News: Anyone wishing to register as a new member on the forum is strongly recommended to use a "proper" email address. Following continuous spam/hack attempts on the forum, "disposable" email addresses like Gmail, Yahoo and Hotmail tend to be viewed with suspicion, and the application rejected if there is any doubt whatsoever
 
Recent Articles: Navitron Partners With Solax to Help Create A More Sustainable Future | Navitron Calls for Increased Carbon Footprint Reduction In Light of Earth Overshoot Day | A plea from The David School - Issue 18
   Home   Help Search Login Register  
Pages: [1]   Go Down
  Print  
Author Topic: Relay wiring questions  (Read 18007 times)
freddyuk
Sr. Member
****
Offline Offline

Posts: 437


« on: January 12, 2018, 10:27:19 AM »

I am rewiring my S PLAN central heating system to separate the UFH and Radiator heating circuits. I have 3 radiator zones and 2 ufh zones with 2 cylinders for DHW.
All the radiator zones and DHW are in one wiring centre with UFH in a second wiring centre (too much for 1 centre!)
All zones controlled by programmable room stats. DHW by standard cylinder stats (with solar surplus diversion control).
I have a mixing valve for the UFH which uses boiler circuit water so this cools it down. You need to pull the UFH flow through this valve so a second pump is required. Pump 1 is standard S Plan feeding 5 wire motorised valves to each zone.
Pump 2 has 2 motorised valves which split the loops into 2 zones.

In standard S plan the pump and boiler are switched on by any of the valves energising the orange wire via any of the thermostats calling for heat and switching power through. The pump and boiler are common.
If I want to use 2 pumps and separate the zones for each pump I need to separate the pumps from the boiler power or otherwise both pumps will run.
I have a relay (8 pin) which I want to use to connect Pump1 for all the rads and switch over to Pump2 for just the UFH.
If both pumps are required then they must be able to run together. I think I need 2 relays to achieve this as one will switch on or off just one pump.
I have no idea how to wire this to make it work.
Has anyone done this?

Logged
offthegridandy
Hero Member
*****
Offline Offline

Posts: 1013



« Reply #1 on: January 12, 2018, 11:10:38 AM »

A drawing would help Freddy but I think I get your drift.

I agree you will need two relays.

Live feed from boiler to relay 1 C and relay 2 C. Relay one gets signal from zone one to switch relay one, and pump one goes live. Relay 2 takes signal from zone 2 if zone 2 is calling then pump two gets switched as well. Or vice versa.

Andy
Logged

8 KVA Lister TS2 Startamatic Genny
24 Volt 1000amp battery bank
Outback VFX3024
4.6 Kw PV array ground mounted
Outback Flexmax 80
2 X Flexmax 30 PV CC
2.5 Kw WT H Piggot design 4.5 Mtr Dia AC coupled
12 Mtr free standing Tower.
u/floor heating from oil boiler cross linked to 12 K wood stove
martin W
Hero Member
*****
Offline Offline

Posts: 700


what do you mean my snoring is too loud!


WWW
« Reply #2 on: January 12, 2018, 06:11:08 PM »

Slightly off topic, as a drawing would help me understand the layout you've got...


Salus do a cracking wiring centre which is quite large, and very configurable..

http://www.salus-tech.com/products/trv-and-accessories/tc100/

usually about 15 from eBay, amazon, etc...
Logged

Woodstove owner since Feb 2011 Tongue (yes it's finally off the pallet)
Solar Water Heating since 17th March 2009, 2.94kW PV since Dec 2011
Chicken Owner - Self sufficient in chicken c*@p, boy watch those tomatoes grow. Allotment owner since August 2011
Now an Lister wannabie Tongue
freddyuk
Sr. Member
****
Offline Offline

Posts: 437


« Reply #3 on: January 13, 2018, 08:08:59 AM »

Here is a standard S Plan layout. The pump and boiler are connected to terminal 10 so each valve can open and switch on both boiler and pump. Now add a new zone valve with it's own pump for UFH and you can see you cannot connect the new pump to the boiler as the boiler must be fired by pump 1 and if that boiler connection is live both pumps will come on. You have to separate the new pump from main pump and also connect to the boiler but be isolated from the other zones on terminal 10 and the main pump.

I ended up with 8 pin DPDT relays. I need to split the zone valves to there own switched terminal so UFH goes to one terminal and the other zones go to a separate terminal.

I power up relays through pins 1 and 7 to energise the coil from the switched terminals of the valves ie. orange wires (say terminal 11 and 12)) so any valve opening will power up the respective relay? I have live from terminal 11 going to pin 7 and a neutral going to pin 1. Valve opens and relay closes the NO contacts?
How do I wire the pumps and boiler to these. ? Is it just the live feed for pump 1 in and out with neutral picked up in wiring centre on one NO connection and boiler live feed to the same NO connection? Then do the same for the other relay with another common boiler live feed and live feed to pump 2.
Zone 1 calls for heat and boiler and Pump 1 switch on. Then UFH calls and boiler is already running so just pump 2 starts up. Then Zone 1 is satisfied so valve closes and Pump 1 stops but pump 2 and boiler keep going.......

Logged
freddyuk
Sr. Member
****
Offline Offline

Posts: 437


« Reply #4 on: January 13, 2018, 05:19:59 PM »

It does not work! Tried various ways to wire in the boiler via separate terminal but it still backfeeds to the relays. I can have one pump and boiler running OK. I then switch second zone with Pump 2 and both pumps run and boiler runs.
When I turn off either zone the relays remain energised so pumps run but valves are closed.

Commoning the boiler into relay backfeeds.
Using the other terminal NC to get a relay feed does work but as soon as both relays are on one or the other will not switch off due to the boiler which must power up the relay either terminal that is connected.

I am out of ideas?

Logged
paul149
Hero Member
*****
Offline Offline

Posts: 733


« Reply #5 on: January 13, 2018, 06:40:19 PM »

PhotoBlockit strikes again, Brilliant, the death knell to all highly informative and enlightening forum threads!!!

Paul m.
Logged

3.5 kWp (14 x Sanyo H250E01 + SB3000TL) 225' (SW) at 35' Pitch Lat 51.30' (Bristol) Installed cost 2.63/Wp (Nov 2011) now with solarimmersion and 250L unvented dhw (Almost Zero gas input for DHW from Apr to mid Sep)
Antman
Global Moderator
Hero Member
*****
Offline Offline

Posts: 2039


WWW
« Reply #6 on: January 13, 2018, 06:50:58 PM »

Can't see your diagram due to pbucket hosting restriction. Try uploading it to the Forum store.

I'm trying to get my head around the various posts. But have you tried separating the boiler CFH (Call for Heat) from UFH and S-Plan via two independant relay NO contacts? So...

  S-Plan valve runs main pump from term 10 (commoned Zvalve switches) as usual but also to coil of Relay1.  NO to Live and Com of relay 1 to boiler CFH.

  UFH valve runs UFH pump and coil of Relay2. NO of Relay2 goes to L and Com of Relay2 to boiler CFH.

This should isolate the CFH to boiler from respective sources. I am assuming that the primary S-Plan pump is directly connected to terminal 10 and not direct from the boiler via a pump over-run relay (within the boiler). That may give you unexpected results.
Also make sure there is no hidden/missed commoned connection link left in somewhere joining the pump or boiler connections.

Antman
Logged

20 x 47mm, 172 l cylinder, Heat Dump, 15 x Sanyo HIT-H250E, SB4000TL,  Nestor Martin IQ13 WBS
DIY Solar System Support at http://www.handyantman.co.uk/antman.html
All support is voluntary and free of charge. I'm not employed by Navitron so responses may not be same-day
freddyuk
Sr. Member
****
Offline Offline

Posts: 437


« Reply #7 on: January 13, 2018, 07:24:33 PM »

I think I have it sorted. There are a lot of permutations but I had switched lives when I could use permanent lives and also the boiler feeds were connected to a different pin. Andy was correct but there are a few other cables to get right!
I will do a drawing so it can be verified in case anyone else wants to do this. I feel a bit inadequate having not got this right first time.... banghead
Logged
offthegridandy
Hero Member
*****
Offline Offline

Posts: 1013



« Reply #8 on: January 14, 2018, 09:26:17 PM »

Sorry Freddy I can't see a diagram either so can't be of more help yet I'm sure it must be possible.

Good luck.
Andy
Logged

8 KVA Lister TS2 Startamatic Genny
24 Volt 1000amp battery bank
Outback VFX3024
4.6 Kw PV array ground mounted
Outback Flexmax 80
2 X Flexmax 30 PV CC
2.5 Kw WT H Piggot design 4.5 Mtr Dia AC coupled
12 Mtr free standing Tower.
u/floor heating from oil boiler cross linked to 12 K wood stove
Pages: [1]   Go Up
  Print  
 
Jump to:  

Powered by MySQL Powered by PHP Powered by SMF 1.1.20 | SMF © 2013, Simple Machines
SMFAds for Free Forums
Simple Audio Video Embedder
Valid XHTML 1.0! Valid CSS!