
Offline Offline

Posts: 8920



WWW
« Reply #15 on: June 24, 2014, 08:28:48 AM »

Quote
Maybe Billi's switches work fine because he doesn't turn his PV off often in full sunlight (why would he)?

EA ,  the one i suggested to Stephan is not the one i have , but many others use them , cause they address the bespoke problem

It seems a nightmare  , what some "Accessoires" can cost  and probably a good idea to get as much info  as possible  about those

I have three of those  between the battery and the inverter  and the 2 PV  controllers

and surely i used those  a few times to disconnect the PV from the system  (if needed )

But hey , my PV is only wired to 66 V    so kinda low and remaining in the hobby league     ,  but this was intended from the start .... DC is my Voltage for AC  i get Bon Scott (my electrician)

my fuses are fitted in the Victron  DC Link box  that seemed pricy when i got it  8 years back , but worth  it for people like me (in a growing system)  , with two right hands and a brain that has other things to do then always thinking  in numbers


CU





* GTI.jpg (106.77 KB, 709x578 - viewed 300 times.)
« Last Edit: June 24, 2014, 08:39:03 AM by billi » Logged

1.6 kw and 2.4 kw   PV array  , Outback MX 60 and FM80 charge controller  ,24 volt 1600 AH Battery ,6 Kw Victron inverter charger, 1.1 kw high head hydro turbine as a back up generator , 5 kw woodburner, 36 solar tubes with 360 l water tank, 1.6 kw  windturbine
Eccentric Anomaly
Sr. Member
****
Offline Offline

Posts: 404


WWW
« Reply #16 on: June 24, 2014, 08:42:09 AM »

Quote
Maybe Billi's switches work fine because he doesn't turn his PV off often in full sunlight (why would he)?

EA ,  the one i suggested to Stephan is not the one i have , but many others use them , cause they address the bespoke problem

Hi Billi, I think we might be talking at cross-purposes. I was commenting on and asking about the “disconnect” switches that Stephen linked to in his first post. I've no idea what switches you use other than that you implied you used something very similar. I think those 150 A breakers you linked to ought to be fine and agree with you that if Justme is right that they're not adequate then they're badly specified.
Logged

He who refuses to do arithmetic is doomed to talk nonsense - John McCarthy.
Tinbum
Hero Member
*****
Offline Offline

Posts: 1156


« Reply #17 on: June 24, 2014, 08:59:04 AM »

I use something like this.

I have a 60kVa 3 phase ups and the battery bank of about 32x12v (384v) batteries is protected by a similar item as manufactured. They do come up for sale at good prices on auction sites. Take careful note of the sensor part through as some are AC, some DC and some both.


* IMAG0471.jpg (148.26 KB, 816x460 - viewed 293 times.)
« Last Edit: June 24, 2014, 11:19:20 AM by Tinbum » Logged

85no 58mm solar thermal tubes, 28.5Kw PV, 3 x Sunny Backup 5048, 3x Sunny Island 5048, 2795 Ah (135kWh) (c20) Rolls batteries 48v, Atmos wood gasification boiler, Brosley wood burner, 2000lt buffer tank and 250lt DHW
billi
Global Moderator
Hero Member
*****
Offline Offline

Posts: 8920



WWW
« Reply #18 on: June 24, 2014, 09:50:06 AM »

Quote
Hi Billi, I think we might be talking at cross-purposes

Can happen ,  actually happens very often  in such a big universal brain    Grin


Surely , if Justme knows
Quote
I would not dream of putting more than about 20 amps through them.
the specs of a 150 A  rated  fuse better than the supplier , i will be the last person  that recommends this product  again

Logged

1.6 kw and 2.4 kw   PV array  , Outback MX 60 and FM80 charge controller  ,24 volt 1600 AH Battery ,6 Kw Victron inverter charger, 1.1 kw high head hydro turbine as a back up generator , 5 kw woodburner, 36 solar tubes with 360 l water tank, 1.6 kw  windturbine
Justme
Hero Member
*****
Offline Offline

Posts: 3526


« Reply #19 on: June 24, 2014, 05:07:07 PM »

Hi Justme, why not??

Is it breakers in general that you don't like as disconnects, or that specific model? 


Well when you think that the cable that carry my 300amps at 12v for the inverter feeds are 120mm2 & those tiny screw terminals are less than 15mm2 I cant see them lasting that long before they melt.


Quote
I would not dream of putting more than about 20 amps through them.

then report to the supplier , i would say    Wink


They were bought by me for the purpose of disconnecting under 10 amps.

They suit that purpose. They were cheap.
Logged

Navitron solar thermal system
30 x 58mm panel 259L TS
1200watts solar 120vdc
FX80 Solar controller
Victron 12v 3000w 120a
6kva genny
6 x 2v cells 1550amp/h 5C
24 x 2v cells 700amp/h 5C
Total bank 4350 amp/h 5C
Eccentric Anomaly
Sr. Member
****
Offline Offline

Posts: 404


WWW
« Reply #20 on: June 24, 2014, 08:33:51 PM »

300 A at 12 V is a bit mind boggling. Why?

An aside on selection of nuts and bolts for this sort of thing: http://edavies.me.uk/2013/11/resistance-stainless/.
Logged

He who refuses to do arithmetic is doomed to talk nonsense - John McCarthy.
billi
Global Moderator
Hero Member
*****
Offline Offline

Posts: 8920



WWW
« Reply #21 on: June 25, 2014, 05:21:29 AM »

Quote
Quote from: stephendv on June 23, 2014, 04:43:18 PM
Hi Justme, why not??

Is it breakers in general that you don't like as disconnects, or that specific model?


Well when you think that the cable that carry my 300amps at 12v for the inverter feeds are 120mm2 & those tiny screw terminals are less than 15mm2 I cant see them lasting that long before they melt.

Hmm ... this somehow sounds logical  , but why are cable terminals  then having no bigger holes ??

Logged

1.6 kw and 2.4 kw   PV array  , Outback MX 60 and FM80 charge controller  ,24 volt 1600 AH Battery ,6 Kw Victron inverter charger, 1.1 kw high head hydro turbine as a back up generator , 5 kw woodburner, 36 solar tubes with 360 l water tank, 1.6 kw  windturbine
Justme
Hero Member
*****
Offline Offline

Posts: 3526


« Reply #22 on: June 25, 2014, 08:56:26 AM »

The cable terminals dont rely on the hole or the contact around the hole to transmit the current.
Its the flat faces that are held together. Those resetable fuses dont have large external contact surfaces.
I guess they also dont have large internal contacts on the switch.

We are off grid to have an inverter for our mains power.
We dont often pull the full capacity through the cables but they still need to be sized to take the max load.
Logged

Navitron solar thermal system
30 x 58mm panel 259L TS
1200watts solar 120vdc
FX80 Solar controller
Victron 12v 3000w 120a
6kva genny
6 x 2v cells 1550amp/h 5C
24 x 2v cells 700amp/h 5C
Total bank 4350 amp/h 5C
biff
Global Moderator
Hero Member
*****
Offline Offline

Posts: 11867


An unpaid Navitron volunteer who lives off-grid.


« Reply #23 on: June 25, 2014, 09:42:19 AM »

This is the main reason why we went the 120volt route.
                                     Our first system was 12volt and I learned quickly that if we were going to be anyway successful of-grid,we had to get as high in the voltage as possible within reason. I know that most off-gridders are 48volt but the amps are still very high on long runs to a DC immersion heater dump load. So 120volt seemed a reasonable compromise at the time.
  As it turned out,140volt travels well over long stretches and the fuses are still 20amp per string, with the same 20amp fuse for the turbine.
   I also believe that 120volt is kinder to the battteries. It delivers the charge better and the bank can be 2 ton Grin.
    We still have the same original 2kw iron core Chinese Inverter,sitting there unfussed for over 6 years. Our very first controller was the old type grey box affair which blew one night during a bad storm but   I installed two of the new type digital controllers. This is a good idea because if one gets whacked,the other can cope.
        We had our own way of testing dump loads, hysteria hysteria during a storm but I have grown out of that lark.
  I kept enough cardboard and tarp to cover the array if I needed to work on it in daylight.I am well aware that it is still live even after I have disconnected but the m4 connectors can be pulled apart without any nasty arcing once you disconnect the bank. Even car headlights can make the panels deliver a charge in the dark.
                                                                                             Biff
Logged

An unpaid Navitron volunteer,who has been living off-grid,powered by wind and solar,each year better than the last one.
Eccentric Anomaly
Sr. Member
****
Offline Offline

Posts: 404


WWW
« Reply #24 on: June 25, 2014, 10:28:07 AM »

We are off grid to have an inverter for our mains power.

Of course, but why 12 V? The only reason I can think of is that you started with a small 12 V system and it just grewed. Starting from scratch, 24 V would be the minimum, I'd have thought, and you'd probably need a good reason not to use 48 V or, as Biff says, more though then you get less choice of inverters.
Logged

He who refuses to do arithmetic is doomed to talk nonsense - John McCarthy.
billi
Global Moderator
Hero Member
*****
Offline Offline

Posts: 8920



WWW
« Reply #25 on: June 26, 2014, 05:39:42 AM »

The cable terminals dont rely on the hole or the contact around the hole to transmit the current.
Its the flat faces that are held together. Those resetable fuses dont have large external contact surfaces.
I guess they also dont have large internal contacts on the switch.

We are off grid to have an inverter for our mains power.
We dont often pull the full capacity through the cables but they still need to be sized to take the max load.

So back to Stephan s question ,  would you suggest then  , that the outback 175 a rated  unit are the way to go  with their "huge  3/8”  studs and contact area" ?? at a pricy price
... plan B ?

« Last Edit: June 26, 2014, 10:23:37 AM by billi » Logged

1.6 kw and 2.4 kw   PV array  , Outback MX 60 and FM80 charge controller  ,24 volt 1600 AH Battery ,6 Kw Victron inverter charger, 1.1 kw high head hydro turbine as a back up generator , 5 kw woodburner, 36 solar tubes with 360 l water tank, 1.6 kw  windturbine
Billy
Guest
« Reply #26 on: June 26, 2014, 08:29:55 AM »

Morning all,

My high current gear is all joined up with 3/8th"/10mm stud and 140mm2 cable.  We are talking 350/400 draw for the thruster and a bit less for the winch.  Mega fuses for me, and some suitably rated battery disconnects.
Logged
Justme
Hero Member
*****
Offline Offline

Posts: 3526


« Reply #27 on: June 26, 2014, 04:48:57 PM »

We are off grid to have an inverter for our mains power.

Of course, but why 12 V? The only reason I can think of is that you started with a small 12 V system and it just grewed. Starting from scratch, 24 V would be the minimum, I'd have thought, and you'd probably need a good reason not to use 48 V or, as Biff says, more though then you get less choice of inverters.

We first sourced a 12v victron at a bargain price, then matched a medium battery bank (at a bargain price) to it. From there it just grew so the next victron had to be 12v then increased the battery bank. If we need to change the inverter again we could go 12 24 or 48v without needing to buy extras as the outback controller will do all of them.
Logged

Navitron solar thermal system
30 x 58mm panel 259L TS
1200watts solar 120vdc
FX80 Solar controller
Victron 12v 3000w 120a
6kva genny
6 x 2v cells 1550amp/h 5C
24 x 2v cells 700amp/h 5C
Total bank 4350 amp/h 5C
stephendv
Hero Member
*****
Offline Offline

Posts: 928



WWW
« Reply #28 on: June 30, 2014, 09:43:15 AM »

In the end I went for a 150A megafuse + chunky mechanical disconnect switch linked to on the first page.  Since this is for someone else's system I don't want to take any chances with having short circuited batteries and then having a breaker which may not be able to break the massive currents.

The part of the megafuse that's designed to melt is only a thin flat strip about 1mm thick and 2mm wide.
Logged

http://www.casanogaldelasbrujas.com
2.8kW PV, SMA Sunny Island 5048, 5 PzS 700 battery bank, stinky diesel.