News: Anyone wishing to register as a new member on the forum is strongly recommended to use a "proper" email address - following recent spam/hack attempts on the forum, all security is set to "high", and "disposable" email addresses like Gmail, Yahoo and Hotmail tend to be viewed with suspicion, and the application rejected if there is any doubt whatsoever
 
Recent Articles: Navitron Partners With Solax to Help Create A More Sustainable Future | Navitron Calls for Increased Carbon Footprint Reduction In Light of Earth Overshoot Day | A plea from The David School - Issue 18
   Home   Help Search Login Register  
Pages: [1]   Go Down
  Print  
Author Topic: iBoost wont turn off!  (Read 416 times)
Miked2714
Newbie
*
Offline Offline

Posts: 14


« on: May 14, 2018, 08:42:03 PM »


We've had an iBoost for just over two years, and it has worked flawlessly until last week. It is now refusing to modulate itself and just heats the HW immersion element regardless of how much electricity is being generated by solar. This results in it drawing on the grid. My suspicion is that it's running at maximum (3kW) regardless as I can hear the immersion element "kettling" (and I can see on my energy monitor what we're drawing from the grid) BUT it's generally reporting on the LCD that it's "off".

The wireless connection to the sender / clamp unit in the meter box is fine so far as I know, it's certainly not saying it's lost contact.

I've turned off the master switch between iBoost and immersion for now.

Any ideas.? Installer not much use unfortunately. They prompted the iBoost as it was apparently more reliable than the other well known brand. I will go back to Marlec, but I just wondered if anyone had encountered this problem before, or am I missing something.
thanks
Mike
Logged
sunandwindy
Sr. Member
****
Offline Offline

Posts: 392



WWW
« Reply #1 on: May 15, 2018, 12:48:53 PM »

I'd be interested to hear what Marlec have to say as mine does the same/similar and a friend who has the same also does it. I've not really stopped to examine it closely.

'ours' must be about four years or more since install.
Logged

Miked2714
Newbie
*
Offline Offline

Posts: 14


« Reply #2 on: May 16, 2018, 08:09:35 AM »

Thanks, at least I'm not the only one. Do you just switch on your immersion manually now when its sunny?

I might try an inquiry via their facebook page.
Logged
TheFairway
Hero Member
*****
Online Online

Posts: 893


« Reply #3 on: May 16, 2018, 09:54:35 AM »

I don't think this is the case as you say that it is drawing from the grid and you hear kettling, but will just mention it incase anyone else stumbles upon this with a similar issue.

With some immersion controllers that have a neon indicator, this will still glow even though the comtroller effectively says that it is 'off'. Not sure of the reason, but suspect some imperfect 'off' condition in the controller or capacitance inducing a tiny voltage enough for the neon to glow but not enough to create any measurable or usable current.

So just because the neon indicator is on, doesn't necessarily mean that the immersion is heating.
Logged

3.995kWp SE PV. 5kW Burley Hollywell woodburner. Vent-Axia Sentinel Kinetic Plus MVHR

All posts are my own personal thoughts and opinions and do not represent those of my employer, clients or partners.

sunandwindy
Sr. Member
****
Offline Offline

Posts: 392



WWW
« Reply #4 on: May 16, 2018, 10:05:40 AM »

So just because the neon indicator is on, doesn't necessarily mean that the immersion is heating.
In my case I haven't looked at the neon on the spur switch, it was the rumbling in the tank I was going by.
Logged

Antman
Global Moderator
Hero Member
*****
Offline Offline

Posts: 1906


WWW
« Reply #5 on: May 16, 2018, 07:24:11 PM »

Mike
I am not familiar with the innards of the iBoost but it sounds like the SSR (solid state relay) - assuming that is what they have used - has failed short circuit. That would give the symptoms you describe.
Regards
Antman
Logged

20 x 47mm, 172 l cylinder, Heat Dump, 15 x Sanyo HIT-H250E, SB4000TL,  Nestor Martin IQ13 WBS
DIY Solar System Support at http://www.handyantman.co.uk/antman.html
All support is voluntary and free of charge. I'm not employed by Navitron so responses may not be same-day
offthegridandy
Hero Member
*****
Offline Offline

Posts: 772



« Reply #6 on: May 16, 2018, 08:16:27 PM »

Doesn't the thermostat in the immersion turn the power off when the set temperature is achieved?
Logged

8 KVA Lister TS2 Startamatic Genny
24 Volt 1000amp battery bank
Outback VFX3024
4.6 Kw PV array permanently ground mounted
Outback Flexmax 80
2 X Flexmax 30 PV CC
0.75 Kw wind turbine H Piggot design 2.4 Mtr Dia
12 Mtr lattice Tower.
u/floor heating from oil boiler cross linked to 12 Kw WBS
Dave Fowler
Newbie
*
Offline Offline

Posts: 17


WWW
« Reply #7 on: May 16, 2018, 09:27:03 PM »

Mike
I am not familiar with the innards of the iBoost but it sounds like the SSR (solid state relay) - assuming that is what they have used - has failed short circuit. That would give the symptoms you describe.
Regards
Antman
It wouldn't be an SSR (on/off device) but a proportional controller like the PAC2 from United Automation.  I'd agree in the theory that the output appears to have gone permanently 'on'.
Logged
Tinbum
Hero Member
*****
Online Online

Posts: 979


« Reply #8 on: May 17, 2018, 09:22:45 AM »

I don't think this is the case as you say that it is drawing from the grid and you hear kettling, but will just mention it incase anyone else stumbles upon this with a similar issue.

With some immersion controllers that have a neon indicator, this will still glow even though the comtroller effectively says that it is 'off'. Not sure of the reason, but suspect some imperfect 'off' condition in the controller or capacitance inducing a tiny voltage enough for the neon to glow but not enough to create any measurable or usable current.

So just because the neon indicator is on, doesn't necessarily mean that the immersion is heating.

The neon would only come on if the immersion controller is diverting to the tank or the tank is up to temperature and the thermostat has cut in. It wont be on if the immersion controller is not diverting and the tank is below temp.

It's due to a slight 'leak' though the SSR /triac when in the off state. A high resistance resistor from the output of the SSR to neutral is enough to stop it.
« Last Edit: May 17, 2018, 09:25:23 AM by Tinbum » Logged