News: Anyone wishing to register as a new member on the forum is strongly recommended to use a "proper" email address - following recent spam/hack attempts on the forum, all security is set to "high", and "disposable" email addresses like Gmail, Yahoo and Hotmail tend to be viewed with suspicion, and the application rejected if there is any doubt whatsoever
 
Recent Articles: Navitron Partners With Solax to Help Create A More Sustainable Future | Navitron Calls for Increased Carbon Footprint Reduction In Light of Earth Overshoot Day | A plea from The David School - Issue 18
   Home   Help Search Login Register  
Pages: [1] 2 3 4 5   Go Down
  Print  
Author Topic: Water Source Heat Pump Project  (Read 12144 times)
nowty
Hero Member
*****
Offline Offline

Posts: 777



« on: July 28, 2018, 12:16:01 PM »

A few years ago I fixed a major problem under my house which involved building a reinforced concrete box culvert to slightly divert an underground river. sh*tfan
When fixing the problem I purposely created a catchpit to provide a pool of subterranean water,

(a)   So I could easily pump out and harvest the water.
(b)   To incorporate a heat exchanger for a heatpump as water temp ranges from a high of 14 degrees in summer to a min of 7 degrees in winter.

(a) was done some years ago with over 190,000 litres extracted do far, (averaged 500 litres per day this month for the garden) extrahappy
 but for (b), I could not find much technical data for a water sourced heat pump so its been on the back burner. flyingpig

Now I have found some good technical info on the Kensa heatpump website. It seems that for a water sourced heat pump in moving water, there is a 3 litres per minute per kW rule. Although it has not rained here for over two months I have measured a flow rate of around 15 litres per min which suggests I could theoretically extract 5 kW or so. Given that in winter the flow is generally better, maybe 7 or 8 kW is possible. The Kensa website also says one submersible mat with 250m of 32mm HDPE pipe can provide 6kW.

Hmmmmmm, I donít have the space for 250m of 32mm HDPE and the manhole access is only 600mm wide but what if I used copper ? wackoteapot
Its thermal conductivity is 800 times more than HPDE but then 250 / 800 = 0.3m of HPDE obviously would not work as its insanely short. Therefore I think the much lower thermal conductivity of water needs to be taken into account. Then I found on the EngineeringToolbox website that the overall heat transfer for copper as a heat exchanger in still water is circa 400w / k m2.

Therefore assume a 5 degree temp difference and an 8kW extraction I would need a copper surface area of 8000 / (400 x 5) = 4 m2.

I can buy coils of 25m of 10mm copper microbore pipe, each of which are easy to lower down the manhole. Each one has a surface area of 0.79 m2. So I bought one and I found it fitted easily with enough room for 4 or 5 of them. So thatís a total copper surface area of 3 or 4 m2. Mmmmmmm, its now getting interesting. fingers crossed!

Ground source heatpumps seem to be pricey bits if kit, but I found an 8kW discontinued and ex display one currently in a showroom on fleebay being sold by a heatpump company for around £1k. So took a punt and it arrives next week. tumble

Heatpump Spec


Bought the rest of the copper and I have been prototyping the heat exchanger on my lounge floor, much to the dismay of SWMBO. fight





Obviously more to follow ..................................................... chocolateteapot
« Last Edit: July 28, 2018, 07:37:46 PM by nowty » Logged

11kW+ of PV installed and 54+ MWh generated.
Lithium battery storage of 50+ kWh.
Hot water storage of 15+ kWh.
Heat storage of 15+ kWh.
6kW Ground source heatpump.
EV BMW i3 (another 30+ kWh's of storage).
250,000+ litres of water harvested from underground river.
Home grown Fruit and Veg.
offthegridandy
Hero Member
*****
Offline Offline

Posts: 979



« Reply #1 on: July 28, 2018, 02:51:29 PM »

This looks really good Nowty.  I remember following your subterranean adventures.  The copper coils look good.  Is the water clean(ish) or is the copper likely to be attacked by the water?

Keep us informed as you progress looks like a really interesting project.

Andy
Logged

8 KVA Lister TS2 Startamatic Genny
24 Volt 1000amp battery bank
Outback VFX3024
4.6 Kw PV array ground mounted
Outback Flexmax 80
2 X Flexmax 30 PV CC
2.5 Kw WT H Piggot design 4.5 Mtr Dia AC coupled
12 Mtr free standing Tower.
u/floor heating from oil boiler cross linked to 12 K wood stove
nowty
Hero Member
*****
Offline Offline

Posts: 777



« Reply #2 on: July 28, 2018, 03:13:29 PM »

The copper coils look good.  Is the water clean(ish) or is the copper likely to be attacked by the water?

The water is clean but it gets very cloudy when stirred up because of a layer of very fine silt. This silt builds slowly builds up in the catchpit, but gets cleared out when we have a heavy rain shower.

I have had a copper pipe connected to a small submersible pump down their for 5 years now for the water harvesting, and apart from a layer of crud on it, its fine.

I have two concerns,

1) The extra friction of the pipes causing more turbulence which may result in a slower max flow rate if we have a deluge.

2) I found a few stones in the catchpit the size of a fist so they must come through with some force, so there is potential for damage to the soft copper.
Logged

11kW+ of PV installed and 54+ MWh generated.
Lithium battery storage of 50+ kWh.
Hot water storage of 15+ kWh.
Heat storage of 15+ kWh.
6kW Ground source heatpump.
EV BMW i3 (another 30+ kWh's of storage).
250,000+ litres of water harvested from underground river.
Home grown Fruit and Veg.
offthegridandy
Hero Member
*****
Offline Offline

Posts: 979



« Reply #3 on: July 28, 2018, 03:36:21 PM »

Can you get some mesh in front of the incoming flow to catch any large debris?
Logged

8 KVA Lister TS2 Startamatic Genny
24 Volt 1000amp battery bank
Outback VFX3024
4.6 Kw PV array ground mounted
Outback Flexmax 80
2 X Flexmax 30 PV CC
2.5 Kw WT H Piggot design 4.5 Mtr Dia AC coupled
12 Mtr free standing Tower.
u/floor heating from oil boiler cross linked to 12 K wood stove
nowty
Hero Member
*****
Offline Offline

Posts: 777



« Reply #4 on: July 28, 2018, 05:58:03 PM »

Can you get some mesh in front of the incoming flow to catch any large debris?

Maybe, I will think about getting some stainless steel mesh if I can find some suitable for the job.
Logged

11kW+ of PV installed and 54+ MWh generated.
Lithium battery storage of 50+ kWh.
Hot water storage of 15+ kWh.
Heat storage of 15+ kWh.
6kW Ground source heatpump.
EV BMW i3 (another 30+ kWh's of storage).
250,000+ litres of water harvested from underground river.
Home grown Fruit and Veg.
donegal
Jr. Member
**
Offline Offline

Posts: 66


« Reply #5 on: July 28, 2018, 08:10:35 PM »

Looking good, i cant wait to see how this turns out. You've a lot to live up to after the last project genuflect.

Good luck
Logged
titan
Hero Member
*****
Offline Offline

Posts: 530


« Reply #6 on: July 28, 2018, 08:19:30 PM »

I would think with the copper coils that tight the total surface area would be reduced considerably. Had you considered pumping the water out and through an external heat exchanger, it would mean you would not be size constrained and could have optimum flow rates.
Logged
ecogeorge
Hero Member
*****
Offline Offline

Posts: 1311


« Reply #7 on: July 28, 2018, 09:44:14 PM »

Excuse me if i am missing something here but why are you building a collector (be it mdpe pipe or copper) ? why not just pump the water through your heatpump and return to waste ??
George.
Logged
nowty
Hero Member
*****
Offline Offline

Posts: 777



« Reply #8 on: July 29, 2018, 12:00:18 AM »

Excuse me if i am missing something here but why are you building a collector (be it mdpe pipe or copper) ? why not just pump the water through your heatpump and return to waste ??
George.

I did consider this as this as an option. i.e. do an an open loop design instead of a traditional closed loop collector. But everything I have read recommends against it unless the water is very clean and deep, even then there are issues.
I would need a large settling tank and more pumps and filtration, even then you can feck your heat pump heat exchanger very quickly with corrosion or blockages. Lots of maintenance.
An open loop design requires considerably more energy to pump out the water.
The water could freeze in the heat exchanger as there is no antifreeze.
If I returned the waste water to the river then licencing with the Environment Agency may be required.

I currently pump small quantities out for harvesting purposes and its not without its problems so attempting to do it on a larger scale and filter it etc, I just don't want to go there.

It would be best to have a direct heat exchange design where the refrigerant gas is circulated in a small pipe in the the water but thats unlikely to be a DIY project.
Logged

11kW+ of PV installed and 54+ MWh generated.
Lithium battery storage of 50+ kWh.
Hot water storage of 15+ kWh.
Heat storage of 15+ kWh.
6kW Ground source heatpump.
EV BMW i3 (another 30+ kWh's of storage).
250,000+ litres of water harvested from underground river.
Home grown Fruit and Veg.
nowty
Hero Member
*****
Offline Offline

Posts: 777



« Reply #9 on: July 29, 2018, 12:21:59 AM »

I would think with the copper coils that tight the total surface area would be reduced considerably. Had you considered pumping the water out and through an external heat exchanger, it would mean you would not be size constrained and could have optimum flow rates.

You could be right about the surface area being reduced, I did originally consider coiling it like a slinky and fixing it to a couple of strips of aluminium, but its just the practicality of doing it, and getting it all down there down a narrow manhole. I am hoping it won't make a huge difference as the thermal conductivity of copper is so huge compared with the water.

If you think about it, imagine it was a solid block of copper with hollow water channels within the block for the water to circulate. I think the most relevant factor would be the surface area of the water channels rather than just the surface area of the copper block exterior.

With regards to simply pumping the water out, I think I have answered it to my reply to ecogeorge.
Logged

11kW+ of PV installed and 54+ MWh generated.
Lithium battery storage of 50+ kWh.
Hot water storage of 15+ kWh.
Heat storage of 15+ kWh.
6kW Ground source heatpump.
EV BMW i3 (another 30+ kWh's of storage).
250,000+ litres of water harvested from underground river.
Home grown Fruit and Veg.
titan
Hero Member
*****
Offline Offline

Posts: 530


« Reply #10 on: July 30, 2018, 03:17:47 PM »


With regards to simply pumping the water out, I think I have answered it to my reply to ecogeorge.

Not quite, I was suggesting through a heat exchanger, closed loop for your HP, with anti freeze, open with no contamination for the cooling water. Also the effective cooling area for the copper coils is that which is in contact with the coolant, the coils will be much less effective in tight coils.
« Last Edit: July 30, 2018, 03:21:24 PM by titan » Logged
knighty
Hero Member
*****
Offline Offline

Posts: 2789


« Reply #11 on: July 31, 2018, 02:47:58 PM »

I think they're coiled a bit tight too... not enough room to let water flow between the coils?

could you coul the copper in slinky fashion - but keep the coils tight torture

run a few of lengths of copper/aluminium/stainless/whatever bar the full length and cable tie the coils to it

coils sized to fit down the length of the drain... then post them down? - guess you might have to cable tie the coils down in the hole to let you slide theme

you could rap all 4 coils at the same time, or have one after another... I guess if you're running them in parallel coil them all at the same time, if you're running them in series run them one after another?  (and flow water through them in opposite direction to the water flow through the drain)

put them in the drain pipe flowing away from your box area, then you can add some kind of rock catcher to the box area?

Logged
nowty
Hero Member
*****
Offline Offline

Posts: 777



« Reply #12 on: July 31, 2018, 07:42:17 PM »

I think they're coiled a bit tight too... not enough room to let water flow between the coils?

could you coul the copper in slinky fashion - but keep the coils tight torture

run a few of lengths of copper/aluminium/stainless/whatever bar the full length and cable tie the coils to it

Thats exactly what I had intended to do but when I went down the hole with a single 10m coil to see how it would fit as a slinky I realised its not really possible. Its difficult to explain, but the access, the shape, the depth, the claustrophobic space, working in cold water, all conspire against you.

The compromise was to use 25m coils all individually dropped in and tied together, at different depths and offset against each other so the water flow runs in and around each coil. After 4 of them, I found I had enough space for a 5th so I added another. The water is now packed with copper and I could not add any more. They are all paralleled up to give a similar cross sectional area to the main 22mm flow and return pipes.

If the ground loop temp keeps dropping and evidently its not working then I will have to re-visit the design and try to loosen out the coils, but I am hoping its just over engineered enough not to have to.



« Last Edit: July 31, 2018, 09:29:03 PM by nowty » Logged

11kW+ of PV installed and 54+ MWh generated.
Lithium battery storage of 50+ kWh.
Hot water storage of 15+ kWh.
Heat storage of 15+ kWh.
6kW Ground source heatpump.
EV BMW i3 (another 30+ kWh's of storage).
250,000+ litres of water harvested from underground river.
Home grown Fruit and Veg.
Nickel2
Hero Member
*****
Offline Offline

Posts: 1710


Method mixed with Madness


« Reply #13 on: July 31, 2018, 09:32:31 PM »

Gravy-mine springs to mind...  whistlie
Logged

1.140kW mono south-facing at 49*
EpEver 4210A at 24v
24V 400 Ah battery. (4x200Ah FLA)
EpEver STI1000-24-230 pure sine inverter
Of course it'll work. (It hasn't caught fire yet).
offthegridandy
Hero Member
*****
Offline Offline

Posts: 979



« Reply #14 on: August 01, 2018, 09:45:33 AM »

I've sussed it.
It's a ruddy great still he's making.

Send us a jar nowty!!
Logged

8 KVA Lister TS2 Startamatic Genny
24 Volt 1000amp battery bank
Outback VFX3024
4.6 Kw PV array ground mounted
Outback Flexmax 80
2 X Flexmax 30 PV CC
2.5 Kw WT H Piggot design 4.5 Mtr Dia AC coupled
12 Mtr free standing Tower.
u/floor heating from oil boiler cross linked to 12 K wood stove