News: Anyone wishing to register as a new member on the forum is strongly recommended to use a "proper" email address - following recent spam/hack attempts on the forum, all security is set to "high", and "disposable" email addresses like Gmail, Yahoo and Hotmail tend to be viewed with suspicion, and the application rejected if there is any doubt whatsoever
 
Recent Articles: Navitron Partners With Solax to Help Create A More Sustainable Future | Navitron Calls for Increased Carbon Footprint Reduction In Light of Earth Overshoot Day | A plea from The David School - Issue 18
   Home   Help Search Login Register  
Pages: [1] 2   Go Down
  Print  
Author Topic: Mixing Lithium and Lead  (Read 3444 times)
nowty
Hero Member
*****
Offline Offline

Posts: 562



« on: February 13, 2018, 11:23:36 PM »

Last year I bought several cheap second hand Growatts with 5 kWh batteries off fleebay, one of which I had been keeping as a spare. But my experience is once you buy a spare item, it never gets used so I started thinking of uses for it. The battery cannot be used without the Growatt controller as its operation is locked down. I was a bit bored the other day so decided to take the back off the battery and have a closer look to see if it could be easily unlocked. tumble



It contains 14 battery modules in series and a proprietary protection circuit board. Each battery module contains 18 of 5,300 mAh cells in parallel so a total of 252 cells. Each cell is apparently two 18650’s in parallel in a single package. Shocked

http://liionbms.com/pdf/bostonpower/swing5300.pdf

First thing was to rip out the protection board and then the two battery racks conveniently come out to give 24v each. Then I had a crazy idea, my Sunny Island runs at 24v using forklift cells. Would it be possible to add them in parallel to increase my OffGrid capacity ? wackoold

It sounded like an absurd idea, mix lithium and lead ?, but the more I thought about it, the more it started to be a possibility. Charge and discharge graphs are different, but my operating range of lead is typically between 100% and 75% SOC. Voltage wise, this matches favourably with lithium between 100% and 40% SOC. Although I would only be adding circa 20% more Ah capacity, the actual usable capacity might increase by 50% or more. At high SOC, the lithium ones would provide most of the power so may extend the life of my forklift cells which are now 6 years old.

I took out the two lithium racks and connected them in parallel with my forklift cells when the voltages were roughly equal to prevent any initial current surges. fingers crossed!





Then I reduced the charging voltage of my Sunny Island from the current 30.5v to 29.4v and set the temp compensation to zero. 29.4v gives the max 4.2v charging voltage per lithium module and is still good enough for the forklift cells. bike

Next day was full sun chocolateteapot, so I measured the voltage of each lithium module regularly. Voltage increased more slowly than just with lead alone and the lithium was taking 75% of the current. When the voltage rose to around 28v the current was shared equally, then over 29v the lead was taking most of the current. The voltage of each lithium module was identical except for one with was 0.1v more, so cells looks nicely balanced so far. When the charging day was over at 29v, the lithium then discharged slightly and continued to charge the lead until the voltages stabilised at around 27v so continued the absorption charge of the lead even after the sun went down. Grin

On discharge, from 27v down to 26v the lithium was supplying almost all the load.
From 26v down to 25v, the lead started to supply some of the load.
At 25v lithium and lead were supplying exactly half and then the voltage hardly moved down to 24.5v by the morning.

My first result is encouraging, no dramas sh*tfan, definite increase in capacity, better voltage stabilisation on discharge and batteries accepted the max charge from the Sunny Island all the time without throttling back. This is an advantage I had not even thought of. ralph

Going forward I need to sort out some sort of protection circuit for the lithium as I cannot risk leaving it day after day charging the lithium to near 100%. norfolk

Watch this space     …………………………..........
« Last Edit: April 21, 2018, 06:37:20 PM by nowty » Logged

10kW of PV installed and 40+ MWh generated.
Usable battery storage of 50+ kWh.
Heat storage of 20+ kWh.
6kW Ground Source Heatpump.
190,000+ litres of water harvested from underground river.
A few cold frames and raised beds.
rogeriko
Hero Member
*****
Offline Offline

Posts: 1281



WWW
« Reply #1 on: February 13, 2018, 11:40:32 PM »

There's hundreds on fleabay https://www.ebay.co.uk/sch/i.html?_from=R40&_sacat=0&_nkw=li-ion+protection+7s
Logged

knighty
Hero Member
*****
Offline Offline

Posts: 2708


« Reply #2 on: February 14, 2018, 02:07:27 AM »

if you search for BMS it will give you a lot of options

there's a hell of a lot to chose from... most will just monitor the cells and dump power into resistors (making heat) to discharge any cells which are over discharging

but... you can get fancy ones which will dump power from high cells into low cells


if you parallel up the balance wires, then you'll only need one BMS for the whole lot :-)
Logged
linesrg
Hero Member
*****
Offline Offline

Posts: 730



WWW
« Reply #3 on: February 14, 2018, 09:08:18 AM »

nowty,

Now I know what the inside of my battery looks like!!!

I can see it wouldn't be that difficult to re-wire things internally to allow the cells to be charged by an external power supply. As I may have noted elsewhere simply connecting the positive and negative leads from the Growatt battery to a charger does nothing as the circuitry obviously needs a signal from the Growatt SP2000 unit.

I some very heavy duty (Albright) DPDT solenoids which can be used for this.

Regards

Richard
Logged

16 BP380 on a Lorentz ETATRACK1000/SB1700, 16 Chinese 80W/SB1700, 16 BP380/SMA SB1700. CTC GSi12 + Ecosol + Flowbox 8010e/Gledhill ASL0085 EHS/3 Navitron 4720AL solar ET panels and Immersun T1060/ T1070/ T1090. 7 Tianwei 235W/ Aurora PVI 3.6kW/ Growatt SP2000 c/w 5kWhr battery and a Renault Zoe
biff
Global Moderator
Hero Member
*****
Offline Offline

Posts: 11461


An unpaid Navitron volunteer who lives off-grid.


« Reply #4 on: February 14, 2018, 09:15:10 AM »

Wow,
    Exciting stuff Nowty,  I wonder what it would take to put together a 120volt bank, ?
   Could I chain a series of Growatts together, ?
                                       Biff
    I guess the thing to do would be to study the suitable BMSs first and then try and find the way to keep them happy.
 I could sell my Lead acid friends.. genuflect
« Last Edit: February 14, 2018, 09:29:01 AM by biff » Logged

An unpaid Navitron volunteer,who has been living off-grid,powered by wind and solar,each year better than the last one.
Westie
Sr. Member
****
Offline Offline

Posts: 459


« Reply #5 on: February 14, 2018, 09:48:25 AM »

Assuming the SI is set for charging LA batts  SI will trickle charge as is normal for LA,  so isn't there a danger of overcharging the Li batteries during trickle charging?

I would be thinking about protecting against fault current flowing between banks  by adding a fuse between them?

Would be nice to get a schematic of the Growatt BMS, if the 'authorisation' handshake could be faked the BMS would probably still operate.


Logged

4kwp south facing array  SMA 4000TL grid connected.  2x30tube Navitron solar thermal panels (east/west). Arada 5kw S/C WBS. 25000Ltr underground rain water tank. KTM E-Bike  Cool
Fionn
Hero Member
*****
Offline Offline

Posts: 508


« Reply #6 on: February 14, 2018, 10:04:10 AM »

Would it not make more sense to connect the pack in parallel with one of your existing growatt units, even if at the module level?

If you're looking for a cheap but useful BMS, this one is worth a look:
https://www.aliexpress.com/item/14S-Smart-Li-ion-Battery-PCB-board-Bluetooth-Mobile-BMS-for-48V-58-8VLi-Ion/32794186005.html

The majority of the ones on eBay have no adjustability on their settings so you can't vary the over voltage and under voltage limits.

Was there any fusing between the parallel packs in each module out of interest?

If you held onto the existing BMS it might be of interest to someone with a bare Growatt and other batteries.
Logged
nowty
Hero Member
*****
Offline Offline

Posts: 562



« Reply #7 on: February 23, 2018, 09:38:51 PM »

Project Updates,

Lined the shed with cement board to prevent the odd fire mishap. It won’t survive a full-on lithium fire, but it will mitigate against scorching by blown fuses, loose connections, etc. fingers crossed!

Added an isolator.

Added fuses for each parallel battery string. fingers crossed!

Picked up another cheap Growatt, so I now have four battery strings. extrahappy




Added a DC isolator to the lead batteries so I can just run off the lithium if I want to. In fact, in future, I am thinking of only running on lithium during the winter months. tumble



I have been manually balancing the batteries by,

Using a 50w resister to reduce down any high cells. I found one cell which was 0.2v too high and bled it off for a couple of hours with a 1 ohm resistor. ballspin


Using a bench low voltage supply to charge up any low cells, I found one which was 0.4v too low. Five hours of individual charging brought it back up in line with the others. fume



Apart from those two cells all other cells were found to be within 0.05v of each other and all are now  keeping balanced after several charge / discharge cycles. signofcross


I have been manually isolating the lithium when the bank voltage hits around 28v (cell voltages of 3.8v and 80% SOC), and then continuing the charge on the lead up to 30v. At the end of the charging day I reconnect the lithium bank.
I have ordered a heavy duty normally closed DC contactor relay which will be opened and closed by a voltage sensing relay to perform this task automatically. whistlie
« Last Edit: April 21, 2018, 07:01:39 PM by nowty » Logged

10kW of PV installed and 40+ MWh generated.
Usable battery storage of 50+ kWh.
Heat storage of 20+ kWh.
6kW Ground Source Heatpump.
190,000+ litres of water harvested from underground river.
A few cold frames and raised beds.
biff
Global Moderator
Hero Member
*****
Offline Offline

Posts: 11461


An unpaid Navitron volunteer who lives off-grid.


« Reply #8 on: February 23, 2018, 10:48:34 PM »

Wow Nowty,
         I am green wif impreszions. You have some crazy good gear. Yours is the battery thread of the century. Real porn.
       Biff
Logged

An unpaid Navitron volunteer,who has been living off-grid,powered by wind and solar,each year better than the last one.
knighty
Hero Member
*****
Offline Offline

Posts: 2708


« Reply #9 on: February 23, 2018, 11:25:00 PM »

you should really parallel up each cell in the packs

you could just join the balance connectors ?

should really have a fuse on each one too!


advantage is if one cell pack is a bit weak it should average out a bit with the others :-)
Logged
nowty
Hero Member
*****
Offline Offline

Posts: 562



« Reply #10 on: February 24, 2018, 05:18:04 PM »

you should really parallel up each cell in the packs

you could just join the balance connectors ?

should really have a fuse on each one too!


advantage is if one cell pack is a bit weak it should average out a bit with the others :-)

I actually did this with the first two strings, i.e. connect the balance connectors together via pin headers, but I was concerned that I would inadvertently short one out so I cut them off. facepalm

I am experimenting using some cheap crop clip test leads to parallel up in a couple of places to improve the balancing but I was only going to do this temporarily, then monitor cells over a long time to see how much the cells  drift. I agree that permanent linking should require fuses.





And today my heavy duty DC relay arrived but I am still waiting for the voltage sensing relay to wing its way from China.
« Last Edit: April 21, 2018, 06:38:14 PM by nowty » Logged

10kW of PV installed and 40+ MWh generated.
Usable battery storage of 50+ kWh.
Heat storage of 20+ kWh.
6kW Ground Source Heatpump.
190,000+ litres of water harvested from underground river.
A few cold frames and raised beds.
fourfootfarm
Sr. Member
****
Offline Offline

Posts: 289



« Reply #11 on: February 26, 2018, 07:47:14 PM »

Croc clips pretty much are fuses!

Really interesting stuff will be keeping this in mind for future upgrading
Logged

Outback FM60. EPsolar 30a MPPT and a bunch of Tristar 45's. Hodge Podge of solar ~ 4500w. Various generators and 1000ah 24v forklift battery.

Turkish Turnip
nowty
Hero Member
*****
Offline Offline

Posts: 562



« Reply #12 on: March 05, 2018, 03:30:30 PM »

Picked up another two Growatts which were sold with red lights on the battery pack so were cheaper than usual. Batteries were fine, one had a low cell which needed some individual charging and the other had batteries down to 10% SOC so just needed charging up a bit. I think I might do away with my lead acid and just run on the lithium. tumble


Other changes,
Upgraded the isolator as the original one was running a little hot. fume

Added the isolating relay and tested it at a charge rate of 80 Amps. I was surprised as it did not even spark when breaking the connection. Shocked
But I am still waiting for my voltage sensing relay from China, so i am still having to disconnect the lithium manually. facepalm

I am currently making up some fused battery links to connect all the cells together. bike

Logged

10kW of PV installed and 40+ MWh generated.
Usable battery storage of 50+ kWh.
Heat storage of 20+ kWh.
6kW Ground Source Heatpump.
190,000+ litres of water harvested from underground river.
A few cold frames and raised beds.
knighty
Hero Member
*****
Offline Offline

Posts: 2708


« Reply #13 on: March 06, 2018, 06:25:22 PM »

how big is your lead acid pack?

20kwh of LiIon is quite a bit?


how's the usable kwh or LiIon vs lead acid compare?
Logged
biff
Global Moderator
Hero Member
*****
Offline Offline

Posts: 11461


An unpaid Navitron volunteer who lives off-grid.


« Reply #14 on: March 06, 2018, 07:01:51 PM »

Neat work Nowty,