News: Anyone wishing to register as a new member on the forum is strongly recommended to use a "proper" email address - following recent spam/hack attempts on the forum, all security is set to "high", and "disposable" email addresses like Gmail, Yahoo and Hotmail tend to be viewed with suspicion, and the application rejected if there is any doubt whatsoever
 
Recent Articles: Navitron Partners With Solax to Help Create A More Sustainable Future | Navitron Calls for Increased Carbon Footprint Reduction In Light of Earth Overshoot Day | A plea from The David School - Issue 18
   Home   Help Search Login Register  
Pages: [1] 2   Go Down
  Print  
Author Topic: AC DC 250v or 600v  (Read 3532 times)
camillitech
Hero Member
*****
Offline Offline

Posts: 5401



WWW
« on: November 14, 2014, 09:37:05 AM »

Bit of a dilemma here chaps,

I need to move the electrickery from my Stream Engine hydro turbine 200m, or do I?

One of my hydro turbines is 450m away from the house I'm in just now, it generates 3 phase at the turbine and is transformed and rectified to charge my 48v bank. Anyway, current house is sold and I need to move the energy to the new house 200m away. The normal AC voltage at around 800w is 250 and the OC voltage around 450.

I seem to have several options, extend the DC from the transformer straight to new battery, would need 35mm square 2 core at least.

Extend the three core 200m to the new battery bank and put the transformer there, 4mm or 6mm would do.

Rectify it where it is now and 'AC couple' it for the price of an inverter with no cables required. This would seem the cheapest and sensible option but the OC voltage once rectified would, I'm guessing be close to the 600v limit of most small inverters.

Any one know of an inverter that will take more, or a way of clamping the voltage at 600v.

Any suggestions of other alternatives most welcome.

Cheers, Paul
Logged

http://lifeattheendoftheroad.wordpress.com/

'Off grid' since 1985,  Proven 2.5kW, Proven 6kW direct heating, SI6.OH, 800ah Rolls, 4.75kW PV ,4xTS45, Lister HR2 12kW, , Powerspout pelton, Stream Engine turgo, 60 x Navitron toobs and a 1500lt store. Outback VFX3048 and 950ah forklifts for backup,
Fintray
Hero Member
*****
Offline Offline

Posts: 793



« Reply #1 on: November 14, 2014, 10:28:20 AM »

Put the AC through a 240 to 110 transformer, rectify it and put into inverter?
Logged

3.87kWp PV
10.24kWp PV SolarEdge system
Tesla Powerwall 2
100 x 47mm Navitron tubes (still being installed!)
MK2 PV router DHW diverter
Morso 5kW WBS
billi
Global Moderator
Hero Member
*****
Offline Offline

Posts: 8921



WWW
« Reply #2 on: November 14, 2014, 10:29:09 AM »

Hi Paul ,

if its transformed to 48 Volt DC  you could  use a small  GTI  like a Soladin or bigger ?

Not the most efficient  way , i assume


But , this sounds ok to me
Quote
Extend the three core 200m to the new battery bank and put the transformer there, 4mm or 6mm would do


Billi
Logged

1.6 kw and 2.4 kw   PV array  , Outback MX 60 and FM80 charge controller  ,24 volt 1600 AH Battery ,6 Kw Victron inverter charger, 1.1 kw high head hydro turbine as a back up generator , 5 kw woodburner, 36 solar tubes with 360 l water tank, 1.6 kw  windturbine
camillitech
Hero Member
*****
Offline Offline

Posts: 5401



WWW
« Reply #3 on: November 14, 2014, 12:50:03 PM »

Put the AC through a 240 to 110 transformer, rectify it and put into inverter?

It's three phase Fintray, would that work?

Extend the three core 200m to the new battery bank and put the transformer there, 4mm or 6mm would do



That's the way I was leaning Billi, for two reasons, 1, I know it'll work and 2 it's going straight into the batteries. However it does mean buying 200m of SWA and laying it. Whereas if I 'AC couple' it I could probably get a second hand GTI for buttons, I actually have a new SB3800 which is good for 500v and I've just noticed it will disconnect if the voltage gets too high. As my 'mini grid' is already in the shed where the transformer is, I could in theory be 'up and running' for the price of a rectifrier. On the other hand I could end up  sh*tfan

Cheers, Paul
Logged

http://lifeattheendoftheroad.wordpress.com/

'Off grid' since 1985,  Proven 2.5kW, Proven 6kW direct heating, SI6.OH, 800ah Rolls, 4.75kW PV ,4xTS45, Lister HR2 12kW, , Powerspout pelton, Stream Engine turgo, 60 x Navitron toobs and a 1500lt store. Outback VFX3048 and 950ah forklifts for backup,
Fintray
Hero Member
*****
Offline Offline

Posts: 793



« Reply #4 on: November 14, 2014, 03:34:19 PM »

Duh, sorry missed the 3 phase bit!

Why not rectify it at the turbine then only 2 core SWA required?
TLC show 4mm 2 core SWA at 125/100m, might be worth trying your "nearest" electrical wholesaler for a better price.
Logged

3.87kWp PV
10.24kWp PV SolarEdge system
Tesla Powerwall 2
100 x 47mm Navitron tubes (still being installed!)
MK2 PV router DHW diverter
Morso 5kW WBS
guydewdney
Hero Member
*****
Offline Offline

Posts: 4320



« Reply #5 on: November 14, 2014, 05:01:42 PM »

The "wind interface" of a power one system limits voltage to 530v......
Logged

Pic of wheel on day 1
7.2kW Waterwheel and 9.8kW PV
Tinbum
Hero Member
*****
Offline Offline

Posts: 1156


« Reply #6 on: November 14, 2014, 05:37:03 PM »

Duh, sorry missed the 3 phase bit!

Why not rectify it at the turbine then only 2 core SWA required?
TLC show 4mm 2 core SWA at 125/100m, might be worth trying your "nearest" electrical wholesaler for a better price.

Also volt for volt dc transmission is also more efficient.
Logged

85no 58mm solar thermal tubes, 28.5Kw PV, 3 x Sunny Backup 5048, 3x Sunny Island 5048, 2795 Ah (135kWh) (c20) Rolls batteries 48v, Atmos wood gasification boiler, Brosley wood burner, 2000lt buffer tank and 250lt DHW
clockmanFR
Hero Member
*****
Offline Offline

Posts: 3584



WWW
« Reply #7 on: November 14, 2014, 06:56:39 PM »

Over distance AC high voltage wins out, as you say one can use thinner cables.

If it were me I would send the 3 phase AC all the way, then you can see what the cable length voltage drop would be, then into some rectifiers to DC. That new Tristar Battery Charger unit can take 500vdc. ?

On the other hand Second hand SMA Sunny Boys are a good price and you can AC couple after your rectifiers now its DC voltage, into your mini Grid at your shed.
NB, I notice that my SB1200 will take 400vdc max while the SB3800 will take 500vdc max. 

I did get some 4 core 16mm/2 for my trackers 130meters distance on the DC output, from fleebay at a good price, and doubled up the cores so I have 32mm/2.

NB, according to Hugh when AC is rectified the DC voltage is nearly 40% more,  faint hmm not sure of that, need to look at that a bit more.
Logged

Everything is possible, just give me TIME.
Mostie
Sr. Member
****
Offline Offline

Posts: 495



« Reply #8 on: November 14, 2014, 07:08:50 PM »

I'm with Clockman, you don't want your kit out in the pi$$ing rain, AC all the way, if it means smaller cable.

keep your rectumfrier warm and dry  ralph
Logged

2x Solis PV = 1.875 kW, Mitsubishi inverter heat pump. Yorkshire Boiler Stove.
camillitech
Hero Member
*****
Offline Offline

Posts: 5401



WWW
« Reply #9 on: November 14, 2014, 07:52:13 PM »



NB, according to Hugh when AC is rectified the DC voltage is nearly 40% more,  faint hmm not sure of that, need to look at that a bit more.

Methinks you multiply the AC x 1.412 to get  the DC CM.

Why not rectify it at the turbine then only 2 core SWA required?

It's already 3core and three phase for 450m to the shed from the turbine, so no point altering that. However rectifying it in the shed then sending the high voltage DC down twin core to the new house is worth investigation.

The "wind interface" of a power one system limits voltage to 530v......


So basically it just 'trips' and does no harm? This would be the simplest solution as there is already a 10 or 16mm square mains cable laid between the shed and new house. Hmmmmmmmmmm
Logged

http://lifeattheendoftheroad.wordpress.com/

'Off grid' since 1985,  Proven 2.5kW, Proven 6kW direct heating, SI6.OH, 800ah Rolls, 4.75kW PV ,4xTS45, Lister HR2 12kW, , Powerspout pelton, Stream Engine turgo, 60 x Navitron toobs and a 1500lt store. Outback VFX3048 and 950ah forklifts for backup,
guydewdney
Hero Member
*****
Offline Offline

Posts: 4320



« Reply #10 on: November 14, 2014, 07:57:44 PM »

It gradually cuts in a dump load maintaining the 530v. Pretty crude but works.
Logged

Pic of wheel on day 1
7.2kW Waterwheel and 9.8kW PV
billi
Global Moderator
Hero Member
*****
Offline Offline

Posts: 8921



WWW
« Reply #11 on: November 14, 2014, 08:03:57 PM »

The "wind interface" of a power one system limits voltage to 530v......
 

Good thinking  GuY

Was there not as well  a WindyGirl idea ?   http://www.windygirl.biz/    

Paul ,    i hope you keep   a  part of   battery charging on the DC side  as well
Logged

1.6 kw and 2.4 kw   PV array  , Outback MX 60 and FM80 charge controller  ,24 volt 1600 AH Battery ,6 Kw Victron inverter charger, 1.1 kw high head hydro turbine as a back up generator , 5 kw woodburner, 36 solar tubes with 360 l water tank, 1.6 kw  windturbine
camillitech
Hero Member
*****
Offline Offline

Posts: 5401



WWW
« Reply #12 on: November 14, 2014, 08:08:55 PM »

It gradually cuts in a dump load maintaining the 530v. Pretty crude but works.

Ahhhh, I recall you mentioning this in a post some years ago, think you referred to it as a 'bit of a sledgehammer' or words to that effect, crude but effective. Sounds like the way forward for me really, the voltage from the turbine is only ever likely to exceed that if the GTI 'drops out' for some reason. However, as I type this I realize that this does occasionally happen with the SMA GTI's if I start my large 'chop saw'. Hmmmmmmmmmmm  help 
Logged

http://lifeattheendoftheroad.wordpress.com/

'Off grid' since 1985,  Proven 2.5kW, Proven 6kW direct heating, SI6.OH, 800ah Rolls, 4.75kW PV ,4xTS45, Lister HR2 12kW, , Powerspout pelton, Stream Engine turgo, 60 x Navitron toobs and a 1500lt store. Outback VFX3048 and 950ah forklifts for backup,
clockmanFR
Hero Member
*****
Offline Offline

Posts: 3584



WWW
« Reply #13 on: November 14, 2014, 08:13:40 PM »

Paul.......

I am getting worried about the Sunny Island charging regime.

Like you, I think, ? I will retain DC battery charging with my 3 tristars, my Midnite and Morningstar MPPT controllers.

My main concern is that the Sun is out, I am getting PV feed in to the SI Mini Grid, AC Coupling, and my Tristar battery charger controllers go to Float first and the ruddy SI keeps trying to put a charge into the batteries.

Then my 3 tristar controllers then try and dump excess voltage, into my 8kW of dump loads,,,,, aaaaaaggggghhhh.

I will experiment.  
Logged

Everything is possible, just give me TIME.
guydewdney
Hero Member
*****
Offline Offline

Posts: 4320



« Reply #14 on: November 14, 2014, 08:19:08 PM »

I have a spare interface, but sonething went wrong with it. Will try to find out. If it still works as an overvoltage protection (a 500v zener diode?) then you can have it.